Question

150 ft3/min of air at 80F dry-bulb temperature and 70% relative humidity enters an air conditioning...

150 ft3/min of air at 80F dry-bulb temperature and 70% relative humidity enters an air conditioning unit and leaves it as saturated air at 50F. Part of the moisture in the air that condensate is collected and removed at 55F. Draw the cycle on the attached chart and

a)Determine the rates of heat removal from the air.

b)Determine the rate of moisture removal from the air

0 0
Add a comment Improve this question Transcribed image text
Answer #1

es 3 8oF DUFT 50°F State) Ti=80°F 2 hi= 36.1 Btullb Y $1=70%. J J W, = 0.015 15/ 0, -13.93 fullb stater T2=5of 2 hz = 20:26 B

Add a comment
Know the answer?
Add Answer to:
150 ft3/min of air at 80F dry-bulb temperature and 70% relative humidity enters an air conditioning...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • The atmospheric air 32 °C dry bulb temperature and 70% relative humidity supplied to the cooling...

    The atmospheric air 32 °C dry bulb temperature and 70% relative humidity supplied to the cooling coil at a rate of 45m3/min. The air cooling to the saturated state and leaving at a temperature of 16 °C. Determine: a- Specific humidity at each state. b- Wet bulb and dew point temperatures at the final state c- Final relative humidity. d- Mass of water condensed. e- Rate of heat removed from the air in kW. f- Show the process on Psychrometric...

  • Name: QUESTION 1 [25 Points] Moist air enters an air conditioning system at a dry bulb...

    Name: QUESTION 1 [25 Points] Moist air enters an air conditioning system at a dry bulb temperature T., 30 'C and relative humidity фі80% and exits at a dry bulb temperature T2 179C and relative humidity ф2.50% as shown in the figure below. The condensate exits the system at 15 °C. The mass flow rate of the dry air is 2.5 kg/s. Assume the air is at atmospheric pressure P-101.3 kPa. Cooling coils T-17 C 0-50 % Pp:-6.282 kPa Ti-30...

  • Air enters a window air conditioner at 1 atm, 30 oC, and 80 percent relative humidity...

    Air enters a window air conditioner at 1 atm, 30 oC, and 80 percent relative humidity at a rate of 10 m3/min, and it leaves as saturated air at 15 oC. Part of the moisture in the air that condenses during the process is also removed at 15 oC. Use this information to answer the following question. choose the nearest value given in (a) – (e). The heat removal rate (kW) is

  • 2. An air conditioning system is to take in air at latm 33C, 70% relative humidity...

    2. An air conditioning system is to take in air at latm 33C, 70% relative humidity and flow rate of 50m3/min and deliver it 23C and 60% relative humidity. The air first flows over the cooling coils, where it is cooled and dehumidified, and then over the resistance heating wires, where it is heated to the desired temperature. Assuming that the condensate is removed from the cooling section at 10C, determine: a) The temperature of the air before it enters...

  • Q 1: In an air conditioning system return air at 26°C dry-bulb temperature and 50% relative...

    Q 1: In an air conditioning system return air at 26°C dry-bulb temperature and 50% relative humidity is mixed with outdoor ambient air at 34°C dry-bulb temperature and 60% relative humidity. The dry air mass flow rate of outdoor air is 30% of the supply air mass flow rate to the space. The pressure is constant at 101.3 kPa. Calculate (i) the enthalpy, (ii) the humidity ratio, and (ii) the dry-bulb temperature of the supply air. (i) Compare the results...

  • Atmospheric air at 32°C and 70% relative humidity passes through a cooling section in an air-conditioning...

    Atmospheric air at 32°C and 70% relative humidity passes through a cooling section in an air-conditioning duct where the air is cooled below its dew point and some of the water is removed. The air then passes over a heating section where heat is added until the final temperature is 22°C and the relative humidity is 45%. Assume the process occurs at constant pressure of 1 atm. Using the psychrometric chart, determine: (a) The amount of water removed in the...

  • 3. Air at a dry bulb temperature of 40C and a wet bulb temperature of 20C...

    3. Air at a dry bulb temperature of 40C and a wet bulb temperature of 20C is first heated in a heater to a dry bulb temperature of 90C. Then it is passed through a bed of apricot slices to dry them. The air exiting from the top of the apricot bed is at a dry bulb temperature of 60C. It is then passed through a dehumidifier to reduce its relative humidity to 10%. Clearly show the various paths of...

  • Problem 7 O/5 points (0%) Humid air at 1 atm, 42 °C dry bulb and 55 % relative humidity is cooled...

    Problem 7 O/5 points (0%) Humid air at 1 atm, 42 °C dry bulb and 55 % relative humidity is cooled at constant pressure to a temperature 9 °C below its dew-point temperature. Sketch the psychrometric diagram for the process and determine the heat transfer from the air o kJ/kg dry air Cooling coils T2 φ2 T1 ф! 101.3 kPa i H-4」+'Condensate Condensate removal Now Problem (resets attempts) Resets Remaining: 10 Attempts Remaining: 10 Submit Problem 7 O/5 points (0%)...

  • a) Define relative humidity (2 marks) b) Describe the relation between relative humidity, the capacity of...

    a) Define relative humidity (2 marks) b) Describe the relation between relative humidity, the capacity of air to hold moisture a ambient temperature. (2 marks) c) Moist air at 22°C and a wet bulb temperature of 9°C enters a steam spray humidifier. The mass flow of the dry air is 90 kg/min. Saturated water vapor at 110 °C is injected into the mixture at a rate of 52 kg/hr. There is no heat transfer with the surroundings, and the pressure...

  • Moist air enters a duct at 10 °C, 80% relative humidity, and a volumetric flow rate...

    Moist air enters a duct at 10 °C, 80% relative humidity, and a volumetric flow rate of 150 m3/min. The mixture is heated as it flows through the duct and exits at 30 °C. No moisture is added or removed and the mixture stays at 1 atm. Determine the rate of heat transfer and the relative humidity at the exit.