You own a mechanically ventilated swine facility. The dry bulb temperature inside the facility is 50 degrees F and outside is only 30 degrees F. Inside you have a relative humidity of 70% and outside the relative humidity is 20%. To keep the humidity from getting any higher you need to remove 12 gallons of water per hour from the facility with the ventilation air. At what rate (cfm) must the fans pull inside air out of the building?
Fan Rate = [Num]cfm
Inside condition => T = 50F, RH = 70%
0.0055 lb moisture/lb dry air
Outside condition => T = 30F, RH = 20%
0.0008 lb moisture/lb dry air
So a ventilation of 1 lb air removes 0.0055 - 0.0008 = 0.0047 lb of water
amount of water to be removed = 12 gallon/hour = 12 * 8.34 lb per hour = 100.08 lb/hour = 0.0278 lb/s
So 0.0278 lb/s moisture can be removed by 0.0278/0.0047 = 5.915 lb/s of air = 354.89 lb/min
density of air = 1.225 kg/m3 = 0.0765 lb/ft3
rate (cfm) must the fans pull inside air out of the building = 354.89/0.0765 = 4639 cfm
[Note: the data of relative humidity are taken from http://www.greenbuildingadvisor.com/sites/default/files/psychrometric-chart-quantities-carrier.jpg graph]
You own a mechanically ventilated swine facility. The dry bulb temperature inside the facility is 50...
A manufacturing building is being ventilated to maintain air temperature, air moisture levels and air quality. The following is known about the situation: • The desired inside conditions are 68°F db with a maximum of 60% RH. • The average outside conditions are 42°F db and 35°F wb. • The building has an overall heat loss factor of 454 BTU/(h·ºF) with a total volume of 76,000 ft3. • Inside the building, people and equipment generate sensible heat at a rate...
Q 1: In an air conditioning system return air at 26°C dry-bulb temperature and 50% relative humidity is mixed with outdoor ambient air at 34°C dry-bulb temperature and 60% relative humidity. The dry air mass flow rate of outdoor air is 30% of the supply air mass flow rate to the space. The pressure is constant at 101.3 kPa. Calculate (i) the enthalpy, (ii) the humidity ratio, and (ii) the dry-bulb temperature of the supply air. (i) Compare the results...
The atmospheric air 32 °C dry bulb temperature and 70% relative humidity supplied to the cooling coil at a rate of 45m3/min. The air cooling to the saturated state and leaving at a temperature of 16 °C. Determine: a- Specific humidity at each state. b- Wet bulb and dew point temperatures at the final state c- Final relative humidity. d- Mass of water condensed. e- Rate of heat removed from the air in kW. f- Show the process on Psychrometric...
2) Very humid air enters a dehumidifier at 500 ft^3/min. The air is at a dry-bulb temperature of 85 degrees F and a relative humidity of 90%. The specific humidity of the mixture must be brought to 30 grains of water per pound mass of air. Assume atmospheric mixture pressure. A) How low must the dry-bulb temperature go to achieve this? B) What is the rate at which energy must be removed to accomplish the reduction in specific humidity, in...
PROBLEM 2. (20 POINTS) A space to be maintained at 25 C dB (dry bulb) temperature and 18°C wB (wet bulb) has a rate of sensible-heat gain of 25 kWand a rate of moisture gain of20 kg/hr. Moist air enters the space at a dry-bulb temperature of 15°C. Outdoor air at 35 C dB temperature and 25 C wB is supplied for ventilation purposes at a rate of 400 Us (litres per second) of standard air. After leaving the room,...
On a typical autumn day, outside air with a dry bulb temperature of 15°C and 40% relative humidity is brought into a processing facility where it is to be used for a controlled storage chamber. The air must be heated to 37°C and humidified to 90% relative humidity. Calculate: (11 marks total) The relative humidity of the air when it is heated to 37°C, but BEFORE it is humidified. (No water has been added to the air yet). (2 marks)...
Exhaust Air Heat Wheel Return Air HRU Outlet Ventilation Air Wheel Type Total HRU .8 Two types of heat recovery units. CHAPTER 4 PROBLEMS 4.1 A sling psychrometer measures the air tempera- tures to be 85°F dry bulb and 72°F wet bulb. Find: relative humidity, dew-point temperature, humidity ratio (in lbmv/lbma and grains), specific volume, and enthalpy. Show results on a chart and verify with the program PsychProcess.xls (on the accom- panying CD). Assume sea level elevation. 4.2 Air flowing...
Please show work 11-43·Atmospheric air with a dry bulb temperature of 30°C and a relative humidity f 40 percent enters the cooling section of an air-conditioning system at a rate of 10 kg/s and is cooled to 18°C. Determine the volumetric flow rate of the air leaving the cooling section, the heat-transfer rate required for this process, and the entropy change of the air per unit mass of dry air. If the velocity of the airstream is not to exceed...
b) A cooling coil of an Air Handling Unit has dew-point of 8'C dry-bulb (db) temperature, and outdoor air enters the cooling equipment at 28 C d.b temperature and leaves at 16'C d.b temperature with mass flow rate of lkg/s determine: i) the contact factor (CF) ii) the volume flow rate iii) the by-pass factor iv) the sensible heat that removed from the outdoor air (1.5 mark) (1.5 marks) (1 mark) (2.0 marks) c) Explain the difference between "relative humidity...
b) A cooling coil of an Air Handling Unit has dew-point of 8'C dry-bulb (db) temperature, and outdoor air enters the cooling equipment at 28 C d.b temperature and leaves at 16'C d.b temperature with mass flow rate of lkg/s determine: i) the contact factor (CF) ii) the volume flow rate iii) the by-pass factor iv) the sensible heat that removed from the outdoor air (1.5 mark) (1.5 marks) (1 mark) (2.0 marks) c) Explain the difference between "relative humidity...