A constant volume air handler with reheat has incoming are to the cooling coil at 80 F and 25% relative humidity. The temperature leaving the cooling coil is 55F. The minimum supply air temp to any zone is 62F.

1. Situation represents good practice

2. Situation represents a case in which unnecessary cooling and reheat will occur

3. Relative humidity of air leaving coil is 100%

4. None of the above

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Option 2 is correct. Minimum air supply is given 62F, so unnecessary cooling to 55F then again reheating to 62F is being done