QUESTION 5 A three-phase 50 Hz, 500 MVA/15 kV, 32 pole hydro-electric generating unit has an...
3.1 When two four pole, 50 Hz synchronous generators are paralleled their phase displacement is 2 mechanical. The synchronous reactance of each machine is 10 n/phase and the common busbar voltage is 66kV. Calculs the s cho nisimlengud AN 2 A synchronous generator has a synchronous impedance of 2p and a resist ance of 0.01 p.u. It is connected to an infinite busbar of voltage 1 pu. through a transformer of reactance 01 pou. If the generated (no-load) emfis 1.1...
QUESTION 5 A 3-phase, 22 kV (phase), 500 MVA star-connected synchronous generator has a per phase reactance Xg of 1.5 pu and supplies 0.8 pu per phase real power (P) at the rated voltage, with a lagging power factor of 0.6 to the load. Find the actual excitation voltage Vo in kV (line value). 96.392
Problem 2. [20 PT] A 25 MVA, three phase, 13.8 KV, A-connected, two pole, 60 Hz synchronous generator was tested by open circuit and short circuit tests and following data was collected. Neglect the stator resistance for this question: Open Circuit Characteristics Line Voltage, KV 13.0 13.8 15.2 16.0 Field Current, A 320 365 380 475 570 14.1 Short Circuit Characteristics Field Current, A 320 Armature Current, A 1046 365 380 475 570 1190 1240 1550 1885 Compute a) [10...
1. A three-phase synchronous generator connected to a 345-KV transmission line through a transformer as shown in Figure P1. Parameters of both generator and transformer are given in the figure. Transformer losses and exciting current are neglected. A three-phase short-circuit occurs on the line side of the circuit breaker when the generator is operated at rated terminal voltage and at no-load. The breaker interrupts the fault three cycles after fault inception. Neglect the effect of the transformer on the time...
Please show all the clearly step
A 500 MVA, 24 kV, 60 Hz three-phase synchronous generator is operating at rated voltage and frequency with a terminal power factor of 0.8 lagging. The synchronous reactance X 0.8. Stator coil resistance is negligible. The internally generated voltage E,-18 kv a) Draw the per phase equivalent circuit. b) Determine the torque (power) angle 5, c) the total output power, d) the line current.
A 12 kV, 300 MVA synchronous generator is tested at a field current of 200 A. The open-circuit voltage was found to be 10 kV and the short-circuit current was 7.5 kA. The stator resistance was measured at 0.1 ohms per phase. i) Find the value of the synchronous reactance in per-unit. [ 2 marks ] ii) The synchronous generator is delivering half rated output at a terminal voltage of 5% below rated voltage and a power factor of 0.7...
A 50 Hz, 250 MVA synchronous generator having inertia constant H=5 MJ/MVA is connected to an infinite bus through transformer and transmission line as shown below. The transformer reactance is based on 500 MVA, while the other impedances are based on the generator MVA Infinite bus 1 2 3 XL 0.1 pu - oto G1 V= 1.0 pu X 0.1 pu Xd = 0.3 pu at 500 MVA The generator is delivering 0.8 of full load current at a power...
A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected
synchronous generator has a resistance 0.5Q/phase and a synchronous
reactance of 5Q/phase. The generator is supplying its rated power
at its rated voltage and at a power factor lagging. The rotational
loss is 2 kW. Calculate:
(a) the power developed,
(b) the power angle,
(c) the voltage regulation, and
(d) the shaft torque.
A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.50/phase and a synchronous...
Q2) A 13.8-kV, 50-MVA, 0.9-power-factor-lagging, 60-Hz, four-pole Y-connected synchronous generator has a synchronous reactance of 2.5 Ω and an armature resistance of 0.2 Ω At 60 Hz, its friction and windage losses are 1 MW, and its core losses are 1.5 MW. The field circuit has a de voltage of 120 V, and the maximum , is 10 A. The current of the field circuit is adjustable over the range from 0 to 10 A. The OCC of this generator...
QUESTION 3 A 200 - MVA, 15/200 kV single-phase power transformer has a per – unit resistance of 1.2 percent and a per-unit reactance of 5 percent (data taken from the transformer's nameplate). The magnetizing impedance is impedance is j80 per unit. a. Find the equivalent circuit referred to the low-voltage side of this transformer. b. Calculate the voltage regulation of this transformer for a full-load current at power factor of 0.8 lagging. c. Assume that the primary voltage of...