1. A balanced delta-connected load has 12 +j16 ohms impedance per phase, and is energized by...
A balanced delta connected load has a per phase impedance of 12+j21 ohms. The load is supplied power from a source with line to line voltage of 480 V through a distribution line. The line impedance is 2 + j4.5 ohms. What is the current magnitude in the distribution line? of the below questions. A balanced A connected load has a per-phase impedance of 12+,21 22. The load is supplied power from a source with line-to-line voltage of 480 V...
Sketch the 3-phase systems, and show your calculations: Problem (a): A positive-sequence balanced thrcc-phase wyc-connected source supplics powcr to a balanced wyc-connected load. The line voltage is 100 V. The line impedance is 2 ? per phase, and the load impedance is 50 +j30 ? per phase. Determine the load voltages if V an-00. Problem (b): A positive-sequence balanced three-phase wye-connected source supplies power to a balanced wye-connected load. The magnitude of the line voltages is 208 V rms. If...
I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....
I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....
A balanced delta connected 3 phase load with per phase impedance of Z1 = 3 + j9 (Ohm) is connected in parallel to a balanced 3 phase star connected load with per phase impedance: Z2 = 6 + j16 (Ohm). Their connection is shown in the Picture attached. This load combination is connected to a balanced 3 phase 415V (line-to-line) supply. Find the magnitude of the line current drawn from the supply. Enter your results in Amps with one digit...
A wye-delta balanced three-phase system with a positive phase sequence has negligible line impedance and a load impedance of Z, = (12+j8) 12. If LAB=14.42286.31° A-rms, determine the line currents and the source voltages.
Question 2: Three phase circuit. (100p) A wye connected generator supplies a delta connected balanced load through short feeder. seree the load line to neutral voltage as reference voltage phase angle zero. 02.1 Q2.2 Q2.3 Q2.4 Draw the equivalent circuit. 10p Calculate the load line-to-neutral voltages and line-to-line voltages. 20p Calculate the delta load currents and feeder currents. 20p Calculate the supply wye connected generator line-to-neutral voltages. Is the obtained values are acceptable? Calculate the generator real and reactive power...
A balanced Y-connected load with a phase impedance of 10 + j 4 Ω is supplied by a balanced, positive sequence Δ-connected voltage source having Vab 208∠0o V. Given that the line impedance is 0.8 + j 0.3 Ω per phase. (i) Construct a single-phase equivalent circuit of the three-phase system. (ii) Calculate the phase currents of the load. (iii) Calculate the line voltages at the load.
2. Two balanced three-phase loads are connected in parallel. One load with per phase impedance 21 ?, is connected in delta, and the other load has per phase impedance 15 2 and is connected in wye. Ignore the line impedance. If the line voltage is a 208230° Vrms, determine (a) the phase voltage for phase-a, ) the line current Ia*, (c) the phase currents in the delta load (d) the complex power of the load and the power factor.
3. A balanced three-phase delta connected load with 15+j10 ohms load on each balanced, wye connected source with Van branch is supplied by a -7.6240 KV, while the transmission line impedances are 1+7j on each line. Calculate the line currents (currents on the transmission lines) la, 1b, and 1c. (Hint: convert the Δ configured load into a Y configured load