Describe the components of an ICS and a SCADA system. Provide examples of how each are configured and used in the industry.
ANSWER:-
THE COMPONENTS OF OF AN ICS AND A SCADA
Industrial control system (ICS) is a general term that encompasses several types of control systems used in industrial production, including supervisory control and data acquisition (SCADA) systems, distributed control systems (DCS), and other smaller control system configurations such as programmable logic controllers (PLC) often found in the industrial sectors and critical infrastructures.
Key ICS Components
Key components include the following:
Control Loop. A control loop consists of sensors for measurement, controller hardware such as PLCs, actuators such as control valves, breakers, switches and motors, and the communication of variables. Controlled variables are transmitted to the controller from the sensors. The controller interprets the signals and generates corresponding manipulated variables, based on set points, which it transmits to the actuators. Process changes from disturbances result in new sensor signals, identifying the state of the process, to again be transmitted to the controller.
Human-Machine Interface (HMI). Operators and engineers use HMIs to monitor and configure set points, control algorithms, and adjust and establish parameters in the controller. The HMI also displays process status information and historical information.
Remote Diagnostics and Maintenance Utilities. Diagnostics and maintenance utilities are used to prevent, identify and recover from abnormal operation or failures.
The following is a list of the major control components of an ICS:
Control Components :
Control Server. The control server hosts the DCS or PLC supervisory control software that communicates with lower-level control devices. The control server accesses subordinate control modules over an ICS network.
SCADA Server or Master Terminal Unit (MTU). The SCADA Server is the device that acts as the master in a SCADA system. Remote terminal units and PLC devices (as described below) located at remote field sites usually act as slaves.
Remote Terminal Unit (RTU). The RTU, also called a remote telemetry unit, is a special purpose data acquisition and control unit designed to support SCADA remote stations. RTUs are field devices often equipped with wireless radio interfaces to support remote situations where wire-based communications are unavailable. Sometimes PLCs are implemented as field devices to serve as RTUs; in this case, the PLC is often referred to as an RTU.
Programmable Logic Controller (PLC). The PLC is a small industrial computer originally designed to perform the logic functions executed by electrical hardware (relays, switches, and mechanical timer/counters). PLCs have evolved into controllers with the capability of controlling complex processes, and they are used substantially in SCADA systems and DCS. Other controllers used at the field level are process controllers and RTUs; they provide the same control as PLCs but are designed for specific control applications. In SCADA environments, PLCs are often used as field devices because they are more economical, versatile, flexible, and configurable than special-purpose RTUs.
Intelligent Electronic Devices (IED). An IED is a “smart” sensor/actuator containing the intelligence required to acquire data, communicate to other devices, and perform local processing and control. An IED could combine an analog input sensor, analog output, low-level control capabilities, a communication system, and program memory in one device. The use of IEDs in SCADA and DCS systems allows for automatic control at the local level.
Human-Machine Interface (HMI). The HMI is software and hardware that allows human operators to monitor the state of a process under control, modify control settings to change the control objective, and manually override automatic control operations in the event of an emergency. The HMI also allows a control engineer or operator to configure set points or control algorithms and parameters in the controller. The HMI also displays process status information, historical information, reports, and other information to operators, administrators, managers, business partners, and other authorized users. The location, platform, and interface may vary a great deal. For example, an HMI could be a dedicated platform in the control center, a laptop on a wireless LAN, or a browser on any system connected to the Internet.
Data Historian. The data historian is a centralized database for logging all process information within an ICS. Information stored in this database can be accessed to support various analyses, from statistical process control to enterprise level planning.
Input/Output (IO) Server. The IO server is a control component responsible for collecting, buffering and providing access to process information from control sub-components such as PLCs, RTUs and IEDs. An IO server can reside on the control server or on a separate computer platform. IO servers are also used for interfacing third-party control components, such as an HMI and a control server.
Network Components
There are different network characteristics for each layer within a control system hierarchy. Network topologies across different ICS implementations vary with modern systems using Internet-based IT and enterprise integration strategies. Control networks have merged with corporate networks to allow control engineers to monitor and control systems from outside of the control system network. The connection may also allow enterprise-level decision-makers to obtain access to process data. The following is a list of the major components of an ICS network, regardless of the network topologies in use:
Fieldbus Network. The fieldbus network links sensors and other devices to a PLC or other controller. Use of fieldbus technologies eliminates the need for point-to-point wiring between the controller and each device. The devices communicate with the fieldbus controller using a variety of protocols. The messages sent between the sensors and the controller uniquely identify each of the sensors.
Control Network. The control network connects the supervisory control level to lower-level control modules.
Communications Routers. A router is a communications device that transfers messages between two networks. Common uses for routers include connecting a LAN to a WAN, and connecting MTUs and RTUs to a long-distance network medium for SCADA communication.
Firewall. A firewall protects devices on a network by monitoring and controlling communication packets using predefined filtering policies. Firewalls are also useful in managing ICS network segregation strategies.
Modems. A modem is a device used to convert between serial digital data and a signal suitable for transmission over a telephone line to allow devices to communicate. Modems are often used in SCADA systems to enable long-distance serial communications between MTUs and remote field devices. They are also used in SCADA systems, DCS and PLCs for gaining remote access for operational and maintenance functions such as entering commands or modifying parameters, and diagnostic purposes.
Remote Access Points. Remote access points are distinct devices, areas and locations of a control network for remotely configuring control systems and accessing process data. Examples include using a personal digital assistant (PDA) to access data over a LAN through a wireless access point, and using a laptop and modem connection to remotely access an ICS system.
SCADA (supervisory control and data acquisition) : Is a system for remote monitoring and control that operates with coded signals over communication channels (using typically one communication channel per remote station). The control system may be combined with a data acquisition system by adding the use of coded signals over communication channels to acquire information about the status of the remote equipment for display or for recording functions. It is a type of industrial control system (ICS).
Common system components:
A SCADA system usually consists of the following subsystems:
Remote terminal units (RTUs) connect to sensors in the process
and convert sensor signals to digital data. They have telemetry
hardware capable of sending digital data to the supervisory system,
as well as receiving digital commands from the supervisory system.
RTUs often have embedded control capabilities such as ladder logic
in order to accomplish Boolean logic operations.
Programmable logic controller (PLCs) connect to sensors in the
process and convert sensor signals to digital data. PLCs have more
sophisticated embedded control capabilities (typically one or more
IEC 61131-3 programming languages) than RTUs. PLCs do not have
telemetry hardware, although this functionality is typically
installed alongside them. PLCs are sometimes used in place of RTUs
as field devices because they are more economical, versatile,
flexible, and configurable.
A telemetry system is typically used to connect PLCs and RTUs with
control centers, data warehouses, and the enterprise. Examples of
wired telemetry media used in SCADA systems include leased
telephone lines and WAN circuits. Examples of wireless telemetry
media used in SCADA systems include satellite (VSAT), licensed and
unlicensed radio, cellular and microwave.
A data acquisition server is a software service which uses
industrial protocols to connect software services, via telemetry,
with field devices such as RTUs and PLCs. It allows clients to
access data from these field devices using standard
protocols.
A human–machine interface or HMI is the apparatus or device which
presents processed data to a human operator, and through this, the
human operator monitors and interacts with the process. The HMI is
a client that requests data from a data acquisition server or in
most installations the HMI is the graphical user interface for the
operator, collects all data from external devices, creates reports,
performs alarming, sends notifications, etc.
A Historian is a software service which accumulates time-stamped
data, Boolean events, and boolean alarms in a database which can be
queried or used to populate graphic trends in the HMI. The
historian is a client that requests data from a data acquisition
server.
A supervisory (computer) system, gathering (acquiring) data on the
process and sending commands (control) to the SCADA system.
Communication infrastructure connecting the supervisory system to
the remote terminal units.
Various processes and analytical instrumentation.
Examples:
1)
Figure shows an example of a SCADA system implementation. This particular SCADA system consists of a primary control center and three field sites. A second backup control center provides redundancy in the event of a primary control center malfunction. Point-to-point connections are used for all control center to field site communications, with two connections using radio telemetry. The third field site is local to the control center and uses the wide area network (WAN) for communications. A regional control center resides above the primary control center for a higher level of supervisory control. The corporate network has access to all control centers through the WAN, and field sites can be accessed remotely for troubleshooting and maintenance operations. The primary control center polls field devices for data at defined intervals (e.g., 5 seconds, 60 seconds) and can send new set points to a field device as required. In addition to polling and issuing high-level commands, the SCADA server also watches for priority interrupts coming from field site alarm systems.
2)
Figure shows an example implementation for rail monitoring and control. This example includes a rail control center that houses the SCADA system and three sections of a rail system. The SCADA system polls the rail sections for information such as the status of the trains, signal systems, traction electrification systems, and ticket vending machines. This information is also fed to operator consoles at the HMI station within the rail control center. The SCADA system also monitors operator inputs at the rail control center and disperses high-level operator commands to the rail section components. In addition, the SCADA system monitors conditions at the individual rail sections and issues commands based on these conditions (e.g., shut down a train to prevent it from entering an area that has been determined to be flooded or occupied by another train based on condition monitoring).
3)
Figure 2-7 gives examples of low-level controllers found on a
DCS system. The field control devices shown include a PLC, a
process controller, a single loop controller, and a machine
controller. The single loop controller interfaces sensors and
actuators using point-to-point wiring, while the other three field
devices incorporate fieldbus networks to interface with process
sensors and actuators. Fieldbus networks eliminate the need for
point-to-point wiring between a controller and individual field
sensors and actuators. Additionally, a fieldbus allows greater
functionality beyond control, including field device diagnostics,
and can accomplish control algorithms within the fieldbus, thereby
avoiding signal routing back to the PLC for every control
operation. Standard industrial communication protocols designed by
industry groups such as Modbus and Fieldbus [7] are often used on
control networks and fieldbus networks.
In addition to the supervisory-level and field-level control loops,
intermediate levels of control may also exist. For example, in the
case of a DCS controlling a discrete part manufacturing facility,
there could be an intermediate level supervisor for each cell
within the plant. This supervisor would encompass a manufacturing
cell containing a machine controller that processes a part and a
robot controller that handles raw stock and final products. There
could be several of these cells that manage field-level controllers
under the main DCS supervisory control loop.
4)Programmable Logic Controllers
PLCs are used in both SCADA and DCS systems as the control components of an overall hierarchical system to provide local management of processes through feedback control as described in the sections above. In the case of SCADA systems, they provide the same functionality of RTUs. When used in DCS, PLCs are implemented as local controllers within a supervisory control scheme. PLCs are also implemented as the primary components in smaller control system configurations. PLCs have a user-programmable memory for storing instructions for the purpose of implementing specific functions such as I/O control, logic, timing, counting, three mode proportional-integral-derivative (PID) control, communication, arithmetic, and data and file processing. Figure 2-8 shows control of a manufacturing process being performed by a PLC over a fieldbus network. The PLC is accessible via a programming interface located on an engineering workstation, and data is stored in a data historian, all connected on a LAN.
Describe the components of an ICS and a SCADA system. Provide examples of how each are...
Describe each category of middleware and provide examples of when and how each category of middleware is used (among clients, servers, databases, and applications) Explain the relationship that each middleware category has with both the client and the server. Provide current examples of middleware.
Create an action plan that depicts how to implement at least (5) NIST controls on the system in a Prison. These controls will be countermeasures against the (3) common ICS/SCADA vulnerabilities related to configurations, applications, protocols, and so forth, identified BELOW Three common vulnerabilities with ICS and SCADA systems: Buffer Overflows: this is nothing but a common vulnerability and it is caused by software code to overrun the boundary and even override the memory blocks. This kind of vulnerability can...
describe the 5 internal contros and give examples how managers used them on business Components of Internal Control aControl Environment Risk Assessment Control Activities lnformation and Communication Monitoring
What is attribution error? Provide examples for components of this theory. How is this related to ethical communication and emotional intelligence?
A digital system board uses 40 ICs manufactured with two different independent processes. 25 ICs are manufactured using process 1 that has 80 % yield and 90 % fault coverage. The cost of these ICs is 10 KD each. The remaining ICs (15) are manufactured using process 2 with 85 % yield and 95 % fault coverage. The cost of these ICs is 20 KD each. The board manufacturer spends 50 KD on the design and test of each board...
1. Discuss and provide examples of data that can be collected by hospices. 2. Describe the four levels of hospice care found in the Medicare Conditions of Participation. 3. List several important functional components of a dental practice management system. 4. Explain why the dentist needs to have a complete and accurate medical history for a patient.
Explain how the National Incident Management System fits into the homeland security apparatus. . What are the five components of NIMS? Explain each in detail. . The ICS is said to be based on 14 previously time-tested management characteristics. Name five of these and describe each in detail.
what are the 5 components of cultural compentence? provide examples
Describe volume, efficiency and rate variances? Provide examples of each of these from your experience.
Describe and provide examples of each type of intelligence that Howard Gardner illustrates in his theory of multiple Intelligences