Question

A manufacturing building is being ventilated to maintain air temperature, air moisture levels and air quality....

A manufacturing building is being ventilated to maintain air temperature, air moisture levels and air quality. The following is known about the situation: • The desired inside conditions are 68°F db with a maximum of 60% RH. • The average outside conditions are 42°F db and 35°F wb. • The building has an overall heat loss factor of 454 BTU/(h·ºF) with a total volume of 76,000 ft3. • Inside the building, people and equipment generate sensible heat at a rate of 46,500 BTU/h. • Inside the building, people and equipment generate moisture at a rate of 14.2 lb H2O/h. • There is no significant amount of water evaporation. • Air quality is provided at a minimum of 1.4 air exchanges per hour. • The ventilation fans exhausts from the building (fan inlet is at the inside conditions). 1. What ventilation rate (in cfm) is needed to maintain the desired inside air temperature? 2. What ventilation rate (in cfm) is needed to maintain the desired maximum relative humidity at the desired inside air temperature? 3. What ventilation rate (in cfm) is needed to maintain air quality? 4. What ventilation rate (in cfm) should be used? 5. Is supplemental heat necessary when the building is ventilated at the rate in #4? If so, how much (in BTU/h)?

0 0
Add a comment Improve this question Transcribed image text
Answer #1

1. We are provided with the Air change rate = 1.4 /h

Volume of room = 76000 cu ft

So, Ventilation rate (cu ft/h) = Air change rate X Room Volume (cu ft)

= 1.4 X 76000 = 106400 cu ft/h

Add a comment
Know the answer?
Add Answer to:
A manufacturing building is being ventilated to maintain air temperature, air moisture levels and air quality....
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 3. A room is to be maintained at 75 deg.F db. 3500 cfm of air is...

    3. A room is to be maintained at 75 deg.F db. 3500 cfm of air is ventilated from this room. The sensible heat load on the room is 70,000 Btu/hr. From the air conditioning equation, what is the db temperature of the air ventilated from the room? The ventilated air is 30% rh. What is the wb temperature of the air ventilated from the room? What is the density of the ventilated air? What is the mass flow rate of...

  • You own a mechanically ventilated swine facility. The dry bulb temperature inside the facility is 50...

    You own a mechanically ventilated swine facility. The dry bulb temperature inside the facility is 50 degrees F and outside is only 30 degrees F. Inside you have a relative humidity of 70% and outside the relative humidity is 20%. To keep the humidity from getting any higher you need to remove 12 gallons of water per hour from the facility with the ventilation air. At what rate (cfm) must the fans pull inside air out of the building? Fan...

  • PROBLEM 2. (20 POINTS) A space to be maintained at 25 C dB (dry bulb) temperature and 18°C wB (we...

    PROBLEM 2. (20 POINTS) A space to be maintained at 25 C dB (dry bulb) temperature and 18°C wB (wet bulb) has a rate of sensible-heat gain of 25 kWand a rate of moisture gain of20 kg/hr. Moist air enters the space at a dry-bulb temperature of 15°C. Outdoor air at 35 C dB temperature and 25 C wB is supplied for ventilation purposes at a rate of 400 Us (litres per second) of standard air. After leaving the room,...

  • Exhaust Air Heat Wheel Return Air HRU Outlet Ventilation Air Wheel Type Total HRU .8 Two...

    Exhaust Air Heat Wheel Return Air HRU Outlet Ventilation Air Wheel Type Total HRU .8 Two types of heat recovery units. CHAPTER 4 PROBLEMS 4.1 A sling psychrometer measures the air tempera- tures to be 85°F dry bulb and 72°F wet bulb. Find: relative humidity, dew-point temperature, humidity ratio (in lbmv/lbma and grains), specific volume, and enthalpy. Show results on a chart and verify with the program PsychProcess.xls (on the accom- panying CD). Assume sea level elevation. 4.2 Air flowing...

  • 4. Moist air enters a chamber at 60°F dry-bulb and 46 °F wet-bulb temperature at a...

    4. Moist air enters a chamber at 60°F dry-bulb and 46 °F wet-bulb temperature at a rate of 5000 cfm. In passing through the chamber, the air absorbs sensible heat at a rate of 20,000 Btu/h and picks up 63 lb/h of saturated steam at 200°F. Determine: (a) The dry-bulb and wet-bulb temperatures of the leaving air. (b) The sensible heat factor (25)

  • a. Calculate the dry air and water vapor mass flow rates (lb/min) if the volume flow...

    a. Calculate the dry air and water vapor mass flow rates (lb/min) if the volume flow rate is 1,000 cfm, the humidity ratio is 0.025 lbv/lba, and the dry air density is 0.072 Iba/ft3. b. Assume the above air enters an evaporator coil at 90°F where it is cooled in a constant humidity ratio process until reaching the 100 % RH curve ( the temperature at that point is the dew point. The air then keeps dropping in temperature, following...

  • 4. Commercial building energy analysis. This problem analyzes how large commercial buildings use using data from...

    4. Commercial building energy analysis. This problem analyzes how large commercial buildings use using data from the Photonics Center In particular, we want to compare the energy needed to condition the air flowing through the building, with the energy needed to 1) provide heat in the winter to balance the heat loss from the walls to the environment, and 2) provide the necessary cooling in the summer time to overcome the heat gain from the outside air (lets ignore solar...

  • An Conference Center is to be air-conditioned for a seating capacity of 3200 people for the...

    An Conference Center is to be air-conditioned for a seating capacity of 3200 people for the following outdoor and comfort conditions a) Outdoor design conditions = 35 °C, db and 65% R.H b) Indoor/return design conditions-26 deg C. db and 55% RH. c) Total sensible room load = 420,000 kJ/hr d) Total latent room load = 200,000 KJ/hr e) The rise in dry bulb temperature of the air inside the conference center is limited to 9 °C (i.e. the Supply...

  • System Model: Automotive Air Conditioning System Outside Air Temp: 45 oC Car Interior Air Temp: 22...

    System Model: Automotive Air Conditioning System Outside Air Temp: 45 oC Car Interior Air Temp: 22 oC Heat Load = 4.2 kJ/sec  rate at which heat must go in to the air conditioner to be removed from the car’s interior Refrigerant: R134a HINT: Heat enters an air conditioning system where? Refrigerant 134a … - leaves the evaporator coil and enters the compressor as a saturated vapor at the evaporator pressure of 2.8 bars. - It leaves the compressor at...

  • 56. Fresh air is introduced into a room at such a rate that the air in...

    56. Fresh air is introduced into a room at such a rate that the air in the room is changed every 5 minutes. The room is 30 by 30 by 10 ft and the air in the room is at 70 °F with a percentage humidity of 60. Outside air at a temperature of 60 °F is used as air supply. The outside air is heated to the room temperature by a heat exchanger. How many BtU per hour must...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT