Question

generator with a rated field current of 5 A was tested, and the following data were taken: a. VT,oc at rated Is was measured

A 200 - kVA, 480 V, 50 Hz, Y connected synchronous generator with a rated field current of 5 A was tested. The following data were taken

VT,oc at rated IF was measured to be 500 V

IL,sc at the rated IF was found to be 250 A

When a rated DC voltage of 20 V was applied to 2 of the terminals, a current of 45 A was measured.

Draw the per phase equivalent circuit of the generator at rated condition

0 0
Add a comment Improve this question Transcribed image text
Answer #1

For the given values of test results, the required equivalent circuit is drawn using the calculations as shown below :

200 KVA 480 V, 50 HZ, Y connection of synchoonous generator Rated field current 5A Data taken is : (Yos 500 V at rated IF = 5

Synchronous reactance at rated field current is Xo Ve BR - RA Asc (288.675) (250) - (0.222) - - 2 So, Хs = 1.133 n EA 288.675

So the equivalent circuit is as above for the given testing conditions.

Add a comment
Know the answer?
Add Answer to:
A 200 - kVA, 480 V, 50 Hz, Y connected synchronous generator with a rated field...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 5. [Synchronous Generator - 15 points] A 200-kVA, 480-V 50-Hz, Y-connected synchronous generator with a rated...

    5. [Synchronous Generator - 15 points] A 200-kVA, 480-V 50-Hz, Y-connected synchronous generator with a rated field current of 5 A was tested, and the following data were taken: a. Vocat rated I was measured to be 500 V b. IL,se at the rated IF was found to be 250 A. c. When a de voltage of 20 V was applied to two of the terminals, a current of 45 A was measured. Draw per phase equivalent circuit of the...

  • 5. [Synchronous Generator - 15 points) A 200-kVA, 480-V 50-Hz, Y-connected synchronous generator with a rated...

    5. [Synchronous Generator - 15 points) A 200-kVA, 480-V 50-Hz, Y-connected synchronous generator with a rated field current of 5 A was tested, and the following data were taken: a. Voc at rated Ip was measured to be 500 V b. ll.sc at the rated Ip was found to be 250 A. c. When a de voltage of 20 V was applied to two of the terminals, a current of 45 A was measured. Draw per phase equivalent circuit of...

  • A 480 V, 60 Hz, 470 kVA, 0.85 PF lagging, 2-pole, Y-connected synchronous generator has a...

    A 480 V, 60 Hz, 470 kVA, 0.85 PF lagging, 2-pole, Y-connected synchronous generator has a synchronous reactance of XS=0.016 Ω and an armature resistance of RA=0.016 Ω. At rated conditions the core losses are 7 kW. Friction losses and field winding losses are 8 kW. Suppose the machine is connected to an infinite bus (hence the terminal voltage is fixed) and it is running at the rated conditions. a) What is the rotor speed in rpm? b) Calculate the...

  • 3. A 480 V, 60 Hz, 470 kVA, 0.85 PF lagging, 2-pole, Y-connected synchronous generator has...

    3. A 480 V, 60 Hz, 470 kVA, 0.85 PF lagging, 2-pole, Y-connected synchronous generator has a synchronous reactance of Xs=0.0162 and an armature resistance of RA=0.0.1622. At rated conditions the core losses are 7 kW. Friction losses and field winding losses are 8 kW. Suppose the machine is connected to an infinite bus (hence the terminal voltage is fixed) and it is running at the rated conditions. a) What is the rotor speed in rpm? b) Calculate the phase...

  • A 12 kV, 300 MVA synchronous generator is tested at a field current of 200 A....

    A 12 kV, 300 MVA synchronous generator is tested at a field current of 200 A. The open-circuit voltage was found to be 10 kV and the short-circuit current was 7.5 kA. The stator resistance was measured at 0.1 ohms per phase. i) Find the value of the synchronous reactance in per-unit. [ 2 marks ] ii) The synchronous generator is delivering half rated output at a terminal voltage of 5% below rated voltage and a power factor of 0.7...

  • A 2300 V (terminal voltage), 1000 kVA, 0.8 PF lagging, 60-Hz, two pole, Y connected synchronous g...

    A 2300 V (terminal voltage), 1000 kVA, 0.8 PF lagging, 60-Hz, two pole, Y connected synchronous generator has a synchronous reactance of 1.1 2 and an armature resistance of 0.15 Ω. At 60Hz, its friction and windage losses are 24 kW, and its core losses are 18 kW The field circuit has a dc voltage of 200 V, and the maximum If Ir is 10 A. The resistance of the field circuit is adjustable over the range from 20 to...

  • A 2300-V 1000-kVA 0.8-PF-lagging 60-Hz two-pole Y-connected synchronous generator has X, = 1.1Q and RA 0.15Q....

    A 2300-V 1000-kVA 0.8-PF-lagging 60-Hz two-pole Y-connected synchronous generator has X, = 1.1Q and RA 0.15Q. At 60 Hz, its friction and windage losses are 24 kW, and its core losses are 18 kW. The field circuit has an adjustable dc source. The OCC of this generator is shown in the following figure. (a) How much field current is required to make V, equal to 2300 V when the generator is running at no load? (b) What is the internal...

  • Assignment 4 An 11 kV, 50-Hz, Y-connected synchronous generator has a synchronous reactance of Xs-0.5Ω and...

    Assignment 4 An 11 kV, 50-Hz, Y-connected synchronous generator has a synchronous reactance of Xs-0.5Ω and armature resistance, Ra-005Ω. The terminal voltage in all working conditions is assumed constant and equal to the rated voltage. The generator is delivering a load current of 2000A at 0.8 PF leading a. Draw the per-phase equivalent circuit of the generator. b. Calculate the induced EMF, EA. c. Calculate the real and reactive power delivered at the generator terminals. d. Sketch the phasor diagram...

  • A 3-phase, 7 kVA, 400 V, 2-pole, star-connected synchronous machine has negligible armature resis...

    A 3-phase, 7 kVA, 400 V, 2-pole, star-connected synchronous machine has negligible armature resistance and Xs-60/phase at rated terminal voltage The machine first runs as a generator in parallel with 3-phase, 400 V, 50 Hz power supply 111 Determine the generated voltage and torque angle of the machine operating as a generator, delivering rated kVA at 0 9 pf lagging Draw and label the corresponding phasor diagram for this condition 1 12 If the field excitation is increased by 18%...

  • Question 5 (Svnchronous machines) a. A synchronous generator connected to an infinite grid has its frequency and terminal b. A six-pole, Y-connected three-phase synchronous machine rated 208 V (line-...

    Question 5 (Svnchronous machines) a. A synchronous generator connected to an infinite grid has its frequency and terminal b. A six-pole, Y-connected three-phase synchronous machine rated 208 V (line-to- voltage fixed. What is the effect of increasing the excitation current in this case? line), 5500 VA has a synchronous reactance of 8 2 per phase at rated terminal voltage. It is operating as a generator connected to an infinite grid Determine the excitation voltage and the power angle if the...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT