Given data :
Span of beam L = 26 ft
Slab thickness hf = 3 in
Breadth of web, bw = 10 in
Overall depth of beam,h = 24 in
Effective depth, d = 21 in
center to center distance
left side = 6 ft
right side = 6 ft
Strength of concrete, = 3000 psi
Yield strength of steel, =fy = 60000 psi
Service live load, =200 psf
CALCULATIONS
STEP-1 ;Computation of factored bending moment
Self weight of beam, = 150 pcf x { 6 x 3/12 + 10 x 21/144}
WDL =444 plf
Uniformly distributed live load,
Therefore,factored design load,
Factored design moment,
STEP -2 : Effective flange width,b
Clear distance
a) b shall not exceed one fourth of the span length
b = L/4
= 26 * 12/4
= 78 in
b) The effective overhanging slab width on each side of the web shall not exceed eight times the slab thickness, that is = 8 x hf = 24 in
b= 24 + 10 + 24
= 58 in
Therefore, b= 58 in ( the smallest of the three values )
STEP - 3: Computation of area of reinforcement, As
Assuming j =0.95,
Provide 2 # 10 bars and these will fit into the web in single layer
Area of steel provided,
STEP 4 : Check if As >= As,min
OK
CAPACITY CHECK
STEP-5 : Computation of a
Since a is less than hf, the beam has rectangular beam action
STEP -6 Check whether fs = fy
Therefore,fs = fy
Check if the section is tension controlled or not
NOTE :
i) For single layer of reinforcement , dt = d
ii) For double layer, dt = d - clear cover stirrup dia-half of bar dia
Since the tension reinforcement is in single layer
dt = 21 in
a/dt = 0.04714
Therefore, the section is tension - controlled and
Note :
i) for tension controlled sections
ii)for compression controlled sections
for transition sections
STEP-7 :Computation of nominal moment capacity of beam,Mn
Lever arm, jd = (d-a/2)
= 20.505 in
nominal moment capacity, Mn = Asfy(d-a/2)
= 2.45 * 6000*20.51 = 3014235 in.lb
=251.2 ft-kips
The design moment capacity of the beam is obtained as:
Hence, it is SAFE
Select reinforcement for the T-beams in the simply-supported floor system shown below. The system is 26-foot-long...
1. T-Beams are used to support a floor in an industrial building. The floor is used for product storage so it must be designed for a heavy 600 psf. The floor must also support a superimposed dead load of 20 psf (in addition to the self-weight of the beams and slab. The layout of the beams and slabs is shown below. The beams span 30.0% and are spaced at 4.0” center to center. The slab is 3” thick. The concrete...
2. A continuous concrete floor system consists of parallel beams spaced 8' on centers and spanning 25' between supports. The 4" thick slab is cast monolithically with the beam webs which have width, b 14 in. and total depth h 28 in. (measured from top of slab). Each T- beam must carry a dead load of 55 psf (the slab weight+ flooring) and service live load of 225 psf in addition to its own weight. Material properties are fe-4 ksi...
For all the problems on this assignment: • Assume concrete with a compressive strength of fi'= 4 ksi and a unit weight of yc = 150 pcf. Assume Grade 60 reinforcement will be utilized. • Assume all live loads have already been reduced if appropriate. Problem 3 (10 points) Design a one-way slab (24-foot-long, simply supported) to support a live load of 150 psf and no additional dead load other than the self-weight of the slab. Round proposed slab dimensions...
CVE 313- 1- Design a square footing for the interior column shown in the figure. The column carries 2 k 't of uniform live load and 1.5 k/t of uniform dead load (including the self weiht of the structure), the base of the footing is 5 ft below grade, the soil weight is 100 lb/ft', and q," 5000 psf. and concrete unit weight is 150 lb/ (25 points) NOTE: Your design should only include the following (one-way shear, two-way shear,...
*please solve ALL questions Assume that the floor between Beams B7 and B8 is supported directly by these two beams only (not by Girders G2 and G3). Beam B7 has a self-weight of 30 plf. The floor slab consists of a 4-in.-thick, normal-weight, reinforced concrete slab (unit weight = 150 pcf). An additional floor dead load of 15 psf is specified to account for the weight of suspended utilities and fixtures. As an exterior beam, B7 must also support one...
Please refer AISC 15th edition 4. A composite floor system consists of a 5-inch slab which is supported by W14x30 beams without shoring. Fy-50 ksi, strength of concrete is 4ksi, beam spacing is 8-ft, the effective width is 81-inches, and the span is 35-ft. Construction load is 20 psf and the live load is 160 psf. Compute the maximum deflection before the concrete has cured. (credit weight 20)
b.323 The empirical provisions of 6.3.2.1 and 6.3.2.2 were developed for nonprestressed T-beams. The flange widths in 6.3.2.1 and 6.3.22 should be uset Problem Two: The beam shown below part is for an interior span and is cast monolithically with a one-wav slab. The clear span for the beam is 30 feet, and the clear spacing between beams is 10 feet. (a) Reinforcement is shown for the positive moment region. Determine if the beam is adequate to support a uniformly...
Problem Two: The beam shown below part is for an interior span and is cast monolithically with a one-way slab. The clear span for the beam is 30 feet, and the clear spacing between beams is 10 feet. (a) Reinforcement is shown for the positive moment region. Determine if the beam is adequate to support a uniformly distributed, factored load of 5 k/ft. (b) Design the slab reinforcement for the positive moment region using a factored load of 500 psf....
is the second floor of a four-story building. a flat Consider the floor framing plan shown below. Thi The design floor live load is 90 psf. The design roof live load is 20 psf. The structure has roof G1 G4 /2 G2 GS 2o G3 FLOOR FRAMING PLAN Assume that the floor between Beams B7 and B8 is supported directly by these two beams only (not by Girders G2 and G3). Beam B7 has a self-weight of 30 plf. The...
fé = 4000 psi * DO fy= 60ksi Please design the rebars for T-beam AB for the floor system shown. The Live Load is 75 psf. Plane view The dead Load is 15 psf including the concrete self weight. Normal weight Concrete is used. 12"