A 2000 V single-phase synchronous generator is being used as a
backup
generator outside a diagnostic center. When the generator
terminals are short-circuited and a field excitation current of 2.5
A is passed, the
ammeter between the terminals read 100 A of full load current. If
the terminals
of the same generator are opened and the voltage across them is
measured using
a voltmeter, we get the value of 500 V with the same excitation
current. The
armature resistance is 0.8 ohms.
Determine the voltage regulation of this generator if it is
delivering 100 A
during normal operation with unity power factor, 100 A with 0.8
leading PF,
and with 0.71 lagging PF.
(Hint: Synchronous Impedance = (0.C Voltage) / (S.C Current))
A 2000 V single-phase synchronous generator is being used as a backup generator outside a diagnostic...
Question 4 (10 marks) A) A 10-kVA, 415-V, three phase, Y -connected synchronous generator has a winding resistance of 0.3 Q and a synchronous reactance of 0.6 on a per phase basis. Determine its voltage regulation at full load when the power factor is (a) 75% lagging and (b) 75% leading. B) (10 marks) A 220-V, Y-connected, three-phase, synchronous motor has a synchronous reactance of 4 O/phase and negligible armature winding resistance. At a certain load the motor takes 7.5...
A 480-V, 50-Hz, Y-connected, 6-pole synchronous generator has a synchronous reactance of 1 Ohm. Its full load armature current is 60 A at 0.8 pf lagging. Under full load conditions, the friction and windage losses are 1.5 kW, and core losses are 1 kW at 50 Hz. Ignore armature copper losses. The field has been adjusted so that the terminal voltage is 480 V at no load. a.What is the speed of rotation of this gen? b.What is the generator...
A 208 V, star-connected, 3-phase synchronous motor has a synchronous reactance of 4 ohms/phase and negligible armature winding resistance. At a certain load, the motor takes 7.2 kW at 0.8 pf lagging. If the power developed by the motor remains the same while the excitation voltage is increased by 50% by raising the field excitation, determine (a) the new armature current and (b) the new power factor.
A 3-phase, 7 kVA, 400 V, 2-pole, star-connected synchronous machine has negligible armature resistance and Xs-60/phase at rated terminal voltage The machine first runs as a generator in parallel with 3-phase, 400 V, 50 Hz power supply 111 Determine the generated voltage and torque angle of the machine operating as a generator, delivering rated kVA at 0 9 pf lagging Draw and label the corresponding phasor diagram for this condition 1 12 If the field excitation is increased by 18%...
Question 1 (Synchronous Generator Voltage Regulation Calculations) The synchronous impedance of a 13.2 kVA, 440 V, A-connected, three-phase, synchronous generator s itj 10 Ω/phase. Calculate the voltage regulation when the generator supplies the full load at a power factor of (a) 0.866 lagging, (b) unity, and (c) 0.866 leading. 10 Mark:s
A 75 MVA, 25 Kv, three-phase, 60 Hz synchronous generator has a synchronous reactance of X= 9 Ω per phase and a negligible resistance. The generator is delivrimg rated power at a 0.8 power factor lagging at the rated terminal voltage to an infinitie bus, as shown in the following figure 1. Figure 1.The synchronous generator connected to infinite bus in single phase. 1) The excitation voltage is E = 26.87 KV, The generator delivring 60 MW. Compute the powe...
In a synchronous generator, at 0.8 lagging power factor, an excitation voltage per phase of 240 V gives a rated terminal voltage V. If the power factor of load increases to unity, the excitation voltage per phase required to produce a terminal voltage of V must be a. 260 V b. 250 V c. 240 V d. 225 V
Assignment 4 An 11 kV, 50-Hz, Y-connected synchronous generator has a synchronous reactance of Xs-0.5Ω and armature resistance, Ra-005Ω. The terminal voltage in all working conditions is assumed constant and equal to the rated voltage. The generator is delivering a load current of 2000A at 0.8 PF leading a. Draw the per-phase equivalent circuit of the generator. b. Calculate the induced EMF, EA. c. Calculate the real and reactive power delivered at the generator terminals. d. Sketch the phasor diagram...
Be detailed please A three-phase y-connected 2300 V, 60 Hz round-rotor synchronous motor has a synchronous reactance of 2 ohms/ phase and negligible armature resistance. 2. If the motor takes a line current of 350 A operating at a leading pf of 0.8. calculate the armature voltage and the power angle. If the motor is operating on load with a load angle of-20%, and the excitation is adjusted so that the armature voltage is equal in magnitude to the terminal...
Question 5 (Svnchronous machines) a. A synchronous generator connected to an infinite grid has its frequency and terminal b. A six-pole, Y-connected three-phase synchronous machine rated 208 V (line-to- voltage fixed. What is the effect of increasing the excitation current in this case? line), 5500 VA has a synchronous reactance of 8 2 per phase at rated terminal voltage. It is operating as a generator connected to an infinite grid Determine the excitation voltage and the power angle if the...