a 270-mile transmission line has 220KV, 3 phase, 60 cps, between
conductors at the supply station end. The impedance, z =
0.18+j0.842 ohms per mile. The admittance, y = j5.01x10^-6 ohms per
miles. Find the following:
a. Find the ABCD constant of the line
b. What is the voltage at the load end when the line has no load
and the charging current.
c. What is the Vs and Is for a load of 125 MW at 200KV and 0.866
lagging P.F.
a 270-mile transmission line has 220KV, 3 phase, 60 cps, between conductors at the supply station...
#2. A 3-phase, 60-Hz transmission line is 140 miles long and has r :0.30 Ohms/mile, x =1.5 Ohms/mile, and the shunt admittance is 7.8 x 100900 mho /mile. The load at the receiving end of the line is 36 MVA at 220 kV and a power factor of 0.90 lagging (i)Find the ABCD parameters of the line. (i)Find the sending end phasor voltage, Vs and phasor current, Is iv)What is the real power, P and the reactive power Q at...
Question: A three-phase, 60-Hz, completely transposed transmission line has a length of 100-km and has a series impedance per phase of (0.25+j0.85) ohms/mile and shunt admittance of 5.0*10^-5 Siemens/mile. The transmission line delivers 150 MW at 0.85 lagging power factor to a load connnected to its receiving end. The line-to-line voltage at the receiving end is 138-kV. Note: The Medium Length Line method should be used since it is used for distances between 50 miles to 150 miles. Determine the...
Show the solution for the following problem 1. A short, 230 kV transmission line has an impedance of 5 cis 78 ohms. The load at the receiving end is 100 MW at 230 kV, 85% lagging power factor. What is the voltage at the sending end? a. 235.43 kV b. 226.3 kV c. 231.78 kV d. 238.21 kV 2. A 66 kv medium length transmission line delivers a load of 10 MW at 66 kv and 80% lagging P.F. the...
power system A single-circuit 60-Hz high voltage power transmission line is 370 km (230 mi) long. The conductors are Rook with flat horizontal configuration and 7.25 ms=(23.8 ft.) conductor spacing. The load on the line is 125 MW at 100% power factor. Use attached Tables A3 to A3to determine; The sending end voltage Vs The sending end current Is The sending end power Ps The percentage voltage regulation The transmission efficiency Given that Ds for the Rook conductor is 0.0327...
A short 3-phase, 33-kV power transmission line delivers a load of 7-MW at a power factor of 0.85 lagging and 33-kV. If the series impedance of the line is 20+j30 Ohms/phase, calculate The ABCD constants (parameters) The sending end voltage The load angle The voltage regulation The transmission efficiency
Problem 3: A three-phase, 60 Hz transmission line is built with an ACSR conductor. The conductor diameter is 0.68 inch, GMR = 0.023 ft., and AC resistance of 0.342 /mile at 50°C. The conductors are laterally spaced with D= 1.7 m between conductor centers. The line is 50 km long and supplies a 5 MW load. The line to line load voltage is 13.2 kV. [40 points] (a) Find the total impedance of the line. (b) Determine the sending-end voltage,...
Problem 2: A 345 kV, 60 Hz, three-phase characteristic parameters of the transmission line are: transmission line is 130 km long. The r= 0.036 ?/km L = 0.8 x 10-3 H/km C = 0.0112 x 10-6 F/km The receiving end load is 270 MVA with 0.8 PF lagging at 325 kV. (k) What is the total series impedance of this transmission line? (5 points) () What is the total shunt admittance of this transmission line? (5 points) (m) Calculate the...
A 230-kV, three-phase transmission line has a per phase series impedance of z = 0.05j0.45 2 per km and a per phase shunt admittance ofy = j3.4 x 10-6 siemens per km. The line is 80 km long. Using the nominal r model, determine (a) The transmission line ABCD constants. Find the sending end voltage and current, voltage regulation, the sending end power and the transmission efficiency when the line delivers (b) 200 MVA, 0.8 lagging power factor at 220...
4. A 500 km, 500kV,60 Hz three-phase transmission line has a positive sequence series impedance z =j 0.38.2/km and a shunt admittance y =j 4.0 x 10-6S/km. Line losses are neglected. a. Calculate the line's characteristic impedance Zc, the propagation constant y and the exact ABCD parameters of the line... b. Calculate the surge impedance loading (SIL) in MW and the maximum power that the line can deliver at rated voltage C. At full load the line delivers 1000 M...
2) A 50 Hz transmission line 300 km long has a series impedance of 40 j125 ohms and a total shunt admittance of 103 S. The load draws 500 MW at 220 kV with 0.8 pf lagging. Find the sending end voltage using (a) Short line approximation and (b) Nominal π method.