a. The beam of the cross section shown has f'c = 3000 psi and fy =...
A rectangular beam made using concrete of fc' = 6000 psi and steel with fy= 60 ksi. The beam has a width B=20 in and a total depth of 20 in with an effective depth d=17.5 in. The tensile steel consists of 4 #11 bars at the bottom side. a) Determine the maximum service load moment that can be resisted without stressing the concrete above 0.45fc' or the steel above 0.4fy. b) Calculate the nominal flexural moment capacity of the...
Find the maximum design axial load strength for the tied column of cross section shown in Figure 1.1. Check the ties. Assume a short column. Use f’c = 4000 psi and fy = 60,000 psi for both longitudinal steel and ties. Also, draw the flexural and shear reinforcement on a sketch. Case 1: Design of Short Columns- Small Eccentricity Find the maximum design axial load strength for the tied column of cross section shown in Figure 1.1. Check the ties....
For the beam shown use f-3000 psi and fy 60000 psi. 1- Compute the effective flange width 2- Compute фМ, for the positive and negative moment regions and check ACI requirements for both sections. At the support, the bottom bars are in one layer and at mid-span, the # 8 bars are in the bottom layer and the # 7 bars are in a second layer. Assume 2.5 in concrete cover (from outside face of concrete to the center of...
4. For the beam shown below,fe' = 4000 psi and fy = 60,000 psi. (20 points) (a) Compute the effective flange width at midspan. 911-6 in (a) Beam section and distance to adjacent beams Support (negative bending) Midspan positive bending) 7 No. 7 bars IIT 3 No. 8 plus 2 No. 7 bars at midspan 22 2 No. 8 bars at ends (b) Beam span supported by 18-in. wide columns (b) Compute Mn for the positive and negative-moment regions and...
B. Select the required reinforcing steel for the following beam section for Mo = 130 fl-k, ML = 275 fl-k, fy = 60,000 psi, fc = 3,000 psi, b = 15'. d = 24", and d' = 2.5". Verify the section using the actual bar selection. Determine the required number of layers for the top and bottom bars. Show a sketch of the cross section indicating bar sizes and bar layout. 2.5" 15'
reinforced concrete A. Select the required reinforcing steel for the following beam section for MD = 190 ft-k, ML = 390 ft-k, fy = 60,000 psi, f'c = 3,000 psi, bi = 54", bw = 15", tf = 3", and d = 24". Verify the section using the actual bar selection. Determine the required number of layers for the bars. Show a sketch of the cross section indicating bar sizes and bar layout. +3+ 15" - As we have discussed...
5. Determine the moment capacity of a doubly reinforced beam below. Use fy=60,000 psi and fc'= 4000 psi. b=20 AS =1.58 h=36" d=33 Las=1248 Doubly Reinforced Section
Problem 2 Determine the design moment capacity (фМ.) for the beam cross section below 20° fy-80,000 psi f 6,000 psi 24" 27 6 # 11 bars 3"
The continuous beam shown in Fig. 1 is part of a beam-and-slab floor system of an office building and is typical of a series of beams spaced at 4 m intervals. In addition to the dead load, the live load on the floor is 3 kPa. Using f'c = 32MPa, N32 bars for main reinforcement, a) Find the maximum positive and negative moments using the AS3600 simplified method. b) Design the beam cross-section for the maximum amount of tensile steel...
1. A simply supported rectangular concrete beam has a clear span of 6m has a width of 400mm and has an effective depth of 625mm. The beam supports a total factored load of 168kN/m which includes the weight of the beam. Use fc’=28MPa, fy=414MPa. Use normal weight of concrete with 1.0. Determine approximately the total number of stirrups needed for the beam. 2. A rectangular beam reinforced for tension only has b=200mm and d=350mm. The tension steel area provided is...