Please Explain in details thanks
Explain why there is (a) a limit less than the kVA rating of the alternator on the kVA the machine can supply at unity p.f., and (b) why there is a limit on the kVA the machine can supply at 0.8 p.f. lagging.
In the case of an alternator rating is expressed in terms of kVA or apparent power. And the power factor of an alternator is determined by the load connected to it. Generally the power factor of an alternator is lagging in nature.
Apparent power ( kVA) of a machine is the amount of power that the alternator can deliver. And real power(kW) is the power that the machine delivering to the load for work. Reactive power is the amount of power the machine delivering for the reactive requirements ( charging and discharging of inductive and capacitive components) of the load
The Apparent power (kVA) = ( Real power(kW) ^2 + ( Reactive power (kVAr) ^2 )
where real power ( kW) = kVA cos
reactive power(kVAr) = kVAsin
a) when an alternator supplies at unity power factor ( cos =1) then Real power = Apparent power
and reactive power ( kVAr) is zero because ( sin =0) at unity power factor the alternator does not have to deliver reactive power and hence the machine or alternator can deliver the full rating kVA at unity power factor for doing work.
here the delivered power to the load in kW = Rating of the alternator in kVA
And hence it is said like that the altentaor supplying at unity power factor can deliver limit less power equal to the rating of the machine in kVA
b)
And when an alternator is supplying a load at 0.8 pf lagging then ,
real power ( kW) = 0.8 * Apparent power (kVA)
Reactive power( kVAr) = 0.2 * Apparent power(kVA)
hence at 0.8 pf lagging 20% of the apparent power or kVA of the alternator has to be supplied for reactive power requirement of the load. And only 80% of apparent power or kVA of the alternator is supplied as real power in kW to the load for doing work. And hence at 0.8 pf lagging there is a limit at the kVA that the machine can deliver. So the machine can not deliver full power rating of the machine at 0.8 pf lagging condition.
Please Explain in details thanks Explain why there is (a) a limit less than the kVA...
please answer 13.16 at rated load of unity power factor and rated terminal voltage, determine efficienc including field rheostat loss. Ans. 93.139 13.11 A generator under test is rated at 100 KVA, 3-phase, 60-Hz; 2,400 volts. (a) If driven b a de motor unexcited, the motor output is 1.26 KW. (b) If driven by a de motor, generato on open circuit and excited to generate rated potential, the motor output is 2.5 KW. ( Ifdriven by a de motor, generator...
can you answer this question and explain why? thanks. A 50-Hz 10-MVA, 66/22-kV distribution transformer has a full-load efficiency of 98% at 0.8 lagging power factor. The transformer core loss is 80 kW. The transformer supplies an industrial load that has a constant demand of 5000 kW at 0.65 lagging power factor. The cost of energy is $0.1 per kWh. 1. In the following questions, assume that the voltage at the load terminal is maintained constant at 22 kV. calculations....
please explain in details. thanks 1. What is a defibrillator? And how does it work? Explain in detail. ( explain it in a minimum of 3 to 4 paragraphs in details) 2. What is the Resistors for human skin? Explain in details 3. How long can you apply Electric currents to the human body? Explain in details 4. Why can we only apply electric currents for a short time in the human body? Explain
If a company has control, but less-than majority, must they consolidate? Please explain why or why not.
Please kindly explain why the answer is B, it a reaction is less than Zero? TIF AGⓇ for a reaction is less than zero, what can you say about the value of K for the reaction? a. K<land the reaction is spontaneous under standard conditions. K >1 and the reaction is spontaneous under standard conditions. = r standard conditions. => Why if da Reaction R = 0 and the reaction is at equilibrium. is less that ou (d) <0 and...
Can someone please explain to me how is this less substituted? Please explain in detail. Thanks!! Remember, you're looking for the less substituted group, so "b" is correct.... 1) ВН, 2) Н,О, ОН- 3) Н,О b a CH3 CH3 он н н он less substituted, anti-markovnikov
Step by step precise and concise full solution please A distribution board distributes energy to various items of plant via an installation which has a high voltage (H.V.) panel, a low voltage (L.V) panel and a transformer. The details are as follows: The H.V. panel obtains a 3-phase supply at 11 kV. The transformer circuit-breaker is equipped with 75/5A current transformers which feed a very inverse 3-poles overcurrent relay of 5-A rating. The transformer has a rating of 1000 kVA...
can you calculate and explain why? thanks A single-phase thyristor rectifier as 50 Hz source. The rectifier delivers a DC voltage of 150 V to a highly inductive depicted in Figure 1 is fed from a 220 V rms, 1. load with a resistive value of 10 Q. SCR, T SCR2 + is Vo SCR3 SCR T Figure 1 (a) for a delay angle component indicating its phase shift with respect to the input voltage v, Sketch the net rectifier...
Linux / Unix: Please explain in details if you can. Thanks 2. Define what is meant by symbolic link with an example.
Please show detailed steps. Thanks Problem # 1: Three Phase Power [35 points] A three-phase substation bus supplies three wye-connected three phase loads that are connected in parallel through a three-phase feeder with an impedance of 0.3 30 per phase Load 1 draws 75kVA at 0.866 lagging power factor, load 2 draws 45 kW at 0.70 leading power factor and load 3 draws 20 kVAR at 0.85 lagging power factor. The line-line voltage at the load is 460V Take the...