Exhaust Air Heat Wheel Return Air HRU Outlet Ventilation Air Wheel Type Total HRU .8 Two...
Outside air (100°F/75°F) flowing at 1000 cfm is mixed with return air (75°F/63°F) at 5000 cfm. Find the mixed air conditions (db, RH, wb, u, and h). Sketch on the psychrometric chart.
Psychrometrics) - Work on Your Own Tlowing at 1500 cfm is heated from 65°F (RH-35 conditions (db. RH ons (db, RH, wb, m) Sketch the process on the psychometri 65°F (RH-3596) at a rate of 50.000 Btu/h. Find the outlet air AMERICAN SOCIETY OF HEATING P RICERATO AND AR-CONDITIONING ENGINEERSING w ENTHALPY,
3. A room is to be maintained at 75 deg.F db. 3500 cfm of air is ventilated from this room. The sensible heat load on the room is 70,000 Btu/hr. From the air conditioning equation, what is the db temperature of the air ventilated from the room? The ventilated air is 30% rh. What is the wb temperature of the air ventilated from the room? What is the density of the ventilated air? What is the mass flow rate of...
A manufacturing building is being ventilated to maintain air temperature, air moisture levels and air quality. The following is known about the situation: • The desired inside conditions are 68°F db with a maximum of 60% RH. • The average outside conditions are 42°F db and 35°F wb. • The building has an overall heat loss factor of 454 BTU/(h·ºF) with a total volume of 76,000 ft3. • Inside the building, people and equipment generate sensible heat at a rate...
a. Calculate the dry air and water vapor mass flow rates (lb/min) if the volume flow rate is 1,000 cfm, the humidity ratio is 0.025 lbv/lba, and the dry air density is 0.072 Iba/ft3. b. Assume the above air enters an evaporator coil at 90°F where it is cooled in a constant humidity ratio process until reaching the 100 % RH curve ( the temperature at that point is the dew point. The air then keeps dropping in temperature, following...
An Conference Center is to be air-conditioned for a seating capacity of 3200 people for the following outdoor and comfort conditions a) Outdoor design conditions = 35 °C, db and 65% R.H b) Indoor/return design conditions-26 deg C. db and 55% RH. c) Total sensible room load = 420,000 kJ/hr d) Total latent room load = 200,000 KJ/hr e) The rise in dry bulb temperature of the air inside the conference center is limited to 9 °C (i.e. the Supply...