1. [20 points] Choose the right answer. a) If phase current of a wye-connected three-phase system...
b) A 1MW, 3300 V, 50 Hz, wye-connected, 3-ф, twenty four-pole, synchronous motor has a synchronous reactance of 3.24 2 per phase. Assume armature resistance is negligible. This machine is connected to an infinite bus-bars at 3300 V. Its field excitation is adjusted to provide P.F-1 at rated load Calculate: 0 the internal generated voltage EA and armature current la at rated conditions (S marks) ii) the maximum power and torqu e that the motor can deliver with its Ir...
A balanced three-phase network supplies a balanced load through a three-phase wye-wye connected transformer as shown in the following figure. Transformer Supply Network B8 Load Y-Y The wye-wye connected transformer has the following parameter: S 25 MVA Xir 15% 240/132 kV The three-phase load parameters are: Pload 20 MW pfload 0.8 The three-phase supply network line voltage and short circuit current are: Vnet 225 kV Inet_short= 15 kA. A. Calculate primary and secondary current rating. B. Calculate trans former actual...
Problem 2 A 15 HP, 96% efficient, three-phase Wye-connected synchronous motor is connected to a 480 VAC, 60 Hz power supply. The field excitation is set such that the power factor is 0.97 leading. The machine draws 9 kW from the supplv. The per-phase armature reactance is 9500. Find the internally generated voltage, E, Calculate the motor torque angle, δ. Draw the phasor diagram, showing Vn E, XsL, IA ,Θ and δ. a. b. c. Problem 2 A 15 HP,...
Problem 4 Three ideal single-phase transformers are connected in a delta/wye configuration with the primary side of the three-phase transformer rated at 120 kV and the secondary side rated at 13.8 kV. The rated power of the transformer bank is 20 MVA. One side of the transformer bank is connected to a 120 kV transmission line, and the other side is connected to a three-phase load of 15 MVA at 0.85 lagging power factor. Compute the following: a) The turns...
a. Three single phase step-up transformers rated at 40 MVA, 13.2 kV/80 kV are connected in delta-wye on a 13.2 kV transmission line. If they feed a 90 MVA load calculate the following: i. The secondary line voltage ii. The current in the transformer windings iii. The incoming line currents iv. If the transformer types are two (2) additive and one (1) subtractive draw the connection diagram for the configuration stated using physical representation. b. A 3-phase squirrel cage motor has twelve (12) leads (labelled 1 to...
4-9 Question Completion Status: QUESTION 4 A three phase delta source is connected to a three phase transformer. The primary of the transformer is connected in a delta configuration The line voltage on the primary is 240V. The turns ratio is 2:1. The secondary of the transformer is connected in a wye configuration. A wye connected load is attached to the secondary of the transformer. Each of the three load resistors has a resistance of 10 ohms. What is the...
I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....
I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....
4. Explain the conditions for parallel operation of synchronous generators. A three phase, wye connected, synchronous generator is rated 150 MW, 0.85 lagging power factor, 12.6 kV, 60 Hz, and 1800 rpm. Each winding has an armature resistance of 0.0522 and a synchronous reactance of 0.612. Draw the phasor diagram with values, show torque angle and determine the induced voltage for the condition of rated load. (30 pts)
A balanced positive-sequence wye-connected 60-Hz three-phase source has line-to-line voltages of VL = 440 V rms. This source is connected to a balanced wye-connected load. Each phase of the load consists of a 0.5-H inductance in series with a 50-Ω resistance. Assume that the phase of Van is zero. home / study / engineering / electrical engineering / electrical engineering questions and answers / A Balanced Positive-sequence Wye-connected 60-Hz Three-phase Source Has Line-to-line Voltages ... Question: A balanced positive-sequence wye-connected...