b) A 1MW, 3300 V, 50 Hz, wye-connected, 3-ф, twenty four-pole, synchronous motor has a synchronous...
A 1500 kW, unity pf, 3-phase, Y-connected, 2300 V-(line), 30 pole, 60 Hz synchronous motor has a synchronous reactance of 1.95 22/phase. For this problem all losses may be neglected. a. Compute the max. torque in Nm which this motor can deliver if it is supplied with power from an infinite bus, and if its field excitation is constant at the value which would result in unity (1.0) pf at rated load. b. Now, suppose that the motor is supplied...
Q2) A 13.8-kV, 50-MVA, 0.9-power-factor-lagging, 60-Hz, four-pole Y-connected synchronous generator has a synchronous reactance of 2.5 Ω and an armature resistance of 0.2 Ω At 60 Hz, its friction and windage losses are 1 MW, and its core losses are 1.5 MW. The field circuit has a de voltage of 120 V, and the maximum , is 10 A. The current of the field circuit is adjustable over the range from 0 to 10 A. The OCC of this generator...
A 100-MVA 12.5-KV 0.85-PF lagging 50-Hz two-pole Y-connected synchronous generator has a synchronous reactance of 1.7 Q and a negligible armature resistance. I) What is the magnitude of the internal generated voltage at rated conditions? 2) What is its torque angle at these conditions? 3) What is its voltage regulation? 4) Ignoring the losses in this generator, what torque must be applied to its shaft by the prime mover at full load? 5) What is the maximum power the generator...
3. A 480 V, 60 Hz, 470 kVA, 0.85 PF lagging, 2-pole, Y-connected synchronous generator has a synchronous reactance of Xs=0.0162 and an armature resistance of RA=0.0.1622. At rated conditions the core losses are 7 kW. Friction losses and field winding losses are 8 kW. Suppose the machine is connected to an infinite bus (hence the terminal voltage is fixed) and it is running at the rated conditions. a) What is the rotor speed in rpm? b) Calculate the phase...
A 480 V, 60 Hz, 470 kVA, 0.85 PF lagging, 2-pole, Y-connected synchronous generator has a synchronous reactance of XS=0.016 Ω and an armature resistance of RA=0.016 Ω. At rated conditions the core losses are 7 kW. Friction losses and field winding losses are 8 kW. Suppose the machine is connected to an infinite bus (hence the terminal voltage is fixed) and it is running at the rated conditions. a) What is the rotor speed in rpm? b) Calculate the...
3.1 When two four pole, 50 Hz synchronous generators are paralleled their phase displacement is 2 mechanical. The synchronous reactance of each machine is 10 n/phase and the common busbar voltage is 66kV. Calculs the s cho nisimlengud AN 2 A synchronous generator has a synchronous impedance of 2p and a resist ance of 0.01 p.u. It is connected to an infinite busbar of voltage 1 pu. through a transformer of reactance 01 pou. If the generated (no-load) emfis 1.1...
A 10MVA 13.8-kV 60-Hz four-pole Y-connected synchronous generator is delivering rated power at unity power factor. a) Draw the equivalent circuit for the analysis of this problem b) Find the synchronous reactance given that the field excitation voltage is 6.89kV (per phase) and leads the terminal voltage by an angle π/4. c) In a special occasion, the generator is operated as a motor (the synchronous reactance is the one derived in (a)). At rated terminal voltage, what is the minimum...
A 100 k VA, 1100 V, three-phase, 6-pole, Y-connected, 50 Hz synchronous machine has synchronousreactance of 6 92 per-phase and negligible armature resistance. Its core losses are 7 k W and itsfriction and windage losses are 8 kW. The speed droop is 2.5%.Initially the machine is operated alone as a generator and the field current is adjusted such that theno-load voltage equals the rated voltage.a) If the generator is supplying a line current of $2.5 A at 0.85 PF lagging....
A three-phase, 5 kVA, 208 V, four-pole, 60 Hz, wye-connected synchronous machine has negligible stator winding resistance and a synchronous reactance of 8 Wper phase. It is operated in parallel with a three-phase, 208 V, 60 Hz power supply.Determine the excitation voltage and the power angle when the machine is delivering rated kVA at 0.8 pf lagging. Draw the phasor diagram
A 60-MVA, 69.3-kV, three-phase synchronous generator has a synchronous reactance of 15 Ω/phase and negligible armature resistance. -a. The generator is delivering rated power at 0.8 power factor lagging at the rated terminal voltage to an infinite bus bar. Determine the magnitude of the generated emfper phase and the power angle δ. -b. If the generated emfis 36 kV per phase, what is the maximum three-phase power that the generator can deliver before losing its synchronism? Winter