1. A balanced delta-connected load has 12 +j16 ohms impedance per phase, and is energized by 208 V line-to-line. The phase sequence is ‘a-b-c'. (a) Find the line and phase voltages and currents at the delta load, and show them in a phasor diagram. (b) If the delta-connected load is rewired and connected in wye, show the line and phase voltages and currents at the wye load in a phasor diagram.
A balanced wye-connected load and a balanced delta con- hected load are supplied by a three-phase 480-V 50 HZ generator. The ranch impedance of the wye and della are 10/30° 2 and 20/-50° 2. respectively. Determine the active and reactive powers drawn by each three loads. Determine the phasor voltage and phase any one branch of each three-phas e branch of each three-phase load, and substitute into wer equation for balanced three-phase loads. Given ise angle of V is 30...
508 CHAPTER 11 . POLYPHASE CIRCUITS 11.40 In a balanced three-phase system, the source has an aboc phase-sequence and is connected in delta. There are two rallel wye-connected loads. The phase impedance of load i and load 2 is 4 The line impedance connecting the source to the loads is 0.3 + j0.2 2. If the curre IAN! = 10/20-Arms, find the delta currents in the source 4 Ω and 10 +/4 Ω, respectively. nt in the a phase of...
Question 2: Three phase circuit. (100p) A wye connected generator supplies a delta connected balanced load through short feeder. seree the load line to neutral voltage as reference voltage phase angle zero. 02.1 Q2.2 Q2.3 Q2.4 Draw the equivalent circuit. 10p Calculate the load line-to-neutral voltages and line-to-line voltages. 20p Calculate the delta load currents and feeder currents. 20p Calculate the supply wye connected generator line-to-neutral voltages. Is the obtained values are acceptable? Calculate the generator real and reactive power...
Three single-phase transformers rated at 250 kVA, 7200 V/600 V, 60 Hz, are connected in wye- delta on a 12.47 kv, 3-phase line. If the load is 450 kVA, calculate: a. The currents in the incoming and outgoing transmission lines b. The currents in the primary and secondary windings 1. sratod t 200 w 3o0 v/6oO V 60 Hz are used to raise the Three single-phase transformers rated at 250 kVA, 7200 V/600 V, 60 Hz, are connected in wye-...
I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....
I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....
A balanced three-phase delta-connected load is connected to a balanced three-phase delta-connected source via a transmission line. The line-line voltage for the source is 100∟0° V/phase and the impedance of load is (27 + j18) Ω/phase. The transmission line has an impedance of (1 + j4) Ω/line. a) Draw the complete schematic of the power system showing the location of wattmeters. (Two-Wattmeter system is considered for this problem). Phase “a” could be considered as a reference phase. b) What must...
In a balanced three-phase system, the source is wye-connected and the source voltage of phase A is Van = ∠ 120 20 V. The load consists of two balanced wyes in parallel with phase impedances of 8 + j6 Ω and 12 + j8 Ω. If the line impedance is zero, find the line currents and the phase currents in each load. (Hint: use per phase analysis, then do angle shift for each phase.)
A balanced three-phase network supplies a balanced load through a three-phase wye-wye connected transformer as shown in the following figure. Transformer Supply Network B8 Load Y-Y The wye-wye connected transformer has the following parameter: S 25 MVA Xir 15% 240/132 kV The three-phase load parameters are: Pload 20 MW pfload 0.8 The three-phase supply network line voltage and short circuit current are: Vnet 225 kV Inet_short= 15 kA. A. Calculate primary and secondary current rating. B. Calculate trans former actual...