For the given system find
1) The total amount of heat exchange (W)
2) The temperature of the water at the outlet (degC)
All information should be included, the pipe is made of copper
and the internal fluid is water, external fluid is air
For the given system find 1) The total amount of heat exchange (W) 2) The temperature...
A counter-flow heat exchanger is stated to have an overall heat transfer coefficient of 284 W/m2.K when operating at design and clean conditions. Hot fluid enters the tube side at 101°C and exits at 71°C, while cold fluid enters the shell side at 27°C and exits at 42°C. After a period of use, built-up scale in the heat exchanger gives a fouling factor of 0.0004 m2 K/W. The surface area is 93 m². Assume both hot and cold fluids have...
Homework 7 heat transfer 2018-20 1) A horizontal tube of 12.5-mm dimeter with an outer srface temperature of 240°C is placed in a room with an air temperature of 20°C. Estimate the heat transfer rate per unit length of the tube due to free convection. 2) Air at -10°C flows at 10 m/s over the roof plate of two 5m length rooms whose air is at Too-200C. The roof plate is 0.20-m thick concrete (k = 0.6 w/ m. K)....
2. (35P) Ashell-and-tube heat exchanger with 1-shell pass and 20-tube passes is used to heat glycerin (Cp = 2480 J/kg) in the shell, with hot water in the tubes. The tubes are thinwalled and have a diameter of 1.5 cm and length of 2 m per pass. The hot water (Cp=4180 J/kg Centers the tubes at 102°C at a rate of 9 kg/s and leaves at 55°C. Overall heat transfer coefficient U=13900 W/m2C. The glycerin enters the shell at 15°C...
Qi. A flat plate of width 1 m and length 0.2m is maintained at a temperature of 32°C. Ambient fluid at 22"C fBlows across the top of the plate in parallel flow. Determine the average heat transfer coefficient, the convection heat transfer rate from the top of the plate, and the drag force on the plate for the following: (a) The Buid is water flowing at a velocity of 0.5 m/s. o) Water is flowing at a velocity of 2.5...