General Information (Problems 2–4) The envelope of a four-story steel building (risk category II) is shown below. ResistanceProblem 3 (30%) Determine the magnitude of the axial force, P, in the brace shown below due to wind loading. Each brace in th

0 0
Add a comment Improve this question Transcribed image text
Answer #1

the value for the questions are as follows:

height of the building = 60 ft

wind speed = 140 mph

Kzt = 1

Kd = 0.85

exposure catagory = C

gust factor G = 0.85

external coefficient pressure Cp = 0.8 ( windward wall )

external coefficient pressure Cp = 0.25 ( leeward wall )

design wind pressure = p = q G Cp −qi (G Cpi) ( from ASCE 7-10)

since internal pressures need not to be evaluated, G Cpi = 0 ( given in question)

design wind pressure = p = q G Cp

q=0.00256 Kz Kzt Kd V2    ( from ASCE 7-10)

Kz = 1.13 (for exposure catogory C at height 60 ft from ASCE 7-10)

q = 0.00256 x 1.13 x 1 x 0.85 x 1402

q = 48.19 lb/ft2

design wind pressure for external coefficient pressure Cp = 0.8 ( windward wall ) ,

pw = 48.19 x 0.85x 0.8 = 32.76 lb/ft2

design wind pressure for external coefficient pressure Cp = 0.25 ( leeward wall ) ,

pl = 48.19 x 0.85x 0.25 = 10.24 lb/ft2

therefore,

magnitude of axial force P due to wind load on windward wall = pw x A

where A is the area of windward wall exposed to wind

Pw = 32.76 x 36 x 60

Pw = 70761.6 lb

Pw = 70.76 kip

magnitude of axial force P due to wind load on leeward wall = pl x A

where A is the area of windward wall exposed to wind

Pl = 10.24 x 36 x 60

Pl = 22118.4 lb

Pl = 22.12 kip

axial load P due to wind load are 70.76 kip and 22.12 kip on windward and leeward wall respectively

Add a comment
Know the answer?
Add Answer to:
General Information (Problems 2–4) The envelope of a four-story steel building (risk category II) is shown...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 1. Your team is designing the lateral load-resisting system for a two-story office building. To do...

    1. Your team is designing the lateral load-resisting system for a two-story office building. To do so, you need to determine the wind loads on the lateral load-resisting elements. At this preliminary stage, consider the floor and roof diaphragms to be flexible, and consider the wind pressure to be uniform. Note that the south and east walls have been cut away so that we can see the system supporting them. 1. When the wind blows from the south, it creates...

  • Design the first story shear wall for a three-story building with unfactored north- south lateral wind...

    Design the first story shear wall for a three-story building with unfactored north- south lateral wind loads of 32 kips, 64 kips, 64 kips at the roof, third floor, and second floor, respectively. The floor-to-floor height is 12 ft and all shear walls have equal thickness and an equal length of 15 ft. Assume normal-weight concrete: fe' is 3000 psi and fy is 60,000 psi. Note: please the units that are in feet and inches if they can draw the...

  • A one-story building shown has a concrete slab roof. The shear walls are all 10-inch concrete...

    A one-story building shown has a concrete slab roof. The shear walls are all 10-inch concrete and also act as bearing walls. All the walls are 12 feet in height. The walls are assumed to act as cantilevers. Consider earthquake in the North-South direction. Determine the distribution of the shears on the shear walls. Assume the design base shear V= 100 kips in the N-S direction. The center of mass is located on the plan. The building is in Seismic...

  • The single-story unbraced frame shown below is subjected to dead load, roof live load, and wind load Figure 1 shows the...

    The single-story unbraced frame shown below is subjected to dead load, roof live load, and wind load Figure 1 shows the results of a first-order analysis relative to the columns of the frame. The axial load and end moment (also equal to the maximum moment in the column) are given separately for the different load cases (i.e., dead load, roof live load, and lateral wind load). All vertical loads are symmetrically placed and contribute only to the Mnt moments (i.e.,...

  • Problem 22. Two-story, one-bay unbraced frame shown below is subjected to gravitational dead and live loads...

    Problem 22. Two-story, one-bay unbraced frame shown below is subjected to gravitational dead and live loads and wind lateral load. The columns are made of W18x65 (I,-1070 in , Ag- 19.1 in2, r-7.49 in, ry-1.69 in) and beams are made of W18x71 (1, 1170 in). The table below shows the moments at the ends of column 4-5 due to three load cases. The frame is fully braced in lateral direction. Use Grade50 steel Bending is about strong axis. All gravity...

  • is the second floor of a four-story building. a flat Consider the floor framing plan shown...

    is the second floor of a four-story building. a flat Consider the floor framing plan shown below. Thi The design floor live load is 90 psf. The design roof live load is 20 psf. The structure has roof G1 G4 /2 G2 GS 2o G3 FLOOR FRAMING PLAN Assume that the floor between Beams B7 and B8 is supported directly by these two beams only (not by Girders G2 and G3). Beam B7 has a self-weight of 30 plf. The...

  • Problem 1: A lateral load resisting system of a 4-story building consists a K-truss and is...

    Problem 1: A lateral load resisting system of a 4-story building consists a K-truss and is shown in the figure below. Based on the ASCE 7-10, the wind load at each floor level was calculated and applied to the truss joints as shown in Figure below. 1. Determine if the truss system is determinate and Stable (support A is pin; and support B is roller) 2. Calculate the support reactions 3. Using any analysis method, calculate the forces in members...

  • Consider the five-story building shown in the figure.The average weights of the floor and roof are 80 lb/ft and 7...

    Consider the five-story building shown in the figure.The average weights of the floor and roof are 80 lb/ft and 70 lb/ft, respectively The values of SDS and Spiare equal to 0.9 g and 0.4 g. respectively. Since steel moment frames are used in the north-south direction to resist the seismic forces, the value of Requals 8. Compute the seismic base shear V. Then, distribute the base shear along the height of the bulding A 4@25' 100 Plan (a) roof 20...

  • Don’t do the extra credit. Just the regular problem. The single-story unbraced frame shown below is...

    Don’t do the extra credit. Just the regular problem. The single-story unbraced frame shown below is subjected to dead load, roof live load, and wind load Figure I shows the results of a first-order analysis selative to the columns of the frame The axial load and end moment (also equal to the maximum moment in the column) are given separately for the diffierent load cases (i e, dead load, roof live load, and lateral wind load) All vertical loads are...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT