Question

A 100 MVA, 12 kV Single-phase generator has a sub transient reactance of 20%. The generator supplies a two synchronous motors

note that
1) single phase system
2) base values at transmission line circuit

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Solution - Given - Shit HU Generator : Ti Ty :: 400 MVA 12 kV , xd=20% Iso mra132/12 kV , **=12% 40 MVA, 132/ 6.6 kV, Xtz 10As we know by transformer rule- 12 132 24 150 5 2 = 13.63 kv HOLO Telemarketingos X= 1363 X • Voltage base at generator sideKoove of TL = : x (P.1) = - Leon = 150 x1 (actual) - or 0-0 4610 | 150 z base For motor, xm, (new) = 0.15* 1 = 0.218 pu Km2 ((c) for Transformer T, Vbase = 132 kV, Sbase = 150 MVA : : Zbost a = 132*116.168 . So, Actual value (2) = Zpu x base = 0.128

Add a comment
Know the answer?
Add Answer to:
note that 1) single phase system 2) base values at transmission line circuit A 100 MVA,...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 3. A 200 MVA, 20 kV, 60 Hz Y-connected solidly grounded three phase synchronous generator connect...

    3. A 200 MVA, 20 kV, 60 Hz Y-connected solidly grounded three phase synchronous generator connected through a 200 MVA 20/138 KV Y-Y transformer to a 138 kV transmission line. The generator reactances to the machine's own base are X-1.10 Both of the transformers Y connections are solidly grounded and its positive, negative and zero sequence series resitances are all 0.10 pu. a. What is the voltage at the terminals of the generator during the sub transient period if a...

  • Problem #1 Part I (50 points) Consider the following one-line diagram of a three-phase power system. Assume that the system has the following base quantities: S3 100 MVA, and VbaselL 38 kV at the...

    Problem #1 Part I (50 points) Consider the following one-line diagram of a three-phase power system. Assume that the system has the following base quantities: S3 100 MVA, and VbaselL 38 kV at the generator side. The rated line-to-line terminal voltage of the generator (BUS 1) is 38 kV. A single-circuit three-phase transposed overhead line composed by one ACSR Partridge conductor per phase with vertical configuration. The transmission line length is 50 km and the distance between phases a-b, b-c...

  • 1. A three-phase synchronous generator connected to a 345-KV transmission line through a transformer as shown...

    1. A three-phase synchronous generator connected to a 345-KV transmission line through a transformer as shown in Figure P1. Parameters of both generator and transformer are given in the figure. Transformer losses and exciting current are neglected. A three-phase short-circuit occurs on the line side of the circuit breaker when the generator is operated at rated terminal voltage and at no-load. The breaker interrupts the fault three cycles after fault inception. Neglect the effect of the transformer on the time...

  • Consider the single-line diagram of the three-phase power system shown in Figure 1. Component ratings are...

    Consider the single-line diagram of the three-phase power system shown in Figure 1. Component ratings are as follows: Generator G1: 750 MVA, 18 kV, X0.2 per unit Generator G2: 750 MVA, 18 kV, X 0.2 per unit Synchronous Motor M: 1,500 MVA, 20 kV, X-20% A-Y Transformers Ti, T2, T's, & T.: 750 MVA, 500 kV Y/20 kV A, X = 10% Y-Y Transformer T's 1,500 MVA, 500 kV Y/20 kV Y, X-10% ne L:X (a) Using bases of 100...

  • solve no: 3.14 , 3.16, 3.19 please show each step and solve for beginners 120 Power...

    solve no: 3.14 , 3.16, 3.19 please show each step and solve for beginners 120 Power System Analysis 3.12. A single-phase system similar to that shown in Figure 3.11 has two transformers A-B a B-C connected by a line B feeding a load at the receiving end C. The ratings and parame ter values of the components are 500 V/1.5 kV, 9.6 kVA. leakage reactance 5 % 1.2 kV/120 V, 7.2 kVA, leakage reactance 4 % series impedance (0.5 +...

  • 03 Consider the following one line diagram. The generator is rated at 25 MVA, IN has...

    03 Consider the following one line diagram. The generator is rated at 25 MVA, IN has subtransient reactance of 20 %. The transmission line has a reactance of 10 The subtransient reactance of motorlis 0.345 pu where is that ol second more pu. Each motor has the following ratings. 10 MVA and 11 kV. Both transformers are rated at 25 MVA and have a reactance of 8.05% each; the transformers 1 and 2 have voltage ratio of 11/121 KV and...

  • Problem 4 Three ideal single-phase transformers are connected in a delta/wye configuration with the primary side of the...

    Problem 4 Three ideal single-phase transformers are connected in a delta/wye configuration with the primary side of the three-phase transformer rated at 120 kV and the secondary side rated at 13.8 kV. The rated power of the transformer bank is 20 MVA. One side of the transformer bank is connected to a 120 kV transmission line, and the other side is connected to a three-phase load of 15 MVA at 0.85 lagging power factor. Compute the following: a) The turns...

  • Three single phase step-up transformers rated at 40 MVA, 13.2 kV/80 kV are connected in delta-wye on a 13.2 kV transmission line

     a. Three single phase step-up transformers rated at 40 MVA, 13.2 kV/80 kV are connected in delta-wye on a 13.2 kV transmission line. If they feed a 90 MVA load calculate the following: i. The secondary line voltage ii. The current in the transformer windings iii. The incoming line currents iv. If the transformer types are two (2) additive and one (1) subtractive draw the connection diagram for the configuration stated using physical representation.  b. A 3-phase squirrel cage motor has twelve (12) leads (labelled 1 to...

  • A single-circuit, 50-Hz, 3-phase transmission line is 150 km long. The line is connected to supply...

    A single-circuit, 50-Hz, 3-phase transmission line is 150 km long. The line is connected to supply a load of 30 MVA at 0.85 pf lag and 138 kV. The line constants are : R = 0.186 ohm/km, L = 2.60 mH/km, and C = 0.012 μF/km. Using nominal π representation calculate : (a) the ABCD constants of the line. (b) the sending end voltage when supplying (i) no load, and (ii) the above load at the receiving end at the...

  • three-phase transformer is rated at 12 kV/135 kV, 100 MVA. It has the following equivalent circuit...

    three-phase transformer is rated at 12 kV/135 kV, 100 MVA. It has the following equivalent circuit parameters (referred to the primary winding where appropriate) : • primary resistance R1 = 0.03 ohms, secondary resistance R2’ = 0.04 ohms • primary leakage reactance X1 = 0.1 ohms, secondary leakage reactance X2’ = 0.1 ohms • magnetising reactance XM = 16 ohms, core-loss resistance RC = 200 ohms. In your calculations, you should use the simplified equivalent circuit. i) The transformer is...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT