Problem #2
Refrigerant 134a enters an adiabatic compressor at 0.1 MPa and -20 oC while it leaves at 1 MPa and 110 oC. The mass flow rate of the compressor is 0.3 kg/s. Determine: a) The power input to the compressor, in kW. b) The volume flow rate of the refrigerant at the compressor inlet.
h inlet = 395.6 kJ/kg
h outlet = 493.7 kJ/kg
Enthalpy values obtained from p-h curve of R134a
Mass flow =0.3 kg/sec
(A)
Power input = m*(hout - hin) = .3*(493.7 - 395.6) =29.43KWatt
(B)
Specific volume at compressor inlet
= 0.2074 (m^{3})/kg (obtained form p-h curve of R134-a)
Any doubt are welcome in commentbox
Please upvote and rate positive
Thanks in advance
Please upvote
Problem #2 Refrigerant 134a enters an adiabatic compressor at 0.1 MPa and -20 oC while it...
1 MPa Isentropic Efficiency of a Compressor Refrigerant-134a enters an adiabatic compressor as a saturated vapor at 100kPa at a rate of 0.7 m/min and exits at 1-MPa pressure. The isentropic efficiency of the compressor is 87%. R-134a Compressor Isentropic Compressor Work hs-h 100 kPa sat. vapor Actual Compressor Work Determine the refrigerant properties at the inlet and outlet for an isentropic process. Actual 2s entropic procEss Inlet state Determine the actual isentropic enthalpy from the efficiency. (Ans: 289.71 J/kg)...
A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated space at by The refrigerant enters the condenser at compressor consumes 3.3 kW of power, determine (a) the mass flow rate of the refrigerant, (b) the refrigeration load, (e) the COP, and (d) the g waste heat to cooling water that enters the condenser at 18°C at a rate of 0.25 kg/s and leaves at 26°C. 1.2 MPa and 50°C and leaves at the same...
Refrigerant-134a is compressed by an adiabatic compressor from the saturated vapor state at 0.12 MPa to 1.2 MPa and 70 C at a rate of 0.108 kg/s. The power input to the compressor is 6.85 kW 59.4 kW 6.42 kW 63.4 kW 587 kW
6. Refrigerant-134a enters an adiabatic compressor as saturated vapor at 100 kPa at a rate of 0.7 m3/min and exits at 1 MPa pressure. If the isentropic efficiency of the compressor is 87%, determine (a) the temperature of the refrigerant at the exit of the compressor, (b) the power input (in kW), and (c) the rate of entropy generation during this process.
Refrigerant 134a enters a compressor with a mass flow rate of 15 kg/s with a velocity of 10 m/s. The refrigerant enters the compressor as a saturated vapor at 10°C and leaves the compressor at 1400 kPa with an enthalpy of 281.39 kJ/kg with a negligible velocity. The rate of work done on the refrigerant is measured to be 380 kW. If the elevation change between the compressor inlet and exit is negligible, determine the rate of heat transfer associated...
Refrigerant-134a enters the compressor of a refrigerator as superheated vapor at 0.14 MPa and -10°C at a rate of 0.124 kg/s, and it leaves at 0.7 MPa and 50°C. The refrigerant is cooled in the condenser to 24°C and 0.65 MPa, and it is throttled to 0.15 MPa. Disregarding any heat transfer and pressure drops in the connecting lines between the components, determine (a) the rate of heat removal from the refrigerated space and the power input to the compressor...
4. Refrigerant- 134a enters an adiahaticpressor as saturated vapor at 240°C and leaves at 09 MIPa and 60°C. The mass flow rate of the refrigerant is 1.2 kg/s. Determine (a) the power input to the compressor and (b) the volume flow rate of the refrigerant at the compressor inlet
1. Refrigerant 134a enters the compressor of a refrigerator as superheated vapor at 0.20 MPa and -10 °C at a rate of 0.07 kg/s, and it leaves at 1.2 MPa and 70 °C. The refrigerant is cooled in the condenser to 44 °C and 1.130 MPa and it is throttled to 0.20 MPa. Disregarding heat transfer and pressure drop in the connecting lines between the components, show the cycle on a T-s diagram with respect to the saturation line. Determine...
A vapor compression refrigeration cycle utilizes R-134a as the working fluid. The refrigerant flow rate is 50 g/s. Vapor at 150 kPa and -10 0C enters the compressor and leaves at 1.2 MPa and 75 0C. The power input to the non-adiabatic compressor is measured and found to be 2.4 kW. The refrigerant enters the expansion valve at 1.15 MPa and 40 0C and leaves the evaporator at 160 kPa and -15 0C. Determine the entropy generation in the compression...
1) A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated space at -30°C by rejecting its waste heat to cooling water that enters the condenser at 16 °C at a rate of 0.25 kg/s and leaves at 26°C. The refrigerant enters the condenser at 1.2 MPa and 65°C and leaves at 42°C. The inlet state of the compressor is 60 kPa and -34°C and the compressor is estimated to gain a net heat of...