Question

1. A renewable energy system delivers 120 kW of three-phase power at 400 V (line-line) to...

1. A renewable energy system delivers 120 kW of three-phase power at 400 V (line-line) to a load with a 0.9 lagging power factor. If each power line has a resistance of R = 0.03 Ω and reactance of X = 0.04 Ω, determine the sending end voltage (line-line) of the three-phase power line connected to the renewable energy system for supplying power to the load.
2. A network service operator found that the voltage rise in a network due to distributed generation is a growing concern. Suggest ways to mitigate this problem.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Rejx = 0.03 e30.04 = 0.05 53.13 Sending End Receiving end 400 -6 I Receiving End Power / ph = = Current 120 - 40 kw 3 Vph Iph

. The voltage rise can be mitigated through the following approaches: • Resistance reduction approach • Reactive power compensation approach • Coordinated voltage control approach

1 Resistance reduction approach If the amount of the connected DG to a DS system is constant it is known that the worst case voltage rise which consider maximum DG penetration, is directly proportional to the the resistance of the line. Therefore, if the resistance of the line is reduced, the voltage rise on the DS will also be be reduced. The resistance of a line can be reduced by increasing the conductor size

.2 Reactive power compensation approach. The amount of reactive power that can be imported generally depends on the parameters of the generators. Typically, a synchronous generator can import power at a 0.95 power factor whereas a wind turbine with uncompensated induction generator can import power at around a 0.9 power factor..We can use a switched capacitor bank or other form of reactive power compensation to restore the system voltages.

3 Coordinated voltage control approach In conventional passive distribution network, it is common practice to maintain the primary DS above the nominal voltage to ensure that the system voltages remain within the specified −6% voltage limit as the voltage drops This can easily be done by using OLTC connected to the system in short distribution system but in case of long distribution system which includes many distribution transformers it may be impractical. However, in more complex network, the value of this voltage, and the corresponding tap position of the OLTC, would have to be optimized.

Add a comment
Know the answer?
Add Answer to:
1. A renewable energy system delivers 120 kW of three-phase power at 400 V (line-line) to...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT