1. Calculate the VA output required from a current transformer of 5A rated secondary current when the burden consists of relays requiring 10VA at 5A plus a loop lead resistance of 0.8 ohms.
2. What output VA would be required from a current transformer of 1A rated secondary current for a burden of 10VA at 1A plus lead resistance as in part 1.
3. An earth fault relay has a burden of 1VA at setting and is set at 0.2A. What output voltage must a current transformer produce to ensure linear operation of the relay at 20 times setting? Assume that ct plus lead resistance is 1.5 ohms and that the relay coil impedance saturates to 1/2 its unsaturated value at 20 times setting.
1. Calculate the VA output required from a current transformer of 5A rated secondary current when...
A 400:5 CT with a secondary resistance of 0.211 ohms is used as part of an over-current relay. The pick-up current setting for the relay is 5 A. 7e What is the minimum line current required to trip the relay if a burden impedance of 0.5 ohms is used? a) b) What is line current required to saturate the CT? A 400:5 CT with a secondary resistance of 0.211 ohms is used as part of an over-current relay. The pick-up...
Problem #1 A multi-ratio current transformer with the following ratios (1200:5, 1000/5, and 800:5) high permeability silicon steel has a cross sectional area of 3.5 square-inches and a secondary resistance winding of 0.29 Ohms. The maximum current for which the transformer will operate is 35kA at 60 Hz. The relay burden including the leads is 2.2 Ohms. Using the formula method determine if the CT will saturate at the three given rations (CT saturation density)
1. (a) State briefly the consequences of opening the secondary of a current transformer when it is in service. State the precaution to be taken should disconnection be necessary. (b) A CT has a current ratio of 100/1. If the primary load current is 100 A, determine the excitation current, the maximum ratio error and the maximum phase angle error if the burden is 5 ohms. The CT characteristic gives an excitation current of 0.014 A for a secondary voltage...