Simple AC circuit problem (I WILL DOWNVOTE IF YOU DO NOT EXPLAIN WHERE I AM GOING...

Simple AC circuit problem (I WILL DOWNVOTE IF YOU DO NOT EXPLAIN WHERE I AM GOING WRONG).

Problem: Obtain the overall impedance Z given the following info: Real Power = 1000 W, Power Factor = 0.8 leading, Vrms = 220 V

I am doing the following:

Get the power angle phi by taking the inverse cosine of Power Factor. phi = 36.87 degrees.

From the power triangle, Q = (Real Power) x tan(phi). Q = 750.

S = P + jQ. So then S = 1000 + j750

We know S = VrmsI*rms (here * means complex conjugate).

Find I*rms.

From this, easily get Irms.

Z = Vrms / Irms.

But my answer is coming out wrong. And I don't know why.

0 0
Add a comment Improve this question Transcribed image text
Know the answer?
Add Answer to:
Simple AC circuit problem (I WILL DOWNVOTE IF YOU DO NOT EXPLAIN WHERE I AM GOING...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • The three figures below show a balanced three phase Delta, its Wye equivalent and the single...

    The three figures below show a balanced three phase Delta, its Wye equivalent and the single phase equivalent of the three phase Wye. All three representations have a complex load ZALD or ZYLD and a complex line impedance ZLINE Refer to these diagrams when answering questions 1-4. ZLINE Vab= 679 L 30° ZLINE ZALD ZLINE = 2+1 DELTA ZALD= 18+24j2 LINE ZLINE ZLINE ZYLD 7yun WYE WYE ZYLD ZLINE ZLINE Van Complex Load ZYLD Single Line WYE 1) In the...

  • Good day all. I am facing the following problem and would like to seek some kind...

    Good day all. I am facing the following problem and would like to seek some kind help, please. Sincerely appreciate all help and input. - Ms Tan 1. An 10 MVA, 33 kV, 34 pole, 60 Hz, three-phase wye-connected synchronous generator has a synchronous reactance of 10 and a negligible armature resistance. a. Find the synchronous speed of this generator. b. At a certain excitation, the generator delivers 50% of rated load at 0.7 leading power factor at '33' kV....

  • I only need help with the discussion there are many info that you do not need put I put just in ...

    I only need help with the discussion there are many info that you do not need put I put just in case as well as my data table. please do it as soon as u can Meauements ODeit1 Check2 Meaurements Checi3 Ced Check5 Check6 Measurements Check7 heck8 4058 33 536 1502 1035 979 119478 041 1.0319|0.554972| 64261| 153|15542033681 995781 5266566 1578807 298h 1631 119 1209430016 079096812 0.418135246 0,00032665 011890:004668155728441 0293237 1.291809502 1.22833 1.28 1952 -1116 4281 140616885511984206317 3346 8162 0.78...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT