1. A 3-phase load consumes 90 kW of power at a leading PF of 0.6. Assume...
A three-phase load of 15 kVA with a PF of 0.8 lagging is connected in parallel with a three-phase load of 36 kW at 0.6 PF leading. The line-line voltage is 2000V. a) Find the total complex power and power factor. Is it inductive or capacitive? b) How much kVAR is needed to make the PF unity? c) What is the magnitude of the current going into the total load?
1, Two balanced three-phase loads are in parallel. Load 1 draws 10 kW at 0.8 PF lagging Load 2 draws 20 kVA at 0.6 PF leading a. b. The loads are supplied by a balanced three-phase 480 Vu source. (a) Draw the power triangle for the combined load. (b) Determine PF of the combined load. (c) Determine the magnitude of the line current from the source. (d) Y-connected inductors are now installed in parallel with the combined load. What value...
(4) Three single-phase AC loads draw power from the same 12020으 kms source. Load 1 draws 120 w at a lagging PF of 0.75, Load 2 draws 75 VA at a leading PF of 0.6 and Load 3 draws 100 VA at a leading PF of 0.8. Determine the complex power consumed by each load. Calculate the rms current phasor for each load. a. b.
10. Two loads connected in parallel draw a total of 2.4 kW at 0.8 pflagging from a 120-V rms, 60- Hz line. One load absorbs 1.5 kW at a 0.707 pf lagging. Determine: (a) the pf of the second load, INV 11. Calculate the line currents for the system shown in figure. Calculate also the total power and reactive power consumed by the load. w 12. For the balanced three-phase circuit in Fig.. Calculate the line currents, the phase voltage...
Problem 4: A plant consumes 20 kW of power. If the load power factor is 0.9 lagging, what is the angle by which the load current lags the load voltage? What is the load current, I, if the load voltage is 240/10° VrMS? Answers: 25.84,-92.59/-15.849 ARMS
3. (40 points) Three-phase loads are connected in parallel across a 24 KV (line-line three-phase power supply. Load 1: 120 KVA at 0.8 power factor leading; Load 2: 180 KW at 0.6 power factor lagging, Load 3: 40 KW at unity power factor Find the total complex power of three loads; (ii) Draw the power triangle of the combined load (ii) Find the overall power factor (iv) Find the line current (magnitude only) in the power supply line.
QUESTION 4: AC POWER - PF CORRECTION points) The voltage and current for a load Z are given by Vrms = 120290° and IRMS = 40230 Volts and Amps respectively; F-60 Hz. Do the following: • Determine the load Z6 • Determine the PF • State whether this is a leading/lagging PF. • Determine the Power delivered to the Load (Watts) • Sketch the power triangle and include all relevant information (quantities, units etc.) • What type of element must...
A three-phase blanced load connected in Y consumes 3kW(total of the 3 phases) at a power factor of 0.8(-). A balanced Y load of capacitors will be added in parallel so that the power factor of the combination improves to 0.85(-). If the frecuency is 60 Hz and the line-to-line voltages a a balanced set of 200 Vrms, get: a) The magnitude of the line current IaA that the line consumes before placing the capacitors. b) The value of the...
4. In the circuit below, the impedance Z1 dissipates 10 kW with a power factor of 0.80 lagging. Z2 draws 14 kVA apparent power with a power factor of 0.70 leading. The frequency of the source is 60 Hz 208 V (rms)- Z1 (a) Determine the impedance Zi. (b) Determine the impedance Z2. (c) Determine the complex power Ssource for the voltage source. (d) Sketch and label the power triangle for each impedance, labeling the lengths of the sides and...
2. Consider the given 3-phase circuit. Assume the load voltage, PAB = 30L30, Kms (3) Are the loads connected in Wye or Delta configuration? Explain your selection. b. a. (3) Are the sources connected in Wye or Delta configuration? Explain your selection. (5) Draw the single-phase equivalent of the given circuit. Label the line-to-neutral voltage numerically. c. d. (4) Calculate the rms line current phasor in each phase. e. (5) Calculate the rms source voltage phasor in each phase. f...