Question

Air at 104°F with a relative humidity of 30% enters a heater and leaves at 77°F...

Air at 104°F with a relative humidity of 30% enters a heater and leaves at 77°F with a relative humidity of 20%. The volumetric flow rate leaving the system is 1,000 in3 per second. Using the psychrometric chart determine the flow rate of dry air (lb/min) through the dryer, whether water is evaporated or condensed, and the rate at which the condensation or evaporation occurs (lb/min)

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Volumetric flowrate of leaving air = 1000 in3/s

1 inch = 0.0254 m

= (0.0254) 3 ×1000= 0.016387 m3/s

T (out) = 77°F = 25°C = 298.15 K

P = 1 atm= 1.013×105 Pa

n = PV/(RT)

n = (1.013×105× 0.016387) /(8.314×298.15)

n = 0.66967 mol/s = 40.1804 mol/min

Outlet R H = 20%

At T = 77°F and R. H = 20%

From psychometric chart

Y'(outlet humidity ratio) = 0.0039 Kg water/kg air

Outlet mole ratio =

(0.003909) (M.W of air/M.W of water) = 0.003909(29/18) = 0.0062978

Total moles of outlet gas = 40.1804 mol/min

Dry air flowrate through dryer = 40.1804/(1+0.062978) = 39.9289 mol/min

M. W of dry air = 29 g/mol = 0.029 Kg/mol

Mass rate of dry air = 39.9289(0.029) =

1.1579 Kg/min

1 Kg = 2.205 lb

Mass rate of dry air (Gs) = 1.1579(2.205) =

2.5532 lb/min

Inlet air conditions

T = 104°F , R. H = 30%

From psychometric chart

Y(inlet humidity ratio) = 0.013877

Inlet humidity ratio is greater than outlet humidity ratio, hence condensation of water occurs

Doing material balance

Water condensed = Gs (Y - Y')

Gs - dry air flowrate

Water condensed = 2.5532(0.013877- 0.003909)

= 0.02545 lb/min

Please upvote if helpful

Add a comment
Know the answer?
Add Answer to:
Air at 104°F with a relative humidity of 30% enters a heater and leaves at 77°F...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Air enters a heating and humidification system at 5◦C, 50% relative humidity. The air first passe...

    Air enters a heating and humidification system at 5◦C, 50% relative humidity. The air first passes over a heater, and is then humidified with steam. The steam is supplied at 200 kPa pressure and 300◦C. The air leaves the system at 30◦C, 60% relative humidity. (a) Determine the heat transfer to the air, per unit mass dry air. (b) Determine the temperature and relative humidity of the air leaving the heating section (i.e., prior to the humidification section). (c) Determine...

  • Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady...

    Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady state. The volumetric flow rate of the incoming air is 895 ft3/min. Liquid water at 68°F enters the cooler and fully evaporates. Moist air exits the cooler at 70°F, 1 atm. There is no significant heat transfer between the device and its surroundings and kinetic and potential energy effects can be neglected. a)Determine the mass flow rate of the dry air in lb(dry air)/min....

  • 1. Wet solids pass through a continuous dryer. Hot dry air enters the dryer at a...

    1. Wet solids pass through a continuous dryer. Hot dry air enters the dryer at a rate of 400 kg/min and mixes with the water that evaporates from the solids. Humid air leaves the dryer at 50°C containing 2.44 wt% water vapor and passes through a condenser in which it is cooled to 10°C. The pressure is constant at 1 atm throughout the system. a. At what rate (kg/min) is water evaporating in the dryer? b. Use the psychrometric chart...

  • The atmospheric air 32 °C dry bulb temperature and 70% relative humidity supplied to the cooling...

    The atmospheric air 32 °C dry bulb temperature and 70% relative humidity supplied to the cooling coil at a rate of 45m3/min. The air cooling to the saturated state and leaving at a temperature of 16 °C. Determine: a- Specific humidity at each state. b- Wet bulb and dew point temperatures at the final state c- Final relative humidity. d- Mass of water condensed. e- Rate of heat removed from the air in kW. f- Show the process on Psychrometric...

  • Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady...

    Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady state. The volumetric flow rate of the incoming air is 1765 ft3/min. Liquid water at 68°F enters the cooler and fully evaporates. Moist air exits the cooler at 70°F, 1 atm. There is no significant heat transfer between the device and its surroundings and kinetic and potential energy effects can be neglected. A. Determine the mass flow rate of the dry air in lbm(dry...

  • Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady...

    Air at 95°F, 1 atm, and 10% relative humidity enters an evaporative cooler operating at steady state. The volumetric flow rate of the incoming air is 1765 ft3/min. Liquid water at 68°F enters the cooler and fully evaporates. Moist air exits the cooler at 70°F, 1 atm. There is no significant heat transfer between the device and its surroundings and kinetic and potential energy effects can be neglected. A. Determine the mass flow rate of the dry air in Ibm(dry...

  • Ouestion 2 (3 marks) Moist air enters the evaporator of an air conditioner at t. 26°C...

    Ouestion 2 (3 marks) Moist air enters the evaporator of an air conditioner at t. 26°C and -70 %. After leaving the evaporator, the relative humidity o,100% and the temperature of the air t tpl-7°C, where tdp is the dew point temperature of the air entering the evaporator. Given: - The mass flow rate of the air passing through the evaporator: 1000kg of dry air/h - The mass flow rate of the air passing through the condenser: 2500kg of dry...

  • corn containing 5% water. Dry air enters the dryer at 70°C and 1 atm and the...

    corn containing 5% water. Dry air enters the dryer at 70°C and 1 atm and the outlet air is at 55°C with a relative humidity of 50%. Calculate the mass flowrate of corn enters the dryer and volumetric flow rate of inlet air. containing 55% water enters a continuous tunnel dryer and leaves at a rate of 500 kg/h

  • Moist air at 20° c, 1 atm, and 43% relative humidity and a volumetric flow rate...

    Moist air at 20° c, 1 atm, and 43% relative humidity and a volumetric flow rate of 900 m/hrs. enters a control volume at steady state and flow along a surface maintained at 65 C, through which heat transfer occurs. Liquid water at 20" C is injected at a rate of 5 kg/hr and evaporates into flowing stream. For the control volume, Wa=0, and kinetic and potential energy effects are negligible. Moist air exits at 32c, 1 atm, (a) draw...

  • 150 ft3/min of air at 80F dry-bulb temperature and 70% relative humidity enters an air conditioning...

    150 ft3/min of air at 80F dry-bulb temperature and 70% relative humidity enters an air conditioning unit and leaves it as saturated air at 50F. Part of the moisture in the air that condensate is collected and removed at 55F. Draw the cycle on the attached chart and a)Determine the rates of heat removal from the air. b)Determine the rate of moisture removal from the air

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT