Question

You own a mechanically ventilated swine facility. The dry bulb temperature inside the facility is 50...

You own a mechanically ventilated swine facility. The dry bulb temperature inside the facility is 50 degrees F and outside is only 30 degrees F. Inside you have a relative humidity of 70% and outside the relative humidity is 20%. To keep the humidity from getting any higher you need to remove 12 gallons of water per hour from the facility with the ventilation air. At what rate (cfm) must the fans pull inside air out of the building?

Fan Rate =  [Num]cfm

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Inside condition => T = 50F, RH = 70%

0.0055 lb moisture/lb dry air

Outside condition => T = 30F, RH = 20%

0.0008 lb moisture/lb dry air

So a ventilation of 1 lb air removes 0.0055 - 0.0008 = 0.0047 lb of water

amount of water to be removed = 12 gallon/hour = 12 * 8.34 lb per hour = 100.08 lb/hour = 0.0278 lb/s

So 0.0278 lb/s moisture can be removed by 0.0278/0.0047 = 5.915 lb/s of air = 354.89 lb/min

density of air = 1.225 kg/m3 = 0.0765 lb/ft3

rate (cfm) must the fans pull inside air out of the building = 354.89/0.0765 = 4639​ cfm

[Note: the data of relative humidity are taken from http://www.greenbuildingadvisor.com/sites/default/files/psychrometric-chart-quantities-carrier.jpg graph]

Add a comment
Know the answer?
Add Answer to:
You own a mechanically ventilated swine facility. The dry bulb temperature inside the facility is 50...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT