a) Secondary phase voltage is 80 kv.
As it is y connected, line voltage Vline = √3Vph
= √3×80 =138.564Kv
b) Secondary phase current
I2 ph = 180 × 10^ 6/ ( √3× Vline)
= 180×10^6/(√3× 80×10^3)
= 1299.038 A
Primary phase current I1ph= 180×10^6/(√3×V1 line)
I1ph = 180×10^6/(√3× 13.2× 10^3)
= 7872.958 A.
C) incoming current I1 line = √3× I1ph = √3×7872.958
= 13636.363 A.
Outgoing line current =secondary phase current = 1299.03A
1. Three single-phase step-up transformers rated at 75 MVA, 13.2 kV/80 kV are connected in delta-...
a. Three single phase step-up transformers rated at 40 MVA, 13.2 kV/80 kV are connected in delta-wye on a 13.2 kV transmission line. If they feed a 90 MVA load calculate the following: i. The secondary line voltage ii. The current in the transformer windings iii. The incoming line currents iv. If the transformer types are two (2) additive and one (1) subtractive draw the connection diagram for the configuration stated using physical representation. b. A 3-phase squirrel cage motor has twelve (12) leads (labelled 1 to...
Three single-phase transformers rated at 250 kVA, 7200 V/600 V, 60 Hz, are connected in wye- delta on a 12.47 kv, 3-phase line. If the load is 450 kVA, calculate: a. The currents in the incoming and outgoing transmission lines b. The currents in the primary and secondary windings 1. sratod t 200 w 3o0 v/6oO V 60 Hz are used to raise the
Three single-phase transformers rated at 250 kVA, 7200 V/600 V, 60 Hz, are connected in wye-...
Problem 4 Three ideal single-phase transformers are connected in a delta/wye configuration with the primary side of the three-phase transformer rated at 120 kV and the secondary side rated at 13.8 kV. The rated power of the transformer bank is 20 MVA. One side of the transformer bank is connected to a 120 kV transmission line, and the other side is connected to a three-phase load of 15 MVA at 0.85 lagging power factor. Compute the following: a) The turns...
1. In order to meet an emergency, three single-phase transformers with 12.470/7.200 V are connected in Delta-Wye to form a three-phase transformer which is fed by a 12.470 V transmission line. If the transformer supplies 60 MVA to a load, calculate: (3 marks) a. The turns ratio for each transformer b. The currents in the primary and secondary windings of the transformer c. The primary and secondary transmission line currents 2. A Wye-Delta transformer is connected to a 66 kV...
Three single-phase transformers are connected in a wye-delta configuration to step down a line voltage of 13.8kV to 4160V to supply an industrial facility. The plant draws 8MW at a 0.80 power factor. Transformer impedances can be neglected. Calculate the following: a. the apparent power (SL) drawn by the load/plant. b. the apparent power (Ss) furnished by the HV source. c. the current in the HV lines (141) d. the current in the LV lines (112) e. the currents in...
2. In order to meet an emergency, three single-phase transformers rated 100 kVA (each), 13.2 kV/2.4 kV are connected in Y-∆ on a 3-phase, 20 kV line. a. What is the maximum load that can connected to the transformer bank? b. What is the outgoing line voltage?
10. In order to meet an emergency, three single-phase transformers with 12.4707.200 Vrms are connected in A-Y to form a three-płuase transformer wluch is fed by a 12,470-V transmission line. If the transformer supplies 60 MVA to a lood, find (a) the tum ratio for each transformer, (b) the currents in the primary and secondary windings of the transformer, (c) the incoming and outgoing transmission line cuarents
Three single-phase transformers are connected in delta-delta configuration to step up a line voltage of 8 kV to 120 kV. A 24 MVA load at angle 30 is connected to the high voltage side. Calculate: a) Transformer turns ratio b) Load power in MW c) Line current in HV and LV sides d) The apparent power supplied by each transformer e) If one transformer is removed for maintenance, what is the reduction percentage in the transformer bank power rating with...
What is the answer for questions 2-5?
Questions: 1. Delta-Wye and Wye-Delta configurations both produce: a) Increases in secondary voltages and currents. b) Decreases in the secondary voltages and currents. c) Phase shift between the incoming and outgoing line voltages. d) Additional V3 increases in the secondary voltages and currents. ANSWER: Choose an item. 2. The line voltage at the secondary of a 10:1 wye-delta connected transformer will be: a) Equal to the line voltage at the primary times b)...
Please answer the problem below for all parts . Please show all
work and write clearly. Thanks.
(a) (0) What is the difference between an autotransformer and a conventional transformer? 2. (ii) Why are high-impedance transformer used in electric toys? (b) Three single-phase transformers each rated at 150 kVA, 7200 V/600 V, 60 Hz, are connected in wye-delta on a 12470 V, 3-phase line. If the load is 450 kVA, calculate the followings: (i) The current flowing in the incoming...