Question

(3) Figure 3 shows a system including three components: heater, thermostat, and room. Assume the initial room temperature is 0 C. The heater is turned on to heat the room to the desired temperature 25C (i.e heater temperature is 25 C). A fan takes room air, and passes it through the heater and back to the room, with volumetric air flow rate q,. The density of air is assumed to 1.225 kg/m The space of the room is 30 m. Assume the heat loss to the ambient is ignorable. Develop a differential equation to describe the room temperature dynamics. Assume 0.2 mscc. Please compute the time constant and time needed to reach the desired room temperature (within 2%). Outside Room Heat Room roo Heat room Air Flow Thermostat Onvo Control Heater av Figure 3

0 0
Add a comment Improve this question Transcribed image text
Answer #1

We assume density and specific heat of air are constants.

Refer the control volume diagram below:

om

From 1st law of thermodynamics.

(Net heat gain by room)= (Increase of internal energy of air in room)

\rho c_pV_{room}\frac{dT_{room}}{dt}=\rho c_pq_v(T_h-T_{room})

Or

\frac{dT_{room}}{dt}+\frac{q_v}{V_{room}}T_{room}=\frac{q_v}{V_{room}}T_h

Substituting values

\frac{dT_{room}}{dt}+\frac{0.2}{30}T_{room}=\frac{0.2}{30}(25)

Or

\frac{dT_{room}}{dt}+0.006667T_{room}=0.1667

The solution of the above differential equation is

T_{room}=ce^{-0.006667t}+25

At t=0 Troom=0

Hence

c=-25

Therefore

T_{room}=25(1-e^{-0.006667t})

This is the required equation for room temperature.

The time constant is

\tau=\frac{1}{0.006667}=150\: s

For reaching within 2% of final value of 250C

T_{room}=0.98(25)=24.5^0C

Hence

24.5=25(1-e^{-0.006667t})

Or

t= 587 s

It will take 587 s to reach within 2% of final temperature of 250C

Add a comment
Know the answer?
Add Answer to:
(3) Figure 3 shows a system including three components: heater, thermostat, and room. Assume the initial...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • for what ?? Question/12_ The room shown in the figure has a heater with heat flow...

    for what ?? Question/12_ The room shown in the figure has a heater with heat flow rate input of go. The thermal capacitances of the heater and the room air are C, and C2, respectively. The thermal resistances of the heater-air interface and the room wall-ambient air interface are R, and R2, respectively. The temperatures of the heater and the room air are T, and T2, respectively. The temperature outside the room is T. which is assumed to be constant....

  • The room shown in Figure 1 has a heater with heat flow rate input of q0. The thermal capacitances of the heater and the...

    The room shown in Figure 1 has a heater with heat flow rate input of q0. The thermal capacitances of the heater and the room air are C1 and C2, respectively. The thermal resistances of the heater–air interface and the room wall–ambient air interface are R1 and R2, respectively. The temperatures of the heater and the room air are T1 and T2, respectively. The temperature outside the room is T0, which is assumed to be constant. a. Draw the circuit...

  • As shown in the figure, a building with an internal volume of 400 m³ is heated...

    As shown in the figure, a building with an internal volume of 400 m³ is heated by an electric heater with a power of 30 kW. The electric heater is located in an adiabatic canal and the canal is inside the building. Initially, the air inside the building is at 14 ° C and the atmospheric pressure at the location of the building is 95 kPa. There is a heat output of 450 kJ per minute from the building. In...

  • As shown in the figure, a building with an internal volume of 400 m³ is heated...

    As shown in the figure, a building with an internal volume of 400 m³ is heated by an electric heater with a power of 30 kW. The electric heater is located in an adiabatic canal and the canal is inside the building. Initially, the air inside the building is at 14 ° C and the atmospheric pressure at the location of the building is 95 kPa. There is a heat output of 450 kJ per minute from the building. In...

  • Please write the answer legibly. Question: As shown in the figure, a building with an internal...

    Please write the answer legibly. Question: As shown in the figure, a building with an internal volume of 400 m² is heated by an electric heater with a power of 30 kW. The electric heater is located in an adiabatic canal and the canal is inside the building. Initially, the air inside the building is at 14 °C and the atmospheric pressure at the location of the building is 95 kPa. There is a heat output of 450 kJ per...

  • hair dryer may be idealized as a circular duct through which a small fan draws ambient...

    hair dryer may be idealized as a circular duct through which a small fan draws ambient air and within which the air is heated as it flows over a coiled electric resistance wire. (1) If a dryer is designed to operate with an electric power consumption of Pelec= 1500 W and to heat air from an ambient temperature of Ti= 20°C to a discharge temperature of To= 45°C, at what volumetric flow rate ∀˙ should the fan operate? Heat loss...

  • 3. (40pts) | In the thermal system shown in Figure 7-28(a), it is assumed that the tank is insula...

    3. (40pts) | In the thermal system shown in Figure 7-28(a), it is assumed that the tank is insulated to eliminate heat loss to the surrounding air, that there is no heat storage in the insula tion, and that the liquid in the tank is perfectly mixed so that it is at a uniform temper ature. (Thus, a single temperature can be used to denote both the temperature of the liquid in the tank and that of the outflowing liquid.)...

  • a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room...

    a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 m3/min of room return air at 30°C, 50% relative humidity is first mixed with 40 m/min of outdoor at 10°C, 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. [Note that air...

  • a) what is the physical interpretation of the wet-bulb temperature? b) during winter time a room...

    a) what is the physical interpretation of the wet-bulb temperature? b) during winter time a room is maintained at a steady temperature and humidity by an air-conditionibg system shown. 200 m^3/ min of room return air at 30 c, 50% relative hunidity is first mixed with 40 m^3/min of outdoor at 10 c, 20% relative humidity. the mixed air is then introduced to a heater where the temp of air is raised to 45 c and supplied to the room....

  • The figure shows data for a portion of the ducting in a ventilation system operating at...

    The figure shows data for a portion of the ducting in a ventilation system operating at steady state. The ducts are well insulated and the pressure is very nearly 1 atm throughout. The volumetric flow rate entering at state 2 is AV2 = 4800 ft3/min. Assume the ideal gas model for air with cp = 0.24 Btu/lb·oR and ignore kinetic and potential energy effects. The figure shows data for a portion of the ducting in a ventilation system operating at...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT