Question

System Model: Automotive Air Conditioning System Outside Air Temp: 45 oC Car Interior Air Temp: 22...

System Model: Automotive Air Conditioning System

Outside Air Temp: 45 oC Car Interior Air Temp: 22 oC

Heat Load = 4.2 kJ/sec  rate at which heat must go in to the air conditioner to be removed from the car’s interior

Refrigerant: R134a

HINT: Heat enters an air conditioning system where?

Refrigerant 134a …

- leaves the evaporator coil and enters the compressor as a saturated vapor at the evaporator pressure of 2.8 bars.

- It leaves the compressor at the condenser pressure of 14 bars

.- It leaves the condenser at the same pressure as a saturated liquid. Finally, after passing through the expansion valve (a throttling process), …

- the refrigerant enters the evaporator coil as a saturated liquid-vapor mixture at the evaporator pressure (2.8 bars).

a) Draw a schematic sketch of the machine labeling pertinent parts. Sketch the line between the low and high pressure sides of the system. Also draw a temperature-entropy plot for this unit. You may start with the ideal model and modify this later if the data shows that this is more realistic. (5 pts)

b) Based on the description of the ideal vapor compression model given above, find …

i. the pressure at each point (states 1, 2, 3, and 4). Give your answers in bars, kPa, and in psi (pounds per square inch). Show the pressures in bars on your schematic (part a).

ii. What property from the tables (v, u, h, s) is assumed to be constant between the compressor inlet and the compressor outlet? Show this on your schematic.

iii. What property from the tables (v, u, h, s) is assumed to be constant between the expansion (throttling) valve inlet and outlet? Show this on your schematic. (5 pts)

c) At each of the four states, list the pressure, the temperature, the quality (where appliable), enthalpy (kJ/kg) and entropy (kJ/kg K) of the R134a. (40 pts)

d) Find the mass flow rate of refrigerant necessary for an air conditioning system heat input rate (Heat In) equal to the heat load. (10 pts)

e) Convert the heat load from kJ/sec (= kW) into BTU/hr. Also give this value in tons of refrigeration capacity (1 ton = 12,000 BTU/hr). (2 pts)

f) Using the mass flow rate found in d), determine the compressor power demand. Give the power demand in kW (=kJ/sec) and horsepower. (10 points)

g) What are the theoretical and the actual coefficients of performance for this machine? (8 pts)

h) Using the mass flow rate found in d), determine how much heat is rejected in the condenser coil in kW. Also give this answer in BTU/hr. (5 points)

i) A more realistic model of vapor compression refrigeration is given in Fig 10.5.

i. For a compressor isentropic efficiency of 80% (see sec. 6.12), find the power needed to run the compressor for a more realistic process. (5 pts)

ii. Your model was based on saturated liquid leaving the condenser and entering the expansion valve. How much additional heat would be rejected if this was a subcooled (compressed) liquid at a temperature of 30 oC entering the expansion valve? (5 pts)

Now – move from the refrigerant inside the machine to the air inside the car.

The conditioned air inside the car is moved by the fan (a squirrel cage blower – do a quick Google search if you don’t know what this looks like) across the surfaces of the evaporator coil. As it passes through the evaporator the air is cooled and dehumidified.

The air enters the evaporator at a pressure of 1 bar and a temperature of 22 oC. The design ΔT across the coil (the drop in temperature) is 10 oC.

j) For the air passing through the coil, find ..

i. The temperature as the air leaves the coil (3 pts)

ii. The change in enthalpy and the mass flow rate of air necessary for the rate of heat going out of the air to equal the design heat input to the evaporator coil. (10 pts)

iii. As the air enters the coil, find the density of the air and the volume flow rate of air through the coil. Give the volume flow rate in m3/sec, liters, and cubic feet per minute (CFM). (12 pts)

I am having trouble understanding the tables on whether I use superheated or liquid or vapor properties of the stages C) I know E-H has been answered somewhere else in Chegg but I am still lost at the whole system

0 0
Add a comment Improve this question Transcribed image text
Answer #1

e.

Heat Load = 4.2 kW

1 kW = 3412.142 BTU/hr

Heat Load = 4.2 * 3412.142

Heat Load = 14330.9964‬ BTU/hr

Heat Load = 14330.9964‬ / 12000 = 1.1942497‬ TR

f.

W1-2 = m (h2 - h1)

= 0.03463 * (279.8 - 246.52)

W1-2 = 1.1524864‬ kW  

1 kW = 1.34102 hp

W1-2 = 1.5455 hp  

g.

COP = RE / W1-2

COP = 4.2 / 1.1524864‬

COP = 3.6443

h.

Q2-3 = m (h2-h3)

= 0.03463 * (279.8 - 125.26)

Q2-3 = 5.3517202 kW

1kW = 3412.142 BTU/hr

Q2-3 = 18260.8292 BTU/hr

Please rate my answer. Thank You.

Add a comment
Know the answer?
Add Answer to:
System Model: Automotive Air Conditioning System Outside Air Temp: 45 oC Car Interior Air Temp: 22...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • QUESTION 4 (15 marks) Below is a schematic of a car air conditioning system that uses...

    QUESTION 4 (15 marks) Below is a schematic of a car air conditioning system that uses R-134a as its refrigerant. Here we will analyze the system under the case of driving through a very hot environment of 40 °C. The interior of the car is kept at 20 °C. Refrigerant leaves the compressor at 1.6 MPa absolute and leaves the condenser as a saturated liquid. The evaporator operates at 400 kPa absolute and the refrigerant leaves as a saturated vapour....

  • Problem I: Not applicable for 2017 Problem II: In an R-134a vapor-compression home heat pump, R-134A...

    Problem I: Not applicable for 2017 Problem II: In an R-134a vapor-compression home heat pump, R-134A enters the compressor (75% isentropic efficiency) as a saturated vapor at 200 kPa and leaves at 800 kPa. The refrigerant goes through a constant pressure condenser and leaves as a saturated liquid. The refrigerant then goes through an adiabatic expansion valve enters the evaporator as a liquid-vapor mixture. The mass flow rate of refrigerant is 0.1 kg/s. and Cod A. Write the equation for...

  • -Rome can get pretty hot in the mid-summer! Most of the air conditioning units in the Tiber campus use the working flui...

    -Rome can get pretty hot in the mid-summer! Most of the air conditioning units in the Tiber campus use the working fluid R-134a (1,1,1,2-tetrafluoroethane), which is replaces the less environmentally-friendly R-12 of years ago. a) Illustrate the following air conditioning cycle, indicating material, heat, and work flows, as well as given/known temperatures and pressures: R-134a is pressurized to 10.2 bar in an adiabatic, reversible compressor. This high-pressure, hot refrigerant is condensed outside of the building using ambient air to a...

  • In a vapor-compression refrigeration cycle, ammonia exits the evaporator as saturated vapor at -22 °C. There...

    In a vapor-compression refrigeration cycle, ammonia exits the evaporator as saturated vapor at -22 °C. There are irreversibilities in the compressor. The refrigerant enters the condenser at 16 bar and 160 °C, and saturated liquid exits at 16 bar. There is no significant heat transfer between the compressor and its surroundings, and the refrigerant passes through the evaporator with a negligible change in pressure. Calculate the coefficient of performance, b, and the isentropic compressor efficiency, defined as: 2s Condenser Expansion...

  • from introduction of chemical engineering thermdynamics 7th edition. chapter 9 question 11 part(c). can you show...

    from introduction of chemical engineering thermdynamics 7th edition. chapter 9 question 11 part(c). can you show me how did you read the graph and get H4=117.5 and S4=0.262. i need you to show the graph and how to read it to get thoses amswers. ARE YOU GOING TO SOLVE IT ?????? you guys know no thing. you never solve any problem right and you always late. 0 Step 6 of 9 Done (c) Draw the flow diagram for the process...

  • Condenser Compressor An ideal vapor-compression refrigeration cycle is modified to include a counter-flow heat exchanger as...

    Condenser Compressor An ideal vapor-compression refrigeration cycle is modified to include a counter-flow heat exchanger as shown. Refrigerant 134a leaves the evaporator as saturated vapor at 0.10 MPa and is heated at constant pressure to 20°C before entering the compressor. Following isentropic compression to 1.4 MPa, the refrigerant passes through the condenser and exits at 45°C and 1.4 MPa. The liquid then passes through the heat exchanger and enters the expansion valve at 1.4 MPa. The mass flow rate of...

  • thermodynamics Page 5 of 12 Problem 3 (SS pts): The following figure provides the schematic o using Refrigerant 134a as the working fluid to keep a ro the outdoor air at 34 "C. The refrigeran...

    thermodynamics Page 5 of 12 Problem 3 (SS pts): The following figure provides the schematic o using Refrigerant 134a as the working fluid to keep a ro the outdoor air at 34 "C. The refrigerant enters the co leaves dhe rate of O.06 m steady site compressor at 320 kPa as a satwrated vapor w a saturated liquid. Assume there is no pressure drop in the eo stray heat transfer for the compressor the valve, leaves at 1 refrigerant leaves...

  • Refrigerant 134a flows through an ideal vapor compression heat pump system with a heating capacity of...

    Refrigerant 134a flows through an ideal vapor compression heat pump system with a heating capacity of 60,000 Btu/hr. The condenser operates at 200 psi, and the evaporator temperature is 0°F. The refrigerant is a saturated vapor at the evaporator exit and a saturated liquid at the condenser exit. The temperature at the compressor exit is 180°F. Assuming the compressor is not 100% isentropic, determine: a) Mass flow rate (lbm/min) b) Compressor power (hp) c) Isentropic compressor efficiency d) Coefficient of...

  • (100 points) Figure below shows the schematic diagram of a two-stage cascade refrigeration system (also called...

    (100 points) Figure below shows the schematic diagram of a two-stage cascade refrigeration system (also called the Economizer 2-Stage Refrigeration Cycle). Comparing to the cascade two-stage refrigeration system discussed in In-class Activity #10a, in this case, the flash chamber (now called Flash Intercooler) is still used but the mixing chamber is removed. The superheated vapor (2) out of the low-pressure compressor (1) is routed into the flash chamber, and the saturated vapor (3) out of the flash chamber enters directly...

  • EXAMPLE 6 A household refrigeration system works with a vapor compression refrigeration system with two evaporators...

    EXAMPLE 6 A household refrigeration system works with a vapor compression refrigeration system with two evaporators using Refrigerant 134a as the working fluid. This arrangement is used to achieve refrigeration at two different temperatures with a single compressor and a single condenser. The low temperature evaporator operates at -18°C with saturated vapor at its exit and has a refrigerating capacity of 10.5 kW (3 tons). The higher- temperature evaporator produces saturated vapor at 3.2 bar at its exit and has...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT