Problems - A two constant air-volume system with duct reheater similar to the one shown in...
Subject Refrigeration and Air Conditioning. Please answer in detail. QUESTION 4 - COOLING AND DEHUMIDIFYING COILS An air conditioned space at 1700 metres altitude has a sensible heat gain of 26 kW and a latent heat gain of 6.5 kW. The space is maintained at 25°C dry bulb and 18°C wet bulb temperature:s The fresh air supply is to be 0.65 m3/s at 35°C dry bulb and 24°C wet bulb temperatures. The air leaving the coil has a relative humidity...
A building is designed for the following cooling loads. Room specific heat gain and latent heat gains are 310 kW and 100 kW respectively. The room is maintained at a dry bulb temperature of 25°C and relative humidity of 50%. The outdoor air is at 28°C with 50% relative humidity, 10% by mass of outdoor air is supplied to the building. If the air supplied to the room should be at a temperature lower than 18°C, detemine the following. (a)...
Question 4 Page 15 It is required to 125 marks] design a cold storage for storing vegetables with the following available data Outside design conditions 36°C DBT. 28 C WBT Inside design conditions T2 19°C DBT, 60% RH Infiltrated air 180 mhr V ms-7.83 kg/s Fresh air supplied from outside 4500 mhr Total mass of air supplied to the room Sensible heat gain through glass SH,5.5AW Sensible heat gain through walls and roof H 10.8 kW Ihr KJ Sensible heat...
A motel in Miami, Florida has a sensible cooling load of 75 tons and a sensible heat ratio on the building of 0.85. Each of the motel's 100 rooms must be supplied with 30 cfm of outside air to satisfy the local ventilation codes. If the rooms are kept at 75F and 50% R.H., determine: a.) sketch of the system b.) Air flow to the building in cfm (fan size) c.) The mixed air condition-temperature and humidity d.) The cooling...
An Conference Center is to be air-conditioned for a seating capacity of 3200 people for the following outdoor and comfort conditions a) Outdoor design conditions = 35 °C, db and 65% R.H b) Indoor/return design conditions-26 deg C. db and 55% RH. c) Total sensible room load = 420,000 kJ/hr d) Total latent room load = 200,000 KJ/hr e) The rise in dry bulb temperature of the air inside the conference center is limited to 9 °C (i.e. the Supply...
Example: The sensible- and latent-heat gains in a space served by a single-zone air conditioner are 65 and 8 kW, respectively. The space is to be maintained at 24 oC and 50% relative humidity. The design conditions of outdoor air are 35 oC dry-bulb and 25 oC wet-bulb temperatures. For ventilation purposes outdoor air is mixed with recirculated air in a 1:4 proportion. When mixed air at the resulting conditions enters the cooling coil, the outlet air conditions are 12...
Question NO. 3 (25 points) A space to be maintained at 27°C dry-bulb temperature has a rate of sensible-heat gain of 13 kW and a rate of latent heat gain of 8.5 kW. The system used to condition the space to the required conditions. The mass flow rate of air supplied to the space is 1.1 kg/s. Outdoor air at 38 °C dry-bulb temperature and 17 ℃ dew-point temperature is introduced into the system at a rate of 0.28 kg/s....
PROBLEM 2. (20 POINTS) A space to be maintained at 25 C dB (dry bulb) temperature and 18°C wB (wet bulb) has a rate of sensible-heat gain of 25 kWand a rate of moisture gain of20 kg/hr. Moist air enters the space at a dry-bulb temperature of 15°C. Outdoor air at 35 C dB temperature and 25 C wB is supplied for ventilation purposes at a rate of 400 Us (litres per second) of standard air. After leaving the room,...
Please show work and explain how and why each step is used. Use psychrometric chart. 3. A portion of a museum is required to be conditioned to 75°F/50% RH year round. Since it's a museum, the humidity must be controlled. Under design conditions, this portion of the museum has sensible cooling loads of 35,000 Btu/hr and latent cooling loads of 15,000 Btu/hir The air handler (Figure 1) designed to maintain conditions has a cooling coil, a reheat coil, and a...
b) A cooling coil of an Air Handling Unit has dew-point of 8'C dry-bulb (db) temperature, and outdoor air enters the cooling equipment at 28 C d.b temperature and leaves at 16'C d.b temperature with mass flow rate of lkg/s determine: i) the contact factor (CF) ii) the volume flow rate iii) the by-pass factor iv) the sensible heat that removed from the outdoor air (1.5 mark) (1.5 marks) (1 mark) (2.0 marks) c) Explain the difference between "relative humidity...