Question 5 4 pts You are considering the purchase of a heat pump system. It will contain a resistive heating element in the alr-handler for back-up during the extra cold winter months when the te...
Question 5 4 pts You are considering the purchase of a heat pump system. It will contain a resistive heating element in the alr-handler for back-up during the extra cold winter months when the temperature is below the heat pump's capability. The manufacturer's technical data states the maximum current draw for the unit you are looking at b 34 amps at 240 volts, 1 phase. The circuit breaker that you would have to Install to carry this resistive load is: 。45 amp), 2-pole 〇20amp, 2 pole O 25 amp 2 pole O 40 amp, 1-pol 。30ames,1-pole Previous
Question 5 4 pts You are considering the purchase of a heat pump system. It will contain a resistive heating element in the alr-handler for back-up during the extra cold winter months when the temperature is below the heat pump's capability. The manufacturer's technical data states the maximum current draw for the unit you are looking at b 34 amps at 240 volts, 1 phase. The circuit breaker that you would have to Install to carry this resistive load is: 。45 amp), 2-pole 〇20amp, 2 pole O 25 amp 2 pole O 40 amp, 1-pol 。30ames,1-pole Previous