4. A W12x50 beam acts compositely with a 4.5-inch concrete slab. The effective slab width is 70 inches. Shoring is not used. Applied bending moments are as follows: from the beam, Mbeam = 14 ft-kips; from the weight of slab, Msiab-78 ft-kips; and from the live load, M1-150 ft kips. Steel is A992, the compressive strength of concrete at 28 days is 4ksi. Determine whether the flexural strength of this beam is adequate. Assume full composite action and assume that the formwork provides lateral support of the W12x50 before curing of the concrete. Use LRFD.
0 0
Add a comment Improve this question Transcribed image text
Answer #1

Given beam is W12x50

Area of steel =14.7 in2

effective width of concrete = 70 inches

thickness of slab = 4.5 in

maximum tension in steel = 50*14.7=735 kips

maximum compression in concrete = 0.85*4*70*4.5=1071 kips

compression is greater than tension

let depth of compression zone in concrete be a

0.85*a*70*4=735

a=3 in

depth of beam =d= 12.19 in

lever arm length = d/2 + 4.5-(a/2) = 12.19/2 + 4.5 -(3/2) = 9.1 in = 0.76 ft

design moment strength of composite beam = 0.9*735*0.76=502.74 kip-ft

Design moment demand = 1.2*(14+78)+1.6*150=350.4 kip-ft

design moment is less than composite beam strength.

Therefore, section is adequate

Add a comment
Know the answer?
Add Answer to:
4. A W12x50 beam acts compositely with a 4.5-inch concrete slab. The effective slab width is...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 10, A w24x 55 floor beam supports a 4-inch-thick reinforced concrete slab with an effective width...

    10, A w24x 55 floor beam supports a 4-inch-thick reinforced concrete slab with an effective width of 78 inches. The 28-day compressive strength of the concrete is 4 ksi. a. Determine required number of anchors to make the beam fully composite. b. Calculate resisting moment of the steel beam before concrete hardens,pMn. c. Calculate resisting moment of the composite beam, Mn. d. If number of studs are reduced by 25%, determine the available flexural strength of composite beam,oMn. Calculate final...

  • Please refer AISC 15th edition 3. A composite beam consists of a concrete slab that has an effective width be 72-in...

    Please refer AISC 15th edition 3. A composite beam consists of a concrete slab that has an effective width be 72-in and a thickness t 7-in. Compressive strength of concrete is 4 ksi. The slabis connected to a A992 steel beam (W36x160) with an adequate number of steel studs to produce a fully composite beam. Determine the nominal moment strength of this beam.

  • Please refer AISC 15th edition 4. A composite floor system consists of a 5-inch slab which...

    Please refer AISC 15th edition 4. A composite floor system consists of a 5-inch slab which is supported by W14x30 beams without shoring. Fy-50 ksi, strength of concrete is 4ksi, beam spacing is 8-ft, the effective width is 81-inches, and the span is 35-ft. Construction load is 20 psf and the live load is 160 psf. Compute the maximum deflection before the concrete has cured. (credit weight 20)

  • IL. A W 14x 22 acts compositely with a 4-inch-thick floor slab whose effective width b is 90 inch...

    IL. A W 14x 22 acts compositely with a 4-inch-thick floor slab whose effective width b is 90 inches. The beams are spaced at 6 feet, and the span length is 30 feet. The superimposed loads are as follows: construction load 20psf, partition load-10psf, weight of ceiling and light fixtures-5 and live load-60 psf . A992 steel is used, and fo 4 ksi a. Compute the maximum deflection before the concrete has cured b. Compute the maximum deflection after composite...

  • Check the adequacy of a W18X35 for a beam (the beam in the vertical direction in...

    Check the adequacy of a W18X35 for a beam (the beam in the vertical direction in the plan) in a floor framing system in terms of 1) bending strength; 2) shear strength and 3) deflection. The beams support a 4-inch-thick reinforced concreted floor slab (with a density of 150 lbs/ft?). Besides the weight of the structure, loads consist of a uniform live load of 80 psf and moveable partitions (with a uniformly distributed load of 20 psf of floor surface)....

  • Based on tributary load analysis, the dead and live loads, wd and wų, respectively, acting on...

    Based on tributary load analysis, the dead and live loads, wd and wų, respectively, acting on a beam in a vertical load resisting system are shown below. The concrete is normalweight with compressive strength f=5000 psi. Note that the given dead load includes the self-weight of the beam and slab. Section wp=1.2 kip/ft, wu=1.5 kip/ft be-45 inch 5 inch 1 30 inch B A 10 inch In=10 ft 1. Design and detail the beam for positive flexure at section A....

  • 2. The composite beam cross section shown below consists of a W16 x 45 steel with...

    2. The composite beam cross section shown below consists of a W16 x 45 steel with ASTM A572 grade 50 and 4in. normal weight (145 pef) concrete slab, with 28-day strength of 3ksi. Assume full-composite action. Consider only the loads shown in the figure. b = 66 Service Leads Construction Dead Load: 0.75 k. Superimposed Dead Load: 0.25 kft. Live Load-1.1 kft. -W16 X 45 L-36-0 a) Determine the design bending strength in k-ft of the composite section using formula....

  • Problem 3 (5 points) A rectangular concrete beam of width b 24 in. is limited by architectural co...

    Problem 3 (5 points) A rectangular concrete beam of width b 24 in. is limited by architectural considerations to a maximum total depth h - 17 in. It must carry a design moment demand, M 400 kips-ft. Design the flexural reinforcement for this member. Use compression steel if needed. The concrete material has compressive strength of fe- 4 ksi. The steel conforms to ASTM A615 Gr. 60. Select reinforcement to provide the needed areas and show a sketch of your...

  • Qu estion 1: (25 points) The beam shown below has a span of 13 ft and is reinforced with bars tha...

    Qu estion 1: (25 points) The beam shown below has a span of 13 ft and is reinforced with bars that ext end 8 inch beyond the face of the support. The centerline of the longitudinal bars nearest the side ace (i.e., the "outside bars") is 3.5 inch from, the side face as shown below. The concrete has a compressive strength of 3.0 ksi, and the reinforcement is Grade 60. The beam is loaded with a distributed live load (w)...

  • Problem 1 Reinforced Concrete T-Flanged Sections (50 pts.) You are required to analyze and design...

    Problem 1 Reinforced Concrete T-Flanged Sections (50 pts.) You are required to analyze and design the propped cantilever t-section from HM 4 but for shear only. Draw shear V and moment M diagrams for uniformly distributed load throughout the 30ft span and equally concentrated loads at 10ft and 30ft. Recall that the connection at the left joint N1 is fixed. The connection at 20ft N3 is a roller. The right end node N2 is a free end. Use a concrete...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT