Question

A heat pump with refrigerant-134a as the working fluid is used to keep a space at 25°C by |absorbing heat from geotherm...

A heat pump with refrigerant-134a as the working fluid is used to keep a space at 25°C by |absorbing heat from geothermal water that enters the evaporator at 50°C at a rate of 0.046 kg/s and leaves at 40°C. The refrigerant enters the evaporator at 20°C with a quality 23 percent and leaves at the inlet pressure as saturated vapor. The refrigerant loses305 W o heat to the surroundings as it flows through the compressor and the refrigerant leaves the compressor at 1.4 MPa at the same entropy as the inlet.


Determine: 

(a) the degrees of subcooling of the refrigerant in the condenser

(b) the mass flow rate of the refrigerant

(c) the heating load and the COP of the heat pump, 

and (d) the theoretical minimum power input to the compressor for the same heating load

image.png


6 0
Add a comment Improve this question Transcribed image text
✔ Recommended Answer
Answer #1

Fm t givn dota atfurme L4MPa S2 edy opecating Candansov 2 Coditng erpaninX 4 Valua EVapah aue Megligible fat ap akrV4ic Tu20Hat loa Q af Cop Q = MR(h-ha) -) 0 070(230-12 24) Qr= 445k inMe (b-ha)tQout = 0-0230(280-261-5V+050 COf-t Cop : S.8 M poLser

Kindly upvote if it's helpful for you .

Add a comment
Know the answer?
Add Answer to:
A heat pump with refrigerant-134a as the working fluid is used to keep a space at 25°C by |absorbing heat from geotherm...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Similar Homework Help Questions
  • QUESTION 1 A heat pump with refrigerant-134a as the working fluid is used to keep a...

    QUESTION 1 A heat pump with refrigerant-134a as the working fluid is used to keep a space at 25°C by absorbing heat from geothermal water that enters the evaporator at 50°C at a rate of 0.065 kg/s and leaves at 40°C. The refrigerant enters the evaporator at 20°C with a quality of 23 percent and leaves at the inlet pressure as saturated vapor. The refrigerant loses 300 W of heat to the surroundings as it flows through the compressor and...

  • 1) A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated...

    1) A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated space at -30°C by rejecting its waste heat to cooling water that enters the condenser at 16 °C at a rate of 0.25 kg/s and leaves at 26°C. The refrigerant enters the condenser at 1.2 MPa and 65°C and leaves at 42°C. The inlet state of the compressor is 60 kPa and -34°C and the compressor is estimated to gain a net heat of...

  • A compressor of a heat pump with refrigerant-134a as the working fluid consumes 2.3 kW of...

    A compressor of a heat pump with refrigerant-134a as the working fluid consumes 2.3 kW of power is used to keep a space at 25°C by absorbing heat from geothermal water that enters the evaporator at 60°C at a rate of 0.065 kg/s and leaves at 50°C. Refrigerant ententhe evaporator at 30Cwithaqualityof 15 percent and leaves atthe same pressure as saturated vapor. determine the mass flow rate of the refrigerant

  • Problem #4 (20 points) A commercial refrigerator with refrigerant-134a as the working fluid is used to...

    Problem #4 (20 points) A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated space at -30°C by rejecting its waste heat to cooling water that enters the condenser at 18°C at a rate of 0.25 kg/s and leaves at 26°C. The refrigerant enters the condenser at 1.2 MPa and 65°C and leaves at 42°C. The inlet state of the compressor is 60 kPa and-34°Cand the compressor is estimated to gain a net heat of...

  • In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating...

    In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating at a rate of 15 kW to maintain a building at 20 °C year-round. During the heating mode in the winter, the outside temperature is 5 °C. It is also used for cooling in the summer when outside temperature is 34 °C. Saturated vapor at 2.4 bar leaves the evaporator and superheated vapor at 8 bar leaves the compressor. There is no significant heat...

  • In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating...

    In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating at a rate of 15 kW to maintain a building at 20 °C year-round. During the heating mode in the winter, the outside temperature is 5 °C. It is also used for cooling in the summer when outside temperature is 34 °C. Saturated vapor at 2.4 bar leaves the evaporator and superheated vapor at 8 bar leaves the compressor. There is no significant heat...

  • In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating...

    In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating at a rate of 15 kW to maintain a building at 20 °C year-round. During the heating mode in the winter, the outside temperature is 5 °C. It is also used for cooling in the summer when outside temperature is 34°C. Saturated vapor at 2.4 bar leaves the evaporator and superheated vapor at 8 bar leaves the compressor. There is no significant heat transfer...

  • A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated space...

    A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated space at −25°C by rejecting waste heat to cooling water that enters the condenser at 20°C at a rate of 0.25 kg/s and leaves at 26°C. The refrigerant enters the condenser at 1.2 MPa and 50°C and leaves at the same pressure subcooled by 5°C. If the compressor consumes 3.3 kW of power, determine (a) the mass flow rate of the refrigerant, (b) the refrigeration...

  • value 10.00 points Question An air-conditioner with refrigerant-134a s the working fluid is used to keep...

    value 10.00 points Question An air-conditioner with refrigerant-134a s the working fluid is used to keep a room at 21°C-Ass by rejecting the waste heat to the outdoor air at 37°C. The room gains heat through the walls and the windows at a rate of 249 kJ/min while the heat generated by the computer, TV, and T lights amounts to 600 W. The refrigerant enters the compressor at 360 kPa as a saturatedV vapor at a rate of 100 L/min...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT