Question

2. The transformer is loaded: 15 KW load, 0.9 lagging PF, and Vs=450 V.
a) Find the voltage at the high-voltage side of the transformer (Vp).
b) Find the Voltage Regulation and the Efficiency of this transformer under this load.
Page 2 of

Problem 3 The equivalent circuit of a 22KVA, 11700/450 V, 60Hz, single phase transformer when referred to its low-voltage sid
0 0
Add a comment Improve this question Transcribed image text
Answer #1

Given app 0295 + j?! wman jX EP 15 kW load 107 lagging pf Moltage V₂ = 450V a pak 1 j4.5k 0 Tyone Ratio Ck) = No = No Up Ve 1b) Voltage Regulation Cuir%) at no load - u at = v fall load xiro V at full load ve - VS X 100 - 476.39 - 450 xico 950 TURY =

Add a comment
Know the answer?
Add Answer to:
2. The transformer is loaded: 15 KW load, 0.9 lagging PF, and Vs=450 V. a) Find...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A 200 kVA, 7200/600 V, 60 Hz transformer is operating at rated load and 0.9 p.f....

    A 200 kVA, 7200/600 V, 60 Hz transformer is operating at rated load and 0.9 p.f. lagging. The core loss, winding resistances and leakage reactances, expressed in per unit are 0.0056, 0.0133 and 0.0557 respectively. Determine: a) The efficiency. b) The voltage regulation. c) The efficiency and regulation at 0.3 load and 0.8 p.f. lagging. A 200 kVA, 7200/600 V, 60 Hz transformer is operating at rated load and 0.9 p.f. lagging. The core loss, winding resistances and leakage reactances,...

  • Q1: A 20-kVA 8000/480-V distribution transformer has the following resistances and reactances: Rp...

    Q1: A 20-kVA 8000/480-V distribution transformer has the following resistances and reactances: Rp 322 X,-45 Ω R,-0.05 Ω X,-0.06 Ω The excitation branch impedances are given referred to the high-voltage side of the transformer. (a) Find the equivalent circuit of this transformer referred to the high-voltage side. (b) Assume that this transformer is supplying rated load (20kVA) at 480 V and 0.8 PF lagging. What is this transformer's input voltage? What is its voltage regulation? (c) What is the transformer's...

  • Electric Machinery Problem 2: [50 points] A 15-KVA, 230/2300-V transformer is considered. The following test data...

    Electric Machinery Problem 2: [50 points] A 15-KVA, 230/2300-V transformer is considered. The following test data have been taken: | OC Test (on Primary) Voc = 230 V loc = 2.8 A Poc = 100 W SC Test (on Secondary) Vsc = 47 V Isc = 9.5 A Psc = 350 W (a) Find the equivalent circuit of this transformer referred to the high- voltage side. [10 points] (b) Find the equivalent circuit of this transformer referred to the low-...

  • 2) A 50kVA, 2400/240V single phase transformer has the test measurements: (20) Open circuit test: 240V,...

    2) A 50kVA, 2400/240V single phase transformer has the test measurements: (20) Open circuit test: 240V, 5.0A, 450W (HV open) Short circuit test: 55V, 20.8A, 600W (LV short) a Caleulate the transformer equivalent circuit parameters and draw the transformer equivalent circuit. b) Find the voltage regulation and efficiency when the transformer is connected to a load that is 75% of the rated load current at 0.8 pf lagging. c) Find the voltage regulation and efficiency when the transformer is full...

  • 4. [Transformer - 15 points) A 50-kVA, 13,800/208-V, A-Y distribution transformer has an equivalent resistance of...

    4. [Transformer - 15 points) A 50-kVA, 13,800/208-V, A-Y distribution transformer has an equivalent resistance of 3 percent and a reactance of 9 percent per unit. (a) What is the transformer's phase impedance referred to the high-voltage side? (b) Calculate this transformer's voltage regulation at full load and 0.9 PF leading.

  • Solvein pu sysvem 2-10. A 13,800/480 V three-phase Y-A-connected transformer bank consists of thr...

    please solve the question in pu sysyem !!!! Solvein pu sysvem 2-10. A 13,800/480 V three-phase Y-A-connected transformer bank consists of three identical 100-kVA 967/480-V transformers. I is supplied with power directly from a large constant-voltage bus. In the short-circuit test, the recorded values on the high-voltage side for one of these transformers are Isc 12.6 A Pc3300 w (a) If this bank delivers a rated load at 0.85 PF lagging and rated voltage, what is the line-to-line voltage on...

  • A 5 MVA 230/13.8 kV, single-phase transformer has a per-unit resistance of 1% and a per-unit...

    A 5 MVA 230/13.8 kV, single-phase transformer has a per-unit resistance of 1% and a per-unit reactance of 5%. The open-circuit test performed on the low voltage side of the transfromer yielded the following data: VOC=13.8 kV, IOC=21.1 A, and POC=90.8 kW. (a) Find the equivalent circuit referred to the high voltage side of this transformer. (b) If the transformer is operating at full-load and at 0.8 pf lagging, find the voltage regulation of the transformer at this operating condition.

  • A single-phase transformer of nominal values of 10kVA, 440/220 V and 60 Hz supplies nominal load...

    A single-phase transformer of nominal values of 10kVA, 440/220 V and 60 Hz supplies nominal load at a power factor of 0.85 lagging connected to the side of low voltage. The load operates at a nominal voltage and the transformer has the following parameters: R=0.160, X,=0.48 , R=0.040, X=0.12, R900, Xy=1300. Determine: 1. The voltage regulation of the transformer. 2. The efficiency of the transformer.

  • A three-phase load of 15 kVA with a PF of 0.8 lagging is connected in parallel...

    A three-phase load of 15 kVA with a PF of 0.8 lagging is connected in parallel with a three-phase load of 36 kW at 0.6 PF leading. The line-line voltage is 2000V. a) Find the total complex power and power factor. Is it inductive or capacitive? b) How much kVAR is needed to make the PF unity? c) What is the magnitude of the current going into the total load?

  • The short-circuit test readings for a 50-kVA 2400:240-V transformer are 48 V, 20.8 A, and 617...

    The short-circuit test readings for a 50-kVA 2400:240-V transformer are 48 V, 20.8 A, and 617 W, with the instruments located on the high-voltage side and the low-voltage side short- circuited. An open-circuit test with the low-voltage side energized gives instrument readings on that side of 240 V, 5.41 A, and 186 W. 1. Calculate the equivalent parameters of the transformer as referred to the high-voltage side. 2. Draw the equivalent approximate circuit of that transformer referred to the high...