Data regarding resistance of conductor collected from some ieee studies and it can be calculated by taking resistivity of aluminum conductor and length. We can calculate by placing it in the resistance formula as per ohms law. Thank you..
3 phase like what Numerical Example Power has to be carried over a distance of 200...
Solve all questions and submit through blackboard by March 26, 2020 Q. 1 (i) Classify short, medium and long transmission lines based on distance (km). (ii) Classify transmission lines (low, medium, high, extra high) based on voltage levels (kV). (iii) What is commonly used conductor material for overhead transmission lines. Why Aluminum and copper materials are not used for conductors of transmission lines. Q. 2: A 3-phase, 230 kV transmission line having a length of 50 km is composed of...
[2000] Question 3: A 500-km, 500-kV, 60-Hz, uncompensated three-phase line has a positive sequence series j4.4 x 10-6 S/ impedance z - j0.35 ohm/km and a positive-sequence shunt admittance y km. If at full load, the line delivers 700 MW at unity power factor and at 475 kV, Calculate The nominal voltage level for this line a) the exact ABCD parameters for this line, the sending- end voltagnb transferred, and max theoretical power that can be transferred, and c) d)...
A 230-kV, three-phase transmission line has a per phase series impedance of z = 0.05j0.45 2 per km and a per phase shunt admittance ofy = j3.4 x 10-6 siemens per km. The line is 80 km long. Using the nominal r model, determine (a) The transmission line ABCD constants. Find the sending end voltage and current, voltage regulation, the sending end power and the transmission efficiency when the line delivers (b) 200 MVA, 0.8 lagging power factor at 220...
A 60 km-long three-phase 60-Hz transmission line has per phase line inductance of 1.554 mH/km and per phase line resistance of 10.33 mΩ/km. It supplies a three-phase Y connected 100 MW 0.9 lagging power factor load at 215 kV line-line voltage. Calculate the voltage regulation and efficiency of transmission.
Problem 3: A three-phase, 60 Hz transmission line is built with an ACSR conductor. The conductor diameter is 0.68 inch, GMR = 0.023 ft., and AC resistance of 0.342 /mile at 50°C. The conductors are laterally spaced with D= 1.7 m between conductor centers. The line is 50 km long and supplies a 5 MW load. The line to line load voltage is 13.2 kV. [40 points] (a) Find the total impedance of the line. (b) Determine the sending-end voltage,...
A 3-phase 60 Hz 50 km transmission line delivers 20 MW of power to a load at 69 kV and a power factor of 0.8 lagging. The line has the following parameters r = 0.1112/km L = 1.11 mH/km C = negligible Determine: The line impedance. (4 Marks) The "receiving end" phase voltage and current (7 Marks) The "sending end" voltage and current (10 Marks) The voltage regulation. (4 Marks)
A short 3-phase, 33-kV power transmission line delivers a load of 7-MW at a power factor of 0.85 lagging and 33-kV. If the series impedance of the line is 20+j30 Ohms/phase, calculate The ABCD constants (parameters) The sending end voltage The load angle The voltage regulation The transmission efficiency
QUESTIONS 1- A 69-kV, three-phase transmission line is 20 km long. The line has a per phase series impedance of 0,120 + 10,4325 per km. Detemine the sending end voltage, voltage regulation, the sending end power, and the transmission efficiency when the line delivers (a) 60 MVA, 0.8 lagging power factor at 60 kV. (b) 110 MW, unity power factor at 60 kV
power system A single-circuit 60-Hz high voltage power transmission line is 370 km (230 mi) long. The conductors are Rook with flat horizontal configuration and 7.25 ms=(23.8 ft.) conductor spacing. The load on the line is 125 MW at 100% power factor. Use attached Tables A3 to A3to determine; The sending end voltage Vs The sending end current Is The sending end power Ps The percentage voltage regulation The transmission efficiency Given that Ds for the Rook conductor is 0.0327...
4. A 500 km, 500kV,60 Hz three-phase transmission line has a positive sequence series impedance z =j 0.38.2/km and a shunt admittance y =j 4.0 x 10-6S/km. Line losses are neglected. a. Calculate the line's characteristic impedance Zc, the propagation constant y and the exact ABCD parameters of the line... b. Calculate the surge impedance loading (SIL) in MW and the maximum power that the line can deliver at rated voltage C. At full load the line delivers 1000 M...