The following readings were taken during an open-circuit test and short-circuit test on a three-phase, 10 MVA, 13.8 kV, 50 Hz synchronous generator driven at rated speed. Open Circuit Test Field Current 150 A 180 A 200 A 250 A 300 A 350 A Line voltage 11.2 kV 12.0 kV 12.5 kV 13.5 kV 14.3 kV 14.8 kV Short Circuit Test Field Current 150 A 180 A Short Circuit Current 400 A 480 A a) Plot the open-circuit and short-circuit characteristics on the same graph and determine the saturated synchronous reactance of the generator. b) If the generator delivers rated kVA to a load at rated voltage and 0.8 pf lagging, use the saturated synchronous reactance to determine the required excitation voltage E and load angle d. c) If the generator excitation is reduced to 80% of its value in part b), find the new load angle assuming the real power is unchanged.
The following readings were taken during an open-circuit test and short-circuit test on a three-phase, 10...
09C6 p.): The Open Circuit and the Short Circuit characteristics of a 14.1-KV 30-MVA synchronous generator are given in the tables shown. Calculate (a) the unsaturated synchronous reactance, (b) the saturated synchronous reactance. Open-circuit test Field current, A Line voltage, KV Extrapolated air gap voltage, KV Short-circuit test Field current, A Armature current, A 275 12.2 1 3.3 320 13.0 15.4 365 13.8 17.5 380 14.1 18. 3 475 | 15.2 22.8 570 16.0 27.4 275320365 890 1040 1190 380...
a. The figure below is a set of Synchronous Generator and Synchronous Motor. The ratings of the machines are as follows: Synchronous Generator:. 3ph, 1.0MVA, 2.3kV, 50Hz, 0.85 lagging power factor, X.=0.9 pu Synchronous Motor: 3ph, 0.5 MVA, 2.36V, 50Hz, 0.85 leading power factor, X.=0.8 pu Synchronous generator Synchronous motor The generator is equipped with a voltage regulator which maintains the terminal voltage at the rated value. The motor delivers 500 hp and it field current is adjusted to make...
Problem 2. [20 PT] A 25 MVA, three phase, 13.8 KV, A-connected, two pole, 60 Hz synchronous generator was tested by open circuit and short circuit tests and following data was collected. Neglect the stator resistance for this question: Open Circuit Characteristics Line Voltage, KV 13.0 13.8 15.2 16.0 Field Current, A 320 365 380 475 570 14.1 Short Circuit Characteristics Field Current, A 320 Armature Current, A 1046 365 380 475 570 1190 1240 1550 1885 Compute a) [10...
A 12 kV, 300 MVA synchronous generator is tested at a field current of 200 A. The open-circuit voltage was found to be 10 kV and the short-circuit current was 7.5 kA. The stator resistance was measured at 0.1 ohms per phase. i) Find the value of the synchronous reactance in per-unit. [ 2 marks ] ii) The synchronous generator is delivering half rated output at a terminal voltage of 5% below rated voltage and a power factor of 0.7...
HOMEWORK PROBLEMS Q1: Repeat all part of the problem in the "Class Activity" if the generator is Delta connected Q2: For the "Class Activity" problem what is the efficiency of this generator if it is loaded by a 500 kVA pure resistive load (at the same rated voltage and frequency) Q3: A 13.8-kV 10-MVA 0.8-PF-lagging 60-Hz two-pole Y-connected steam-turbine generator has a synchronous reactance of 12 Ω per phase and an armature resistance of 1.5 Ω per phase. (a) What...
4. Synchronous generator DC test, open circuit test and short circuit test are done to a 240V, 60Hz, Wye-connected, 12-pole synchronous generator. The test results are shown below: DC test: Line-to-line voltage: 15V Line current: 45A OC test: Field current (W): 5A Line-to-line voltage: 240V SC test: Field current (l): 5A Line current: 68.514A Per-phase Reactance Xs: 22 a. Determine the per-phase model resistance R for the synchronous generator and draw the 3- phase model of this generator labeled with...
A three-phase synchronous generator with rated data VM = 20 kV, SM = 100 MVA, n = 500 rpm is driven by a turbine that can provide a maximum of 1.6 MNm. Synchronous reactance, XS = 3Ω / phase. The armature resistance (Ra ) is neglected. In open circuit mode (P = 0), an excitation current of 300 A is required to obtain rated voltage (VM ). The machine should be phased into a strong grid, 3x20 kV, 50 Hz....
Q2) A 13.8-kV, 50-MVA, 0.9-power-factor-lagging, 60-Hz, four-pole Y-connected synchronous generator has a synchronous reactance of 2.5 Ω and an armature resistance of 0.2 Ω At 60 Hz, its friction and windage losses are 1 MW, and its core losses are 1.5 MW. The field circuit has a de voltage of 120 V, and the maximum , is 10 A. The current of the field circuit is adjustable over the range from 0 to 10 A. The OCC of this generator...
A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.5Q/phase and a synchronous reactance of 5Q/phase. The generator is supplying its rated power at its rated voltage and at a power factor lagging. The rotational loss is 2 kW. Calculate: (a) the power developed, (b) the power angle, (c) the voltage regulation, and (d) the shaft torque. A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.50/phase and a synchronous...
Question 4 (10 marks) A) A 10-kVA, 415-V, three phase, Y -connected synchronous generator has a winding resistance of 0.3 Q and a synchronous reactance of 0.6 on a per phase basis. Determine its voltage regulation at full load when the power factor is (a) 75% lagging and (b) 75% leading. B) (10 marks) A 220-V, Y-connected, three-phase, synchronous motor has a synchronous reactance of 4 O/phase and negligible armature winding resistance. At a certain load the motor takes 7.5...