The per phase parameters for a 60 Hz, 200 km long transmission line are R =...

The per phase parameters for a 60 Hz, 200 km long transmission line are R = 2.07 Ω, L = 310.8 mH, and C = 1.4774 µF. The line supplies a 100 mW, Y-connected load at 215 kV (line-to-line) and 0.9 power factor lagging.

Solve the problem treating it as a two port network.(A, B,C, D constants).

Answers should be: [A = D = 0.967<0.0340 , B = (117.19<99.090) Ω, C = (5.54 x 10-4<-89.960 ) S, 139.32 kV / phase]

0 0
Add a comment Improve this question Transcribed image text
Know the answer?
Add Answer to:
The per phase parameters for a 60 Hz, 200 km long transmission line are R =...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A 60 km-long three-phase 60-Hz transmission line has per phase line inductance of 1.554 mH/km and...

    A 60 km-long three-phase 60-Hz transmission line has per phase line inductance of 1.554 mH/km and per phase line resistance of 10.33 mΩ/km. It supplies a three-phase Y connected 100 MW 0.9 lagging power factor load at 215 kV line-line voltage. Calculate the voltage regulation and efficiency of transmission.

  • A 3-phase 60 Hz 50 km transmission line delivers 20 MW of power to a load...

    A 3-phase 60 Hz 50 km transmission line delivers 20 MW of power to a load at 69 kV and a power factor of 0.8 lagging. The line has the following parameters r = 0.1112/km L = 1.11 mH/km C = negligible Determine: The line impedance. (4 Marks) The "receiving end" phase voltage and current (7 Marks) The "sending end" voltage and current (10 Marks) The voltage regulation. (4 Marks)

  • PROBLEM: A 230-kV, 50 Hz, three-phase transmission line is 120 km long. The line has a per phase ...

    PROBLEM: A 230-kV, 50 Hz, three-phase transmission line is 120 km long. The line has a per phase series impedance of z-0.05 +j0.45 Ω per km, and a per phase shunt admittance of y 3.4x10-6 Siemens per km. The line delivers (at the receiving end) 200 MVA, 0.8 lagging power factor at 220 kV. Now consider two cases: A- Assume that shunt parameters of the transmission line are ignored (i.e. even if this is a medium length transmission line, under...

  • A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters...

    A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters of r = 0.09 Ohm/km, x = 0.88 Ohm/km, y = 4.1 * 10^-6 s/km. Calculate the ABCD constants of this transmission line. What is the sending end voltage if the line is supplying rated voltage and apparent power at 0.85 PF lagging? What is the voltage regulation of the transmission line for the conditions in question 11. What is the efficiency of the...

  • A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters...

    A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters of r = 0.09 ohm/km, x = 0.88 ohm/km, y = 4.1 * 10^-6 S/km. 10. Calculate the ABCD constants of this transmission line. 11. What is the sending end voltage if the line is supplying rated voltage and apparent power at 0.85 PF lagging? 12. What is the voltage regulation of the transmission line for the conditions in question 11. 13. What is...

  • Phase of a three-phase, 60 Hz, 300 km long power transmission line with a nominal operating...

    Phase of a three-phase, 60 Hz, 300 km long power transmission line with a nominal operating line voltage of 500 kV. its inductance per 291 mH/phase, and its capacitance is 3.45uF/phase. Voltage between 500 kV phases from the end of the energy transmission line Under it, a load of 1000 MVA is fed with a power factor of 0.8 back. Power transmission line lossless assumption. This according to the operating conditions, a.) The line's phase constant (61), characteristic impedance (ZC)...

  • Problem #1: A single-circuit, 500 kV, 60 Hz, three-phase transmission line is 250 km long. The...

    Problem #1: A single-circuit, 500 kV, 60 Hz, three-phase transmission line is 250 km long. The characteristic parameters of the transmission line are: x0.4 0/km At full load, the line delivers 1000 MVA at 500 kV with 0.80 PF lagging y j4 x 10 S/km r0.045 /km a. Assume that identical shunt reactors (inductors) are connected from each phase conductor to neutral at both ends of the line during light-load conditions, providing 50% total shunt compensation. The reactors are removed...

  • A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters...

    A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters of r = 0.09 Ohm/km, x = 0.88 Ohm/km, y = 4.1*10^-6 S/km. What is the sending end voltage if the line is supplying rated voltage and apparent power at 0.85 PF lagging? What is the voltage regulation of the transmission line for the conditions in question 11.

  • Problem 2: A 345 kV, 60 Hz, three-phase characteristic parameters of the transmission line are: transmission...

    Problem 2: A 345 kV, 60 Hz, three-phase characteristic parameters of the transmission line are: transmission line is 130 km long. The r= 0.036 ?/km L = 0.8 x 10-3 H/km C = 0.0112 x 10-6 F/km The receiving end load is 270 MVA with 0.8 PF lagging at 325 kV. (k) What is the total series impedance of this transmission line? (5 points) () What is the total shunt admittance of this transmission line? (5 points) (m) Calculate the...

  • A 200-km, 230-kV, 60-Hz three-phase line has a positive-sequence series impedance ?=0.08+?0.48 Ω/km and a positive-sequence...

    A 200-km, 230-kV, 60-Hz three-phase line has a positive-sequence series impedance ?=0.08+?0.48 Ω/km and a positive-sequence shunt admittance ?=?3.33×10−6 S/km. At full load, the line delivers 250 MW at 0.99 pf lagging and at 220 kV. Using the nominal ? circuit, calculate: a. The ABCD parameters, b. The sending-end voltage and current, c. The percent voltage regulation.

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT