Air entering a dryer has a temperature (dry bulb) of 60°C and a dew point of 26.7°C. Using the humidity chart, determine the actual humidity H, percentage humidity HP, humid heat cS and humid volume vH.
dew point = 26.7*C
% saturation = 100%
From the Humidity chart for 100% humidity
actual humidity at 60 C
H = 0.0225 kg H2O/kg dry air
% Humidity = 14%
Humid heat Cs = 1.005 + 1.88H
= 1.005 + 1.88*0.0225
= 1.047 kJ/kg dry air - K
Humid volume = 2.83*10^-3 T + 4.56*10^-3 T H
= 2.83*10^-3 * (60 +273) + 4.56*10^-3 (60 +273) (0.0225)
= 0.977 m3/kg dry air
Air entering a dryer has a temperature (dry bulb) of 60°C and a dew point of...
Exercise 2 Moist air at 1 atm. barometric pressure has a dry bulb temperature of 40°C and a wet bulb temperature of 320C. Using both the equations for the moist air properties and the psychrometric chart find: g) the partial pressure of the water vapor h) humidity ratio i) relative humidity j) dew-point temperature k) specific volume 1) enthalpy of moist air Insert the data and the results from the chart in the following table: Enthalpy Specific kJ/kg m/kg Humidity...
1. Wet solids pass through a continuous dryer. Hot dry air enters the dryer at a rate of 400 kg/min and mixes with the water that evaporates from the solids. Humid air leaves the dryer at 50°C containing 2.44 wt% water vapor and passes through a condenser in which it is cooled to 10°C. The pressure is constant at 1 atm throughout the system. a. At what rate (kg/min) is water evaporating in the dryer? b. Use the psychrometric chart...
b) A cooling coil of an Air Handling Unit has dew-point of 8'C dry-bulb (db) temperature, and outdoor air enters the cooling equipment at 28 C d.b temperature and leaves at 16'C d.b temperature with mass flow rate of lkg/s determine: i) the contact factor (CF) ii) the volume flow rate iii) the by-pass factor iv) the sensible heat that removed from the outdoor air (1.5 mark) (1.5 marks) (1 mark) (2.0 marks) c) Explain the difference between "relative humidity...
b) A cooling coil of an Air Handling Unit has dew-point of 8'C dry-bulb (db) temperature, and outdoor air enters the cooling equipment at 28 C d.b temperature and leaves at 16'C d.b temperature with mass flow rate of lkg/s determine: i) the contact factor (CF) ii) the volume flow rate iii) the by-pass factor iv) the sensible heat that removed from the outdoor air (1.5 mark) (1.5 marks) (1 mark) (2.0 marks) c) Explain the difference between "relative humidity...
What would be the dry bulb temperature, wet bulb temperature, dew point, percent saturation, enthalpy and humidity ratio would be if the following quantities of air were mixed: 1000 ft3 at 80°F and 70% saturated and 2500 ft3 at 100°F dry bulb and 87°F wet bulb temperature. Show your answer in a psychrometric chart and be sure to turn in your chart. 13)
Exercise 3 Moist air at 1 atm. barometric pressure has a dry bulb temperature of 29 C and a wet bulb temperature of 22°C. Using the psychrometric chart and the table for saturated vapor find the following air properties: Pr T- 40 a) the partial pressure of the water vapor b) humidity ratio c) relative humidity d) dew-point temperature e) specific volume ) enthalpy of moist air
The atmospheric air 32 °C dry bulb temperature and 70% relative humidity supplied to the cooling coil at a rate of 45m3/min. The air cooling to the saturated state and leaving at a temperature of 16 °C. Determine: a- Specific humidity at each state. b- Wet bulb and dew point temperatures at the final state c- Final relative humidity. d- Mass of water condensed. e- Rate of heat removed from the air in kW. f- Show the process on Psychrometric...
seperation process , show graph Questi (aho Question: An atmospheric direct heat dryer is to operate with air containing water vapors entering at partial pressure of water i.e. 0.028 atm and vapor pressure of water i.e. 1.56 atm. From the psychrometric chart and relationships, determine the followings: 1) Wet bulb temperature (°F) Dew point Temperature (°F) Enthalpy (Btu per pound of dry air) Dry bulb temperature (°F) Humid volume (ft) from (both relationship and psychrometric chart) Humidity (grains of moisture...
Problem 7 O/5 points (0%) Humid air at 1 atm, 42 °C dry bulb and 55 % relative humidity is cooled at constant pressure to a temperature 9 °C below its dew-point temperature. Sketch the psychrometric diagram for the process and determine the heat transfer from the air o kJ/kg dry air Cooling coils T2 φ2 T1 ф! 101.3 kPa i H-4」+'Condensate Condensate removal Now Problem (resets attempts) Resets Remaining: 10 Attempts Remaining: 10 Submit Problem 7 O/5 points (0%)...
104. An air-water vapour mixture has a dry-bulb temperature of 333 K and a dew-point temperature of 313 K. The total pressure is 101.3 kPa and the vapour pressure of water at 313 K is 7.3 kPa and that at 333 K is 19.91 kPa. The humidity of air expressed as kg of water vapour per kg of dry air is (a) 0.048 (b) 0.079 (c) 0.122 (d) 0.152