Ans)
A)
Given
the primary rated current is (as it is star connected line current is same as phase current)
secondary current is
===================
B)
Reactance referred to primary is
===============
C)Reactance referred to secondary is
A balanced three-phase network supplies a balanced load through a three-phase wye-wye connected transformer as shown...
Problem 4 Three ideal single-phase transformers are connected in a delta/wye configuration with the primary side of the three-phase transformer rated at 120 kV and the secondary side rated at 13.8 kV. The rated power of the transformer bank is 20 MVA. One side of the transformer bank is connected to a 120 kV transmission line, and the other side is connected to a three-phase load of 15 MVA at 0.85 lagging power factor. Compute the following: a) The turns...
Question I The rating of a three phase three winding transformer are: Y-connected 10 KV 40 MVA Secondary Y-connected 22 KV 40 MVA A-connected 4 KV 15 MVA Primary Tertiary Neglecting winding resistance and exciting current, the per unit leakage reactance are: Mps 9.6 % pu on 40 MVA, 11022 KV xm = 7.2 % pu on 40 MVA, I 10/ 4 KV Xsti: 12 % pu on 40 MVA, 22/ 4 KV Determine the era nyimpedances of the transformer...
A delta-wye connected transformer is shown in Figure below. This is a 220 kV to 450 kV transformer, line-line, RMS. The 'X' side is the 220 kV side. Assume that Phase A voltage on the X' side has zero phase angle (that is, use VaX as the phase reference) 1) What is the turns ratio NX: NH? 2) Draw phasor diagrams of the primary and secondary voltages. Be sure to get relative phase angles right. 3) If a balanced load...
The ratings of a three-phase, three-winding transformer are Y connected, 66 kV, 20 MVA Primary (1): Secondary (2):Y connected, 13.2 kV, 15 MVA Tertiary (3): A connected, 2.3 kV, 5 MVA Neglecting winding resistances and exciting current, the per-unit leakage reactances are: X12 0.08 on a 20-MVA, 66-kV base X13 0.10 on a 20-MVA, 66-kV base X23 0.09 on a 15-MVA, 13.2-kV base (a) Determine the per-unit reactances Xi, X2, X3 of the equivalent circuit on a 20- MVA, 66-kV...
Solution of two part please with steps Question 1: Ve-le The rating of s three phase three winding transformer are: Y-connected un KV 40 MVA Y-connected 22 KV 40 MVA 4 KV 15 MVA Primary Secondary Tertiary A-connected Neglecting winding resistance and exciting current, the per unit leakage reactance are X 9.6 % pu on 40 MVA. 110/22 KV X7.2 % pu on 40 MVA, 110/ 4 KV Xg 12 % pu on 40 MVA, 22 4 KV a) Determine...
1. In order to meet an emergency, three single-phase transformers with 12.470/7.200 V are connected in Delta-Wye to form a three-phase transformer which is fed by a 12.470 V transmission line. If the transformer supplies 60 MVA to a load, calculate: (3 marks) a. The turns ratio for each transformer b. The currents in the primary and secondary windings of the transformer c. The primary and secondary transmission line currents 2. A Wye-Delta transformer is connected to a 66 kV...
three-phase transformer is rated at 12 kV/135 kV, 100 MVA. It has the following equivalent circuit parameters (referred to the primary winding where appropriate) : • primary resistance R1 = 0.03 ohms, secondary resistance R2’ = 0.04 ohms • primary leakage reactance X1 = 0.1 ohms, secondary leakage reactance X2’ = 0.1 ohms • magnetising reactance XM = 16 ohms, core-loss resistance RC = 200 ohms. In your calculations, you should use the simplified equivalent circuit. i) The transformer is...
3. A balanced three-phase delta connected load with 15+j10 ohms load on each balanced, wye connected source with Van branch is supplied by a -7.6240 KV, while the transmission line impedances are 1+7j on each line. Calculate the line currents (currents on the transmission lines) la, 1b, and 1c. (Hint: convert the Δ configured load into a Y configured load
Problem 1: A three-phase transformer has the following name plate data: Rated Power Primary voltage Secondary Voltage Excitation reactance Series Impedance 150 MVA 230 kV 32 kV 30 (pu) 0.02+0.15j (pu) The transformer is Y/A connected. Answer the following questions: a) What are the nominal (rated) primary and secondary line currents?| b) What is the nominal value of the Delta-side winding (internal) current? c) What is the secondary to primary winding turn ratio? d) The transformer is supplying 150 MVA...
Question 2: Three phase circuit. (100p) A wye connected generator supplies a delta connected balanced load through short feeder. seree the load line to neutral voltage as reference voltage phase angle zero. 02.1 Q2.2 Q2.3 Q2.4 Draw the equivalent circuit. 10p Calculate the load line-to-neutral voltages and line-to-line voltages. 20p Calculate the delta load currents and feeder currents. 20p Calculate the supply wye connected generator line-to-neutral voltages. Is the obtained values are acceptable? Calculate the generator real and reactive power...