Question

Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW at 0.8 power factor lagging. The line impedance is (1.4 +J1.6) Ω per phase between generator G1 and the load, and (0.8 +jl ) Ω per phase between generator G2 and the load. If generator Gl supplies 15 kW at 0.8 power factor lagging, with a terminal voltage of 460 V line- to-line, determine 1. The voltage at the load terminals. 2. The voltage at the terminals of generator G2 3. The real and reactive power supplied by generator G2 Assume balanced operations. Please provide detailed calculation.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

la, 2 O Volbiy - 23. S 33 - 36.37 V 3 37s.&S 2 .737ф Voltagrał bn..uh 뎔 ga S7· 636 ,-39.61 623. S 3s -36- 87 54.ISヒ4/.47 8 A リ 257. 73 。 636 V 0124.43 +) /7409.176 VA 20.124

Add a comment
Know the answer?
Add Answer to:
Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Problem 3. Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs...

    Problem 3. Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW at 0.8 power factor lagging. The line impedance is (1.4 + j1.6) 12 per phase between generator G1 and the load, and (0.8 + jl) 2 per phase between generator G2 and the load. If generator G1 supplies 15 kW at 0.8 power factor lagging, with a terminal voltage of 460 V line-to-line, determine: 1. The voltage at the load terminals. 2....

  • EXPLAIN THESE QUESTIONS WITH THE HELP OF DIAGRAMS AND LABEL DIAGRAMS IN SUCH A WAY THAT...

    EXPLAIN THESE QUESTIONS WITH THE HELP OF DIAGRAMS AND LABEL DIAGRAMS IN SUCH A WAY THAT I CAN EASILY UNDERSTAND WHAT WE ARE FINDING AND HOW WE ARE FINDING THE REQUIRED THINGS .I AM POSTING MY QUESTION 4TH TIME PLEASE DONOT WASTE IT AND PLEASE DO ALL STEPS I NEED MY ANSWER STEP BY STEP by the line Two balanced Y-connected loads, one drawing 10 kW at 0.8 power factor lagging and the other 15 kW at 0.9 power factor...

  • UISIZULU Problem 4 A three phase, 5 kW, wye-connected load operate onnected load operates at 0.8...

    UISIZULU Problem 4 A three phase, 5 kW, wye-connected load operate onnected load operates at 0.8 power factor lagging with a terminal voltage of 100 V (line to line). The cables connecting e bles connecting each phase of the load to the wye-connected supply has an impedance of (0.25 +0.25) 12. Compute the following: a) Reactive power drawn by the load. b) Real and reactive power losses in the system. me current and line voltage at the source terminals and...

  • A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel...

    A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel connected loads: • Load 1 absorbs a total of 125 kW and 100 KVAR • Load 2 is a delta-connected impedance load with (125+j 40)ohms/phase • Load 3 absorbs 120 kVA at 0.8 power factor (lagging) Given that the line-neutral voltage at the load end of the line is 2400 V, determine the magnitude of the line-to- line voltage at the source end of...

  • The impedance of a three-phase line is 0.3 + j 2.4 per phase. The line feeds...

    The impedance of a three-phase line is 0.3 + j 2.4 per phase. The line feeds two balanced three- phase loads connected in parallel. The first load takes 600 kVA at 0.7 p.f. lagging. The second takes 150 kW at unity power factor. The line to line voltage at the load end of the line is 3810.5 V. Find a) The magnitude of the line voltage at the source end of the line. b) The total active and reactive power...

  • A three phase line has an Impedance of 0.4+j2.7 Ω per phase. The line feeds two...

    A three phase line has an Impedance of 0.4+j2.7 Ω per phase. The line feeds two balanced three phase loads that are connected in parallel. The first load is absorbing 560.1kVA @ PF=0.707 lagging and the second load absorbs 132kW @ PF=1. The line-to-line voltage at the load side is 3810.5/_30° V. Determine: a) The magnitude of the line voltage at the source side b) Total active & reactive power loss in the line c) Active and reactive power at...

  • 12. For a three-phase balanced system, a generator serves a remote load through two parallel tran...

    12. For a three-phase balanced system, a generator serves a remote load through two parallel transmission lines with 4 transformers. The system parameters are as follows: Generator: T1: (A-Y, with Y side voltage leading) T2: (A-Y, with Y side voltage leading) T3: (A-Y, with Y side voltage leading) T4: (A-Y, with Y side voltage leading) Line-1 Line-2 Load 100MVA, 21kV, x-0.15pu 120MVA, 20Д/165Y kV, x-O.12pu 80MVA, 20A/1 10Y kV, x-O.1pu 120MVA, 165A/33Y kV, x-0.12pu 80MVA, 11ОД/33Y kV, x-O.1pu 30+j100 O...

  • Rework problem 3.4 if the load connected to the 240-V secondary winding absorbs 110 kVA under...

    Rework problem 3.4 if the load connected to the 240-V secondary winding absorbs 110 kVA under short-term overload conditions at an 0.8 power factor leading and at 230 volts. Reference of problem 3.4 A single phase 100-kVA 2400/240-volt 60 Hz distribution transformer is used as a step down transformer. The load, which is connected to the 240-volt secondary winding, absorbs 60kVA at 0.8 power factor lagging and is at 230 volts. Assuming an ideal transformer, calculate the following: a) primary...

  • 10. Two loads connected in parallel draw a total of 2.4 kW at 0.8 pflagging from...

    10. Two loads connected in parallel draw a total of 2.4 kW at 0.8 pflagging from a 120-V rms, 60- Hz line. One load absorbs 1.5 kW at a 0.707 pf lagging. Determine: (a) the pf of the second load, INV 11. Calculate the line currents for the system shown in figure. Calculate also the total power and reactive power consumed by the load. w 12. For the balanced three-phase circuit in Fig.. Calculate the line currents, the phase voltage...

  • Q3. (10 marks) A three-phase delta-connected load absorbs 7.5 kW at a lagging power factor of...

    Q3. (10 marks) A three-phase delta-connected load absorbs 7.5 kW at a lagging power factor of 0.823 when connected to a 660 V, 3-phase supply. Calculate the three line currents in the circuit. Answers: (7.972 -34.61) A. (7972-154,61) A. (7.972-274.619) A.

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT