Question

Question 3 b: /Mark 17] (CLO 3 and 4). A 236 kV, three-phase medium transmission line is 211 km long. The line has a per phas

please,I need the solution within 15 min
0 0
Add a comment Improve this question Transcribed image text
Answer #1

Giren Data ! Ve= 236 KV (rated) d=211km R = 0.0411 , X4=jo-301-2/km XL = 30-301X211 XL = 163.5112 Xc, = .211.8 kr - km 1.003kmedium transmission line as a model Z 1 T VR L Y a Z = XL = 963-511 2 ; y = jwc = = j). Xc -3 X10 1.033 3 y=j1x103 1 - Univer= cos(0.79) IRL - IRph = Load voltage Vp = 231 kV Vene raphase = 231 k VR = 133.3619 KV VBVR, IR, Coso = 98x106 Tre - IpphaseIsph= (31•015 x103) (133-36x103) + 10-968)* ( 310.04 -34-8) Isph = 135.3664 + 300-118 |-3418) Isph = 237.01 - 948-27 Isph = 2

Add a comment
Know the answer?
Add Answer to:
please,I need the solution within 15 min Question 3 b: /Mark 17] (CLO 3 and 4)....
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Please help me with question 2 ASAP Question 1 [15 Marks A 500-kV, 60-Hz, 3-phase completely...

    Please help me with question 2 ASAP Question 1 [15 Marks A 500-kV, 60-Hz, 3-phase completely transposed overhead line has the resistance R=0.0201/km, Ds = 0.149m and r=0.16m. The horizontal phase spacings between the conductors are 10, 10, and 20 m. Calculate a) the line inductive reactance in /km, b) the line impedance in /km, c) the line capacitance-to-neutral Can in F/m, d) the admittance-to-neutral in S/km, neglecting the effect of the earth plane, and e) the exact ABCD parameters...

  • PROBLEM: A 230-kV, 50 Hz, three-phase transmission line is 120 km long. The line has a per phase ...

    PROBLEM: A 230-kV, 50 Hz, three-phase transmission line is 120 km long. The line has a per phase series impedance of z-0.05 +j0.45 Ω per km, and a per phase shunt admittance of y 3.4x10-6 Siemens per km. The line delivers (at the receiving end) 200 MVA, 0.8 lagging power factor at 220 kV. Now consider two cases: A- Assume that shunt parameters of the transmission line are ignored (i.e. even if this is a medium length transmission line, under...

  • A 230kV three phase transmission line has a per phase series impedance of z=0.05+j0.45ohms per km...

    A 230kV three phase transmission line has a per phase series impedance of z=0.05+j0.45ohms per km and a per phase shunt admittance of y= j3.4x10^-6 siemens per km. The line is 80km long. Using the medium line pi model: (a) Determine the transmission line model constants A, B, C, and D (b) Find the sending end (generating) voltage, current and power when the line delivers to a load of 1. 200 MVA with 0.8 lagging power factor at 220 kV...

  • A three-phase transmission line is 200 km long. lt has a total series impedance of 25+j110)Ω...

    A three-phase transmission line is 200 km long. lt has a total series impedance of 25+j110)Ω Per Phase and a total shunt admittance ofj5x 10 Ω. It delivers 180 MW at 275 kV and 0.8 power factor lagging to a load connected at the receiving end. Using the medium π model of the line, determine the voltage, current, real power, reactive power and power factor at the sending end of the line.

  • power system A single-circuit 60-Hz high voltage power transmission line is 370 km (230 mi) long....

    power system A single-circuit 60-Hz high voltage power transmission line is 370 km (230 mi) long. The conductors are Rook with flat horizontal configuration and 7.25 ms=(23.8 ft.) conductor spacing. The load on the line is 125 MW at 100% power factor. Use attached Tables A3 to A3to determine; The sending end voltage Vs The sending end current Is The sending end power Ps The percentage voltage regulation The transmission efficiency Given that Ds for the Rook conductor is 0.0327...

  • Q2. Draw the nominal π circuit that is used to represent the medium-length transmission line model with total series impedance Z and total shunt admittance Y. Then derive the equations to express the...

    Q2. Draw the nominal π circuit that is used to represent the medium-length transmission line model with total series impedance Z and total shunt admittance Y. Then derive the equations to express the ABCD parameters (a) 20% (b)A 200 km, 230 kV, 50 Hz three-phase overhead transmission line has a positive-sequence series impedance z (0.08 + j0.48) Ω/km, and a positive-sequence shunt admittance y-j3.33 x 10T° S/km. At full load, the line delivers 250 MW at 0.99 power factor lagging...

  • Question: A three-phase, 60-Hz, completely transposed transmission line has a length of 100-km and has a...

    Question: A three-phase, 60-Hz, completely transposed transmission line has a length of 100-km and has a series impedance per phase of (0.25+j0.85) ohms/mile and shunt admittance of 5.0*10^-5 Siemens/mile. The transmission line delivers 150 MW at 0.85 lagging power factor to a load connnected to its receiving end. The line-to-line voltage at the receiving end is 138-kV. Note: The Medium Length Line method should be used since it is used for distances between 50 miles to 150 miles. Determine the...

  • A 230-kV, three-phase transmission line has a per phase series impedance of z = 0.05j0.45 2...

    A 230-kV, three-phase transmission line has a per phase series impedance of z = 0.05j0.45 2 per km and a per phase shunt admittance ofy = j3.4 x 10-6 siemens per km. The line is 80 km long. Using the nominal r model, determine (a) The transmission line ABCD constants. Find the sending end voltage and current, voltage regulation, the sending end power and the transmission efficiency when the line delivers (b) 200 MVA, 0.8 lagging power factor at 220...

  • Solve all questions and submit through blackboard by March 26, 2020 Q. 1 (i) Classify short,...

    Solve all questions and submit through blackboard by March 26, 2020 Q. 1 (i) Classify short, medium and long transmission lines based on distance (km). (ii) Classify transmission lines (low, medium, high, extra high) based on voltage levels (kV). (iii) What is commonly used conductor material for overhead transmission lines. Why Aluminum and copper materials are not used for conductors of transmission lines. Q. 2: A 3-phase, 230 kV transmission line having a length of 50 km is composed of...

  • A 3-ph, 50 Hz overhead transmission line 100 km long delivers 20 MW at 0.9 p.f...

    A 3-ph, 50 Hz overhead transmission line 100 km long delivers 20 MW at 0.9 p.f lagging and at 110 kV. The resistance and reactance per phase per km are (0.2) Ω and (j0.4) Ω respectively, while capacitive admittance per phase per km is (j2.5 * 10-6) siemen. Using nominal T circuit, Find: 1- Constants A, B, C, and D. 2- Sending end voltage.        3- Sending end current 4- Sending end power factor    5- Voltage regulation of this T.L.    6-...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT