Question

A 50 kW load operates from a 60 Hz and 10kV line with a power factor of 0.6 lagging. Compute the capacitance that must be placed in parallel with the load to achieve 0.9 lagging power factor.

In-Class #10 Problem A 50 kW load operates from a 60 Hz and 10 kV line with a power factor of 0.6 lagging. Compute the capaci

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Page 1

P. Load power p = 50kW frealency f = 50HZ Line voltage Vc = IOKV Initial power factor (ose) = 0.6 lag New power factor Cost2

Page 2

Qc = P(tandi – tan62) = 50kw Cų - 0.4843) = 42.45 Kvar. It is known that Qc = X Qc = ULLY WC uc Qc = VLL WC с= Qс View 42.45

Add a comment
Know the answer?
Add Answer to:
A 50 kW load operates from a 60 Hz and 10kV line with a power factor...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 3) Abow load is power by a 60 Hz, 240V line. He power factor PF G...

    3) Abow load is power by a 60 Hz, 240V line. He power factor PF G 0.7071 lagging Caleulate the parallel Capacitance required to correct the power factor to 0.9 lagging

  • An induction motor draws 1.0 kW at 0.8 lagging power factor from a 250 V, 60...

    An induction motor draws 1.0 kW at 0.8 lagging power factor from a 250 V, 60 Hz source. [38] (a) What value of capacitance must be placed in parallel with the motor to raise the line power factor to 93% lagging? (b) With the capacitor in service, what are the magnitudes of the motor current, capacitor current, and line current? Solution:

  • 3 phase, 37.3 Kw, 440 V, 50 Hz induction motor operates at full load with efficiency...

    3 phase, 37.3 Kw, 440 V, 50 Hz induction motor operates at full load with efficiency 89% and power factor 0.85 lagging. Calculate: A) The total KVA rating of capacitor required to rise full load power factor to 0.95 lagging. B) What is capacitance per phase if capacitor: 1) Delta connected. 2) Star connected.

  • Two loads, A and B, are connected in parallel across a 1-kV-rms 60-Hz line, as shown...

    Two loads, A and B, are connected in parallel across a 1-kV-rms 60-Hz line, as shown in (Figure 1). Load Aconsumes 10 kW with a 60 percent lagging power factor. Load B has an apparent power of 20 kVA with an 80 percent lagging power factor. a) Find the power delivered by the source. b) Find the reactive power delivered by the source. c) Find the apparent power delivered by the source. d) What is the power factor seen by...

  • A single Phase load draws 10 kW from a 410 V line at a power factor...

    A single Phase load draws 10 kW from a 410 V line at a power factor of 0.707 lagging. Determine: (a) The rms current (b) The reactive power required by the load (c) We want to correct the power factor to be 0.9 lagging by adding a capacitor, what will be the new reactive power? (d) draw the power triangle with the old and new reactive powers

  • A 220 kW load having 0.8 lagging power factor is supplied from a 600 V (line...

    A 220 kW load having 0.8 lagging power factor is supplied from a 600 V (line to line) three-phase supply. A bank of power factor capacitors is delta connected. (a) Draw neat schematic diagram showing the connection of the capacitor bank in Delta connection. (b) Determine the KVAR rating of each individual capacitor needed to bring power factor to 0.9. (c) Determine the capacitance of each capacitor in uF.

  • A 220 kW load having 0.8 lagging power factor is supplied from a 600 V (line to line) three-phase...

    A 220 kW load having 0.8 lagging power factor is supplied from a 600 V (line to line) three-phase supply. A bank of power factor capacitors is delta connected Q2. (a) Draw neat schematic diagram showing the connection of the capacitor bank in Delta connection. (b) Determine the kVAR rating of each individual capacitor needed to bring power factor to 0.9 (c) Determine the capacitance of each capacitor in μF.

  • A 3-phase 60 Hz 50 km transmission line delivers 20 MW of power to a load...

    A 3-phase 60 Hz 50 km transmission line delivers 20 MW of power to a load at 69 kV and a power factor of 0.8 lagging. The line has the following parameters r = 0.1112/km L = 1.11 mH/km C = negligible Determine: The line impedance. (4 Marks) The "receiving end" phase voltage and current (7 Marks) The "sending end" voltage and current (10 Marks) The voltage regulation. (4 Marks)

  • Chapter 9, Problem 9.096 A particular load has a pf of 0.4 lagging. The power delivered...

    Chapter 9, Problem 9.096 A particular load has a pf of 0.4 lagging. The power delivered to the load is 40 kW from a 220-V rms 60-Hz line. What value of capacitance placed in parallel with the load will raise the pf to 0.5 lagging? mF the tolerance is +/-2%

  • Example 9 Three loads are connected in parallel across 1400 V, 60 Hz supply: Load 1:...

    Example 9 Three loads are connected in parallel across 1400 V, 60 Hz supply: Load 1: 125 KVA, 0.28 PF lag Load 2: 10 kW, 40 kVAR capacitive load Load 3: 15 kW Find the total kW, kVAR, KVA, and the supply power factor . The KVAR and the capacitance in mF of the capacitor needed to improve the PF to 0.8 lagging

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT