Here is the energy analysis of the hydronic heating system depicted in the diagram.
The boiler plant consists of two identical boilers, each having the following characteristics:
• Fuel: natural gas
• Burner Type: on/off
• Rated Output = 85 kW
• Rated Efficiency, nFL = 80%
The boilers operate in a “Lead/Lag” arrangement, i.e., Boiler 1 operates first to meet the load (up to its capacity), and Boiler 2 operates as necessary to meet any remaining load.
The pump and motor have the following characteristics:
• Flow Rate = 15 L/s
• Pressure Rise = 160 kPa
• Pump Efficiency = 60%
• Motor Efficiency = 88%
a) Estimate the shaft power (W) required by the pump
b) Estimate the fuel consumption rate of the boiler plant (m3 /hr) during a moment when both boilers are cycled on. Assume the heat content of natural gas is 10.33 kWh/m3 .
c) Consider a period when the heat extraction rates from the loop are as follows: Zone 1 = 30 kW, Zone 2 = 12 kW, Zone 3 = 22 kW. Estimate the heat load to be met by each boiler (kW) during this period.
Please forgive me for any calculation mistake and do comment for any short of queries.
Here is the energy analysis of the hydronic heating system depicted in the diagram. The boiler...
10. A boiler system is being designed for a building expected to require heating for approximately 3,500 hours per year. The LDC is indicated below (left). The total annual heating load is about 280,000 kWh. The load will be met by three identical boilers, with each boiler having the following characteristics: Heating Fuel: natural gas (heat content may be estimated to be = 10.33 kWh/m?). • Burner Type: on/off • Rated Output = 100 kW • Rated Efficiency: NA= 82%...
10. A boiler system is being designed for a building expected to require heating for approximately 3,500 hours per year. The LDC is indicated below (left). The total annual heating load is about 280,000 kWh. The load will be met by three identical boilers, with each boiler having the following characteristics: • Heating Fuel: natural gas (heat content may be estimated to be = 10.33 kWh/mº). • Burner Type: on/off • Rated Output = 100 kW Rated Efficiency: na= 82%...
Load Duration Curve A gas-fired boiler system is being design for a new building. The system will consist of 3 identical boilers, each with rated output = 200 kW. The anticipated LDC is shown below. 600 500 Heating Load 400 [kW] 300 200 100 0 The planned operating sequence is as follows: Boiler-1 fires first to meet whatever load it can, up to its capacity. When Boiler-1 reaches its capacity, Boiler-2 fires second and operates to meet whatever load it...
Question 2: A steam power cycle operates such that the steam exits boiler at 4 MPa, 400C and the condenser pressure is 10 kPa. The efficiency of the turbine and pump is 85% and 90% respectively. a. Draw the process on a Ts diagram and calculate the thermal efficiency. b. If the plant produces 100MW of net power, - what is the steam flowrates in kg/hr? - If the plant uses natural gas as a fuel, determine the flowrate of...
1. 1. The primary energy savings in tep (1 MWh -0.086 tep) and diesel, which involves the direct use of heat from a geothermal resource to cover a heat demand of 100 kW for 3,500 h / year, assuming that this demand will be covered with diesel boiler of average yield 0.8 (for diesel 1.12 tep/ton gas oil), they are: a) 30.1 tep/year, 26.9 ton/year b) 37.6 tep/year, 33.6 ton/year c)41.2 tep/year, 36.8 ton /year 1. 2. A hydraulic pump...
A combined cycle gas turbine/vapor power plant uses the turbine exhaust as the energy source for the boiler. Each power system uses a single turbine. The gas power system is modeled as an ideal air-standard Brayton cycle. The vapor power system is modeled as an ideal Rankine cycle. Given specific operating conditions determine the temperature and pressure at each state, the rate of heat transfer in the boiler, the power output of each turbine, and the overall efficiency. --Given Values--...
you can assume all data Nr 7- FINAL TEST 31 may 2019 1. Enhanced geothermal system. Please calculate amount of water steam at pressure Sbar(a), if saturated water 95 ton per hour throttled from 20 bar to 5 bar(a). 2. District heating boiler house with power output 10 MW consuming wood chips with moisture 40% decide to install flue gas condenser. If flue gas temperature will be 40 C please advice how big will be boiler house power after condenser...
A combined cycle gas turbine / vapor power plant uses the turbine exhaust as the energy source for the boiler. Each power system uses a single turbine. The gas power system is modeled as an ideal air-standard Brayton cycle. The vapor power system is modeled as an ideal Rankine cycle. Given specific operating conditions determine the temperature and pressure at each state, the rate of heat transfer in the boiler, the power output of each turbine, and the overall efficiency....
A natural gas-fired furnace in a Textile Plant is used to provide steam at 140 0C. At times of high demand, the furnace supplied heat to the steam at rate of 30 MJ/s. The plant also uses up to 6 MW of electrical power purchased from the local power company. The plant management is considering converting the existing process plant into a Cogeneration Plant to meet both their process-heat and power requirements. Your job is to come up with some...
a) What is the difference between latent and sensible heat gains in building cooling load analysis? Provide examples of each (2 marks) b) In heating load calculations, it is a normal practice to neglect the solar heat gain Explain why. (2 marks) c) An air conditioned single family detached house with a Figure_Q6A is located in Perth, Australia (Latitude 31° South). The ceiling height is 24 m. The summer floor plan shown in design indoor temperature is 25°C. Outside design...