4. B
At least 150 mm (6 in.) of free conductor, measured from the point
in the box where it emerges from its raceway or cable sheath, shall
be left at each outlet, junction, and switch point for splices or
the connection of luminaires or devices.
Code Reference: 300.14
5. E.
Switch loops are used where the installation uses multi color
cable.Article 200.7(C)(2) permits a white or gray conductor to be
reidentified as an ungrounded conductor at all locations where the
conductor is visible. The re-identified white conductor is also
required to be the feed, supplying the source of power to the
switch. Under no circumstances is it permitted to be the switched
return conductor to the load.
Code Reference: 200.7
dwelling un 4. Type NM-B Cable enters a metal device box and is secured by a cable clamp at the bottom of the box....
pleas help me in this do any question you know using National Electrical Code 2011 Applied Electricity NEC worksheet t hree Copper conductors with THHN insulation run in Electrical A branch-circuit Consther conductors. The conductor terminations are rated for a maximum ure in the area of this installation is not expected to exceed 30C size 8 AWG, the maximum ampacity of the conductors If the conductors for this circuit are permitted A 40 amperes. B. 50 amperes. to be used...
can anyone help me with this test please? I'm struggling with it QUESTION 1 A permanently installed overhead strip light is a ____. a.foot light b.track light c.border light d.head light QUESTION 2 Egress lighting for carnivals, circuses and fairs shall not ____. a.contain metal raceways b.be integrated into a central switchboard c.contain branch circuits d.be protected by a GFCI protection device QUESTION 3 The attachment plug cap in a mobile home shall be a ____, rated 50...