CHAPTER 2. SELECTED TOPICS IN THERMODYNAMICS Laboratory Quiz 4 - Psychrometry A new HVAC system is...
Question NO. 3 (25 points) A space to be maintained at 27°C dry-bulb temperature has a rate of sensible-heat gain of 13 kW and a rate of latent heat gain of 8.5 kW. The system used to condition the space to the required conditions. The mass flow rate of air supplied to the space is 1.1 kg/s. Outdoor air at 38 °C dry-bulb temperature and 17 ℃ dew-point temperature is introduced into the system at a rate of 0.28 kg/s....
Problem 7 O/5 points (0%) Humid air at 1 atm, 42 °C dry bulb and 55 % relative humidity is cooled at constant pressure to a temperature 9 °C below its dew-point temperature. Sketch the psychrometric diagram for the process and determine the heat transfer from the air o kJ/kg dry air Cooling coils T2 φ2 T1 ф! 101.3 kPa i H-4」+'Condensate Condensate removal Now Problem (resets attempts) Resets Remaining: 10 Attempts Remaining: 10 Submit Problem 7 O/5 points (0%)...
The atmospheric air 32 °C dry bulb temperature and 70% relative humidity supplied to the cooling coil at a rate of 45m3/min. The air cooling to the saturated state and leaving at a temperature of 16 °C. Determine: a- Specific humidity at each state. b- Wet bulb and dew point temperatures at the final state c- Final relative humidity. d- Mass of water condensed. e- Rate of heat removed from the air in kW. f- Show the process on Psychrometric...
4. Air-Conditioning Unit [20 Marks] 1 m3/s of moist air at 32 °C with a relative humidity of 70% is to be treated by a simple air condition system to produce air at 18 °C with a relative humidity of 50% The system will have two stages. In the first stage, the air will pass over cooling coils to dehumidify it, and in the second stage it will be heated electrically to the specified outlet conditions You may ignore the...
Subject Refrigeration and Air Conditioning. Please answer in detail. QUESTION 4 - COOLING AND DEHUMIDIFYING COILS An air conditioned space at 1700 metres altitude has a sensible heat gain of 26 kW and a latent heat gain of 6.5 kW. The space is maintained at 25°C dry bulb and 18°C wet bulb temperature:s The fresh air supply is to be 0.65 m3/s at 35°C dry bulb and 24°C wet bulb temperatures. The air leaving the coil has a relative humidity...
Example: The sensible- and latent-heat gains in a space served by a single-zone air conditioner are 65 and 8 kW, respectively. The space is to be maintained at 24 oC and 50% relative humidity. The design conditions of outdoor air are 35 oC dry-bulb and 25 oC wet-bulb temperatures. For ventilation purposes outdoor air is mixed with recirculated air in a 1:4 proportion. When mixed air at the resulting conditions enters the cooling coil, the outlet air conditions are 12...
QUESTION 1 [15 marks] Due: 5 August 2020 An air conditioner operating at steady state takes in moist air at 28°C, 1 atm and 70% relative humidity. The moist air first passes over a cooling coil in the dehumidifier unit and some water vapor is condensed. The rate of heat transfer between the moist air and the cooling coil is 38.69 kW. Both saturated moist air and condensate streams exit the dehumidifier unit at the same temperature. The moist air...
o question: An airconditioned space is to be maintained at 26 C dry bulb temperature and 50% RH. The ambient condition is 4 27.78 kW and the latent load is 11.11 kW. 60% of the return air mass is recirculated and mixed with 40% of make-up fresh air before entering the AHU. Calculate: Room SHF -Supply flow rate (m'/sec) (assume supply temperature is 10 C lower than space's) Apparatus sensible and latent load Apparatus sensible heat factor, dew point, and...
Use a psychrometric chart to determine the properties of air under different conditions. 1-Find the properties of air at 70 degrees F and 50% relative humidity. Find humidity ratio, wet bulb temperature, dew point, enthalpy, and specific volume. 2-Find the properties of air at 55 degrees F and 30% relative humidity. Find humidity ratio, wet bulb temperature, dew point, enthalpy, and specific volume. 3-Air enters a furnace at a dry bulb temperature of 60 degrees F and 50% relative humidity...
Air entering a dryer has a temperature (dry bulb) of 60°C and a dew point of 26.7°C. Using the humidity chart, determine the actual humidity H, percentage humidity HP, humid heat cS and humid volume vH.