Question

A refrigerator is operating between a high pressure of 0.7 MPa and low pressure of 0.1 MPa


A refrigerator is operating between a high pressure of 0.7 MPa and low pressure of 0.1 MPa. The Isentropic efficiency of the compressor is 0.8. The working fluid of the refrigeration cycle is R134a flowing at 0.1 kg/s. The specific heat of air is 1.005 kJ/kgk and density of air is 1.2 kg/m. 

Calculate 

a. The compressor exit temperature. 

b. The compressor power input. 

c. The evaporator cooling load. 

d. The coefficient of performance.

e. The steam quality at the evaporator inlet.

f. If the cooling load obtained in part is used to cool a building space for 30 minutes causing drop of 20°C in the space temperature calculate the volume of the space to be cooled. 

3 0
Add a comment Improve this question Transcribed image text
✔ Recommended Answer
Answer #1

A)

Since, which refrigeration cycle is to be followed is not mentioned. we will consider Vapour Compression Refrigeration System (VCRS) for this case.

The following is the T-S chart for the current refrigeration cycle.

Ideal compression process Condenser Throttle valve Actual compression process 4 Evaporator VCRS

Since the properties of R-134a is not given to us in the question, I shall be using the tables which I have with me, for solving this sum.

The data is as follows:

Pressure (MPa) T(saturation) (C) hf (kJ/kg) hg (kJ/kg) sf (kJ/kgK) sg (kJ/kgK)
0.7 26.69 88.82 265 0.3323 0.9199
0.1 -26.37 17.28 234.4 0.07188 0.9518

The compressor inlet enthalpy h1 = hg (at 0.1 MPa) = 234.4 kJ/kg

It is said that the compressor is has an isentropic efficiency of 0.8.

If the compressor was supposed to be ideal, then the exist state would have been (2') (as marked in the image)

In such a case, the s1 = s2'.

  • s1 = sg (at 0.1 MPa) = 0.9518 kJ/kgK

Now, s1 = s2' = 0.9518 kJ/kgK

But s2' = sg+C.ln\frac{T_{final}}{T_{initial}}

where

  • sg (at 0.7 MPa) = 0.9199 kJ/kgK
  • C = Specific heat of R-134a = 1.036 kJ/kgK
  • T(final) = T2' = ?
  • T(initial) = Saturation temperature at 0.7 MPa = 26.69 C = 299.69 K

Thus, s2' = sg+C.ln\frac{T_{final}}{T_{initial}}

0.9518 = 0.9199+1.036\times ln\frac{T_{2'}}{299.69}

T2' = 309.1 K

Now, the enthalpy h2' = hg + C x (T2' - T(sat))

where

  • hg (at 0.7 MPa) = 265 kJ/kg
  • C = Specific heat of R-134a = 1.036 kJ/kgK
  • T2' = 309.1 K
  • T(sat) = Saturation temperature at 0.7 MPa = 26.69 C = 299.69 K

h2' = hg + C x (T2' - T(sat))

h2' = 265 + 1.036 x (309.1 - 299.69) => h2' = 274.75 kJ/kg

Now, since it is given that the isentropic efficiency = 0.8

\eta _{isen}=\frac{h2'-h1}{h2-h1}

We have all the required values, thus,

\eta _{isen}=\frac{h2'-h1}{h2-h1}

0.8=\frac{274.75-234.4}{h2-234.4}=>\mathbf{h2 = 284.84\: kJ/kg}

Now, finally, h2 = hg + C x (T2 - T(sat))

where

  • hg (at 0.7 MPa) = 265 kJ/kg
  • C = Specific heat of R-134a = 1.036 kJ/kgK
  • T2 = Exit temperature of compressor = ? (our answer)
  • T(sat) = Saturation temperature at 0.7 MPa = 26.69 C = 299.69 K

h2 = hg + C x (T2 - T(sat))

284.84 = 265 + 1.036 x (T2 - 299.69) => Exit temperature = T2 = 318.834 K

----------------------------------------------------------

B)

Compressor Power input = m(refrigerant) x (h2 - h1)

where

  • m(refrigerant) = 0.1 kg/s
  • h2 = 284.84 kJ/kg
  • h1 = 234.4 kJ/kg

Compressor Power input = m(refrigerant) x (h2 - h1) = 0.1 x (284.84 - 234.4)

Compressor Power input = 5.044 kW

----------------------------------------------------------

C)

Evaporator cooling load = m(refrigerant) x (h1 - h4)

where

  • m(refrigerant) = 0.1 kg/s
  • h4 = h3 (because of isenthalpic expansion in throttle valve) = hf (at 0.7 MPa) = 88.82 kJ/kg
  • h1 = 234.4 kJ/kg

Evaporator cooling load = m(refrigerant) x (h1 - h4) = 0.1 x (234.4 - 88.82)

Evaporator cooling load = 14.558 kW

----------------------------------------------------------

D)

Coefficient of Performance = \mathbf{COP}=\frac{Refrigeration\: \: load}{Compressor\: \: work}=\frac{14.558}{5.044}=\mathbf{2.886 }

----------------------------------------------------------

E)

We can get the steam quality by equating the enthalpy at the condenser outlet (h3) and enthalpy at the evaporator inlet (h4) because of isenthalpic expansion, these two values are the same.

h4 = h3 (because of isenthalpic expansion in throttle valve) = hf (at 0.7 MPa) = 88.82 kJ/kg

But, h4+hf+x\times (hg-hf)

where

  • hf = hf (at 0.1 MPa) = 17.28 kJ/kg
  • hg = hg (at 0.1 MPa) = 234.4 kJ/kg

Therefore, h4+hf+x\times (hg-hf)

88.82=17.28+x\times (234.4-17.28)=>\mathbf{Quality = x = 0.3295}

----------------------------------------------------------

F)

The cooling load obtained in (C) is 14.558 kW.

We are using this cooling load for 30 mins ( = 30 x 60 = 1800 seconds).

Thus, net cooling energy is 14.558 x 1800 = 26204.4 kJ

This causes the temperature of the room to fall by 20 C.

Net cooling energy = m x Cp x Temp. Change

where

  • m = mass of air in the room = ?
  • Cp = 1.005 kJ/kgK (given)
  • Temp. Change = 20 C

Net cooling energy = m x Cp x Temp. Change

26204.4 = m x 1.005 x 20 => mass of air in the room = m = 1303.7014 kg

Now, we know, Volume=\frac{m}{Density}

where

  • m = mass of air in the room = 1303.7014 kg
  • Density = 1.2 kg/m3 (given)

Volume=\frac{m}{Density}=\frac{1303.714}{1.2}=>\mathbf{Volume=1086.417 m^{3}}

--------------------------------------------------------

Kindly upvote if you are satisfied with my efforts. :)

Add a comment
Know the answer?
Add Answer to:
A refrigerator is operating between a high pressure of 0.7 MPa and low pressure of 0.1 MPa
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Similar Homework Help Questions
  • A refrigeration system with a flash chamber operates with R134a between the pressure limits of 1.0 and 0.1 MPa. Th...

    A refrigeration system with a flash chamber operates with R134a between the pressure limits of 1.0 and 0.1 MPa. The refrigerant leaves the condenser as saturated liquid and is throttled to a flash chamber operating at 0.5 MPa. The refrigerant leaving the low-pressure compressor at 0.5 MPa is also routed to the flash chamber. The vapor in the flash chamber is then compressed to the condenser pressure by the high-pressure compressor, and the liquidis throttled to the evaporator pressure. Assume...

  • 1) A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated...

    1) A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated space at -30°C by rejecting its waste heat to cooling water that enters the condenser at 16 °C at a rate of 0.25 kg/s and leaves at 26°C. The refrigerant enters the condenser at 1.2 MPa and 65°C and leaves at 42°C. The inlet state of the compressor is 60 kPa and -34°C and the compressor is estimated to gain a net heat of...

  • Pressure limits in a two-stage cooling system are 0.9 MPa and 250kPa. Refrigerant condenser comes out...

    Pressure limits in a two-stage cooling system are 0.9 MPa and 250kPa. Refrigerant condenser comes out as saturated liquid and works at 700kPa pressure reduced to the pressure of the evaporation chamber. Meanwhile, some of the refrigerant evaporates and is mixed with the fluid from the low pressure compressor. The mixture is then It is compressed to condenser pressure with high pressure compressor. The liquid in the evaporation chamber is reduced to evaporator pressure and draws heat from the cooled...

  • Problem #4 (20 points) A commercial refrigerator with refrigerant-134a as the working fluid is used to...

    Problem #4 (20 points) A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated space at -30°C by rejecting its waste heat to cooling water that enters the condenser at 18°C at a rate of 0.25 kg/s and leaves at 26°C. The refrigerant enters the condenser at 1.2 MPa and 65°C and leaves at 42°C. The inlet state of the compressor is 60 kPa and-34°Cand the compressor is estimated to gain a net heat of...

  • Refrigerant-134a enters the compressor of a refrigerator as superheated vapor at 0.14 MPa and -10°C at a rate of 0.124...

    Refrigerant-134a enters the compressor of a refrigerator as superheated vapor at 0.14 MPa and -10°C at a rate of 0.124 kg/s, and it leaves at 0.7 MPa and 50°C. The refrigerant is cooled in the condenser to 24°C and 0.65 MPa, and it is throttled to 0.15 MPa. Disregarding any heat transfer and pressure drops in the connecting lines between the components, determine (a) the rate of heat removal from the refrigerated space and the power input to the compressor...

  • 4. The following test data were obtained from a R134A vapour-compression refrigeration system Condenser pressure Evaporator...

    4. The following test data were obtained from a R134A vapour-compression refrigeration system Condenser pressure Evaporator pressure Temperature at compressor inlet Temperature at compressor outlet Temperature at condenser inlet Temperature at condenser outlet Temperature at expansion valve inlet 30 Temperature at evaporator outlet 0.9 MPa 0.6 MPa 30 C 120 C 110 C 25 C 20 °C During compression, 3.5 kJ/kg was transferred from the fluid. Determine the coefficient of performance and perform an energy balance on the system

  • Pressure limits in a two-stage cooling system are 0.9 MPa and 250kPa. Refrigerant condenser comes out...

    Pressure limits in a two-stage cooling system are 0.9 MPa and 250kPa. Refrigerant condenser comes out as saturated liquid and works at 700kPa pressure reduced to the pressure of the evaporation chamber. Meanwhile, some of the refrigerant evaporates and is mixed with the fluid from the low pressure compressor. The mixture is then It is compressed to condenser pressure with high pressure compressor. The liquid in the evaporation chamber is reduced to evaporator pressure and draws heat from the cooled...

  • ycles 1. A refrigeration system operates with a superheated cycle using R134a. The required refrigerating capacity...

    ycles 1. A refrigeration system operates with a superheated cycle using R134a. The required refrigerating capacity is 30 TR. The evaporator works at -10 Cand the condenser pressure is 1 MPa. The refrigerant is superheated by 10°C before entering to the compressor. Assume isentropic compression in the compressor and isenthalpic expansion in the expansion valve. Answering the following questions using the ph diagram. and the c Sion in the ring to a) Sketch the process in the p-h diagram and...

  • Refrigeration Question 1 a) A refrigerant R134a refrigerator is to maintain the refrigerated spac...

    Refrigeration Question 1 a) A refrigerant R134a refrigerator is to maintain the refrigerated space at -100C. Would you recommended an evaporator pressure of 1.6 bar or 2 bar for this system? Why? -la An automotive Air conditioner using refrigerant R134a as the working fluid and operating on ideal vapor compression refrigerant cycle is to maintain a space at 24°C while operating its condenser at 1000 kPa. Determine the COP of the system when a temperature difference of 14°C is allowed...

  • Warm region H The compressor of the vapor-compression refrigerator takes in 0.2 kg/s of R134a as...

    Warm region H The compressor of the vapor-compression refrigerator takes in 0.2 kg/s of R134a as a saturated vapor at 100 kPa. It has a compression ratio of 10 and an isentropic efficiency of 85%. The fluid exits the condenser with a temperature of 35°C. a. Calculate the COP b. Find the power used by the compressor (kw) c. Determine the entropy change across the valve (kJ/kgK). d. Draw the T-s diagram. 1. Condenser Expasion Compressor device Evaporator Cold region...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT