10. In order to meet an emergency, three single-phase transformers with 12.4707.200 Vrms are connected in...
1. In order to meet an emergency, three single-phase transformers with 12.470/7.200 V are connected in Delta-Wye to form a three-phase transformer which is fed by a 12.470 V transmission line. If the transformer supplies 60 MVA to a load, calculate: (3 marks) a. The turns ratio for each transformer b. The currents in the primary and secondary windings of the transformer c. The primary and secondary transmission line currents 2. A Wye-Delta transformer is connected to a 66 kV...
1. Three single-phase step-up transformers rated at 75 MVA, 13.2 kV/80 kV are connected in delta- wye on a 13.2 kV transmission line. If they feed a 180 MVA load, calculate the following: a. The secondary line voltage b. The currents in the primary and secondary windings C. The incoming and outgoing transmission line currents
Three single-phase transformers rated at 250 kVA, 7200 V/600 V, 60 Hz, are connected in wye- delta on a 12.47 kv, 3-phase line. If the load is 450 kVA, calculate: a. The currents in the incoming and outgoing transmission lines b. The currents in the primary and secondary windings 1. sratod t 200 w 3o0 v/6oO V 60 Hz are used to raise the Three single-phase transformers rated at 250 kVA, 7200 V/600 V, 60 Hz, are connected in wye-...
Problem 4 Three ideal single-phase transformers are connected in a delta/wye configuration with the primary side of the three-phase transformer rated at 120 kV and the secondary side rated at 13.8 kV. The rated power of the transformer bank is 20 MVA. One side of the transformer bank is connected to a 120 kV transmission line, and the other side is connected to a three-phase load of 15 MVA at 0.85 lagging power factor. Compute the following: a) The turns...
2. In order to meet an emergency, three single-phase transformers rated 100 kVA (each), 13.2 kV/2.4 kV are connected in Y-∆ on a 3-phase, 20 kV line. a. What is the maximum load that can connected to the transformer bank? b. What is the outgoing line voltage?
a. Three single phase step-up transformers rated at 40 MVA, 13.2 kV/80 kV are connected in delta-wye on a 13.2 kV transmission line. If they feed a 90 MVA load calculate the following: i. The secondary line voltage ii. The current in the transformer windings iii. The incoming line currents iv. If the transformer types are two (2) additive and one (1) subtractive draw the connection diagram for the configuration stated using physical representation. b. A 3-phase squirrel cage motor has twelve (12) leads (labelled 1 to...
Three single-phase transformers are connected in a wye-delta configuration to step down a line voltage of 13.8kV to 4160V to supply an industrial facility. The plant draws 8MW at a 0.80 power factor. Transformer impedances can be neglected. Calculate the following: a. the apparent power (SL) drawn by the load/plant. b. the apparent power (Ss) furnished by the HV source. c. the current in the HV lines (141) d. the current in the LV lines (112) e. the currents in...
3. Three single-phase, 10 kVA, 460/120 V, 60 Hz transformers are connected to form a three-phase 460/208 V transformer bank. The equivalent impedance of each transformer referred to HV side is 1.0 + j2.0 Ω. The transformer delivers 25 kW at 0.9 pf lagging at rated voltage. Answer the following questions: (a) Draw a schematic diagram showing the transformer connection. Draw three separate single-phase transformers and complete their primary and secondary connections. (b) Determine the magnitude of transformer primary and...
Please answer the problem below for all parts . Please show all work and write clearly. Thanks. (a) (0) What is the difference between an autotransformer and a conventional transformer? 2. (ii) Why are high-impedance transformer used in electric toys? (b) Three single-phase transformers each rated at 150 kVA, 7200 V/600 V, 60 Hz, are connected in wye-delta on a 12470 V, 3-phase line. If the load is 450 kVA, calculate the followings: (i) The current flowing in the incoming...
19. Three single-phase transformers are connected in A - A. Each of these transformers has a secondary phase current of 10 A. The value of the secondary line current is 19. Three single-phase transformers are connected in A - A. Each of these transformers has a secondary phase current of 10 A. The value of the secondary line current is