Ans a) Floor plate area = 200 x 175
= 35000 ft2
Given that per ft2 required 1 ton, hence 35000 ft2 require : 35000/350 ton
= 10 ton per floor
For 10 story , chiller ton = 10 x 10
= 100 ton
Ans b) Chiller ton = GPM x /24..........(1)
Cooling tower ton = GPM x /30...........(2)
From eqn 1 ,
GPM x =24 x 10
Cooling tower ton = 24 x 10 /30
= 8 ton /floor
For 10 story , chiller ton = 8 x 10
= 80 ton
Ans c) Total volume of single story = 200 x 175 x 12
= 420000 cfm
Assume one AHU of 60000 cfm
Number of AHU required = 420000/60000
= 7 units
Ans d) Assume total dynamic head as 60 ft and flow as 4 gallon/min
Pump power required = gQh
=1000 x 9.81 x 18.75 x 0.000252
= 463.52 W