Solve all questions and submit through blackboard by March 26, 2020 Q. 1 (i) Classify short,...
Example 22 A three-phase, 60-Hz, completely transposed 345-kV, 200-km line has two 795,000-cmil (403-mm2) 26/2 ACSR conductors per bundle and the following positive-sequence line constants: z 0.032 + 10.35 /km y j4.2 x 10-6 S/km Full load at the receiving end of the line is 700 MW at 0.99 p.f. leading and at 95% of rated voltage. Assuming a medium-length line, determine the following: a. ABCD parameters of the nominal π circuit b. Sending-end voltage Vs, current Is, and real...
Problem 3: A three-phase, 60 Hz transmission line is built with an ACSR conductor. The conductor diameter is 0.68 inch, GMR = 0.023 ft., and AC resistance of 0.342 /mile at 50°C. The conductors are laterally spaced with D= 1.7 m between conductor centers. The line is 50 km long and supplies a 5 MW load. The line to line load voltage is 13.2 kV. [40 points] (a) Find the total impedance of the line. (b) Determine the sending-end voltage,...
Q2. Draw the nominal π circuit that is used to represent the medium-length transmission line model with total series impedance Z and total shunt admittance Y. Then derive the equations to express the ABCD parameters (a) 20% (b)A 200 km, 230 kV, 50 Hz three-phase overhead transmission line has a positive-sequence series impedance z (0.08 + j0.48) Ω/km, and a positive-sequence shunt admittance y-j3.33 x 10T° S/km. At full load, the line delivers 250 MW at 0.99 power factor lagging...
power system
A single-circuit 60-Hz high voltage power transmission line is 370 km (230 mi) long. The conductors are Rook with flat horizontal configuration and 7.25 ms=(23.8 ft.) conductor spacing. The load on the line is 125 MW at 100% power factor. Use attached Tables A3 to A3to determine; The sending end voltage Vs The sending end current Is The sending end power Ps The percentage voltage regulation The transmission efficiency Given that Ds for the Rook conductor is 0.0327...
Problem #1 Part I (50 points) Consider the following one-line diagram of a three-phase power system. Assume that the system has the following base quantities: S3 100 MVA, and VbaselL 38 kV at the generator side. The rated line-to-line terminal voltage of the generator (BUS 1) is 38 kV. A single-circuit three-phase transposed overhead line composed by one ACSR Partridge conductor per phase with vertical configuration. The transmission line length is 50 km and the distance between phases a-b, b-c...
please,I need the solution within 15 min
Question 3 b: /Mark 17] (CLO 3 and 4). A 236 kV, three-phase medium transmission line is 211 km long. The line has a per phase series resistance R = 0.041 N, inductive reactance XL =j 0.3012, per kilo-meter for both, and shunt capacitive reactance X = 211.8 k2-km. Using the medium line model (nt- model) of transmission line to calculate: a- The transmission line A, B, C, and D constants. (Mark 3)...
Problem #1: A single-circuit, 500 kV, 60 Hz, three-phase transmission line is 250 km long. The characteristic parameters of the transmission line are: x0.4 0/km At full load, the line delivers 1000 MVA at 500 kV with 0.80 PF lagging y j4 x 10 S/km r0.045 /km a. Assume that identical shunt reactors (inductors) are connected from each phase conductor to neutral at both ends of the line during light-load conditions, providing 50% total shunt compensation. The reactors are removed...
The answer = 14.49% ; 94.47%
III. A three-phase overhead transmission line, 80 km long, delivers 24 MVA at 66 kV, 50 Hz, 0.8 power factor lagging. The line conductors have a diameter of 1.5 cm and are horizontally spaced at a distance of 2.5 m. Determine the voltage regulation and efficiency of the line. The line resistance is 8.72 ohm/phase.
Show the solution for the following problem 1. A short, 230 kV transmission line has an impedance of 5 cis 78 ohms. The load at the receiving end is 100 MW at 230 kV, 85% lagging power factor. What is the voltage at the sending end? a. 235.43 kV b. 226.3 kV c. 231.78 kV d. 238.21 kV 2. A 66 kv medium length transmission line delivers a load of 10 MW at 66 kv and 80% lagging P.F. the...
Please, i need a explication step by step of this
1. A 00-Hz short transmission line, having R = 0.62 ohms per phase and L = 93.24 millinenrys per phase, supply a three-phase, wye-connected 100 MW load of 0.9 lagging power factor at 215 kV line-to-line voltage. Calculate and determine the following: a. Calculate the sending-end voltage per phase. b. Determine the voltage regulation of the transmission line. c. Determine the efficiency of transmission of the transmission line.