QUESTION 1 A rooftop unit exhausts return air from the space to outdoors exhaust? Assume the COP ...
QUESTION 1 A rooftop unit exhausts return air from the space to outdoors exhaust? Assume the COP for the unit is 3.0 and that electricity costs are $0.10/kWh. Properties of air: density o and replaces it with 7,364 CFM of fresh air. THe exhausted air is at 77F and the fresh 89F. If ths unit is cooling for 2,579 hours each year, what annual savings, in dollars, is possible by cooling the fresh 0743 ib/t3, cp 0.24 Btu/1bm-F
QUESTION 1 A rooftop unit exhausts return air from the space to outdoors exhaust? Assume the COP for the unit is 3.0 and that electricity costs are $0.10/kWh. Properties of air: density o and replaces it with 7,364 CFM of fresh air. THe exhausted air is at 77F and the fresh 89F. If ths unit is cooling for 2,579 hours each year, what annual savings, in dollars, is possible by cooling the fresh 0743 ib/t3, cp 0.24 Btu/1bm-F